[200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO

George Ziri georgeziri at bfms.com.au
Wed Jun 24 17:49:27 AEST 2015


Good afternoon All

Please find attached the review of the cooling tower.

If there is no objection within 72 hours I will issue Sharp Cooling a work order.

[cid:image001.jpg at 01D0AEA6.1B1EC570]


From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf Of Matt Perkins
Sent: Friday, 12 June 2015 4:03 PM
To: ec at 200william.com; Pia Cunningham
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO

Hi Pia,
 Further to my conversation with George on that matter. George is going to engage Sharp cooling to check the ventilation/HVAC Plant  for vibrations.  Can you please advice Mr LaForest that George will be arranging . (give me a call for clarification)

Matt



On 12/06/2015 3:37 pm, Matt Perkins wrote:
Thanks Pia,
  William form BMFS will be attending 601 to see if he can fell the same effect Mr Laforest  is feeling. I would say the next step from there is to get the building engineer to prepare a report as to what if any action we need to take.


Matt.

 On 12/06/2015 3:22 pm, Pia Cunningham wrote:
Hi All,

Please see email from electrician:



Hi Pia,

As you are aware, Craig Laforest called our Glenco office on 21/10/2014 and we listened to his concerns and provided the following opinion based on our own general knowledge. Craig explained that he had concerns about some kind of radiation which he feels is emanating from above his apartment which he says causes him sleeplessness, nausea and irritation. We suggested that "radiation" as such is unlikely and could be caused by RF transmitters or microwave communications equipment etc. On occasion mobile net transmitters and receivers are installed on roof tops under a position lease agreement, owned and serviced by a Telecommunications carrier. Craig indicated that this is not the case for this building.

The possibilities which we can speculate which could be the cause or a factor in causing what Craig claims to be experiencing are as follows;

Vibration - vibration from motors through a ducting system could possibly create a low frequency vibration noise. Low frequency sound waves can cause nausea and discomfort.

Static electricity - static electricity is a common problem and can cause discomfort for very sensitive people.  This varies with ambient weather conditions and is enhanced by the presence of synthetic materials - carpet, blankets, furniture. Static is felt as an electric charge which builds up and often will be felt as a zap when you touch a metallic object or another person as the charge is released.

Air pressure - I mentioned that sudden variations in air pressure can cause dizziness. This can be observed if you stand with your ear to an elevator door. One ear experiences different pressure to the other which makes you feel giddy. Whether or not the lift shaft could cause such an effect is unknown but I would expect this to be unlikely.


Summary


*         Our advice to Craig was to carry out a test by isolating the ventilation system (above his apartment ) and test whether he notices a change. At this per we have not confirm if this is feasible as it may impact on the ventilation operation. If he does notice a change, an air conditioning or ventilation specialist needs to attend to balance the motor & address vibration issues.

*         Arrange for a company who are expert in detecting radiation to attend site and carry out relevant testing with appropriate equipment.

*         Liaise with electrical engineering company for further evaluation on other possibilities that may be imminent.

We are happy to assist in any other way and look forward to hearing from you.




Regards,

Glenn Rosen

<image003.jpg><http://www.glenco.com.au/>

<image004.jpg><http://www.glenco.com.au/><image005.jpg><https://www.facebook.com/glencoelectricalservices> <image006.png><https://twitter.com/GlencoES> <image007.png><http://www.linkedin.com/pub/glenn-rosen/16/317/6b1>

Glenco Electrical Services
Glenco Security and Alarms
T: (02) 9700 9996  |  F: (02) 9700 9966  |  PO Box 7402, Alexandria NSW 2015
W: www.glenco.com.au<http://www.glenco.com.au/>  |  E: service at glenco.com.au<mailto:service at glenco.com.au>

This e-mail and any attachments are confidential. If you are not the intended recipient, you must not disclose or use the information contained in it. If you have received this e-mail in error, please contact us immediately and delete all copies. Glenco is not responsible for any changes made to a document other than those made by Glenco, or for the effect on the document's meaning. Before opening or using attachments please check them for viruses.


Should you have any queries regarding the above, please do not hesitate to contact me.

Have a nice day,

Kind regards,
Pia Cunningham
Strata Manager
BMC Manager and
Company Title Manager

Phone: (02) 9266 2600 | Email: pcunningham at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 72, STRAWBERRY HILLS NSW 2012, Level 7, 447 Kent Street, SYDNEY  NSW  2000

[cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box]<http://www.stratatitle.com.au/>        [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>


[Tile2014_YoungStrataManager_HighCom_S]
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com] On Behalf Of Ed Sainsbury
Sent: Thursday, 11 June 2015 9:45 PM
To: ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO

EC,

I get a strange magnetic field in my apartment next to the column in the kitchen. If I put a compass there it reacts strongly away from North and is effected by what is in the column. I assume that it is an electrical conduit?

Having said that, I would ask that the EC put in writing to Mr Laforest that he gather some kind of evidence as it is a strange type of request. If there is an issue, the strata can look at the facts.

Regards,
Edward

From: Barney Kitay [mailto:barnet at kitays.com]
Sent: Thursday, June 11, 2015 3:04 PM
To: George Ziri
Cc: ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO


I believe that if George is not able to "feel" it, he should get an independent consultant at his own cost to provide evidence of this "power" if something is discovered AND subsequently corrected (by the strata), he can be reimbursed. i don't think we should fund a wild goose chase...


---

Kind Regards



Barney

m:  +61 (0)400 200 446

e:   barnet at kitays.com<mailto:barnet at kitays.com>

==================================================

On 11-06-2015 14:21, George Ziri wrote:
Good afternoon All,

I have briefed Matt on this matter and confirm below.

Approximently 2 years ago the owner of 601 called me into his apartment to investigate the "feeling of power" over the bed in the main bedroom.  When I stood near the bed I was not able to agree or feel the power. The owner insisted it was there.

I suggested to the owner to obtain an independent assessment by an electrical enginneer. To date this has not occurred.

There may or may not be power circulating the apartment but I have never encounted or heard of this unless one was standing in a room with mains power exceeding 415v.

Please advise if you wish for me to arrnage our facilities manager to inspect. And if the matter isnt discovered then how to proceed.

[cid:image001.jpg at 01D0AEA6.1B1EC570]


From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com] On Behalf Of Pia Cunningham
Sent: Thursday, 11 June 2015 10:17 AM
To: Matt Perkins; ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO

Hi George,

Can you please investigate?



Have a lovely day,

Pia Cunningham
Strata Title Management

Ph: 9266 2600


-------- Original message --------
From: Matt Perkins <matt at spectrum.com.au<mailto:matt at spectrum.com.au>>
Date: 11/06/2015 9:32 am (GMT+09:30)
To: ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
Hi Pia,
 I suggest you get George to investigate if this is a strata problem or if he should contact his own Electrician.

Matt.



/On 11/06/2015 9:16 am, Pia Cunningham wrote:
Good Morning All,

Please see below email from Craig regarding a power surge in his unit again.

Should we send someone to investigate?

Should you have any queries regarding the above, please do not hesitate to contact me.

Have a nice day,

Kind regards,
Pia Cunningham
Strata Manager
BMC Manager and
Company Title Manager

Phone: (02) 9266 2600 | Email: pcunningham at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 72, STRAWBERRY HILLS NSW 2012, Level 7, 447 Kent Street, SYDNEY  NSW  2000

[cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box]<http://www.stratatitle.com.au/>        [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>


[Tile2014_YoungStrataManager_HighCom_S]
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: CSCL [mailto:cscl at optusnet.com.au]
Sent: Wednesday, 10 June 2015 1:49 PM
To: Pia Cunningham
Cc: traceyquick at hotmail.com<mailto:traceyquick at hotmail.com>
Subject: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO


Hello Pia,

I left you a message over the weekend but wanted to contact you as soon as possible about an old concern which has started again.  We are still feeling what can be best described as a 'charge' in my bedroom particularly ,and the second bedroom partially.  It can happen at any time of the day or night.

Would you please have this investigated by an expert asap. You'll remember I sent through an expert's advice on this matter.  This testing will probably take several days/nights to find where this is coming from but it feels like it is directly from the ceiling area/walls above the main bedroom and second bedroom.

I look forward to hearing from you at the earliest opportunity.

Thanks Pia and best wishes,
Craig





_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec





--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/


_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec




_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec




--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/




_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec




--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0001.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 35654 bytes
Desc: image001.jpg
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0002.jpg 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 17026 bytes
Desc: image002.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0008.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 4236 bytes
Desc: image003.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0009.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 3977 bytes
Desc: image004.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0010.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 4502 bytes
Desc: image005.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0011.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1473 bytes
Desc: image006.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0012.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1732 bytes
Desc: image007.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0013.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 60738 bytes
Desc: image008.jpg
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0003.jpg 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 1493 bytes
Desc: image009.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0014.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 1724 bytes
Desc: image010.png
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0015.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Power surge complaint.docx
Type: application/vnd.openxmlformats-officedocument.wordprocessingml.document
Size: 43952 bytes
Desc: Power surge complaint.docx
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0001.bin 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Power surge complaint.pdf
Type: application/pdf
Size: 54049 bytes
Desc: Power surge complaint.pdf
Url : http://200william.com/mailman/private/ec/attachments/20150624/c0661c75/attachment-0001.pdf 


More information about the EC mailing list