[200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
Matt Perkins
matt at spectrum.com.au
Wed Jun 24 19:30:10 AEST 2015
Hi George,
I hope that this will put an end to the 3 year + complaints about
noise from the HVAC plant. I endorse the work. I Hope everyone else
agrees.
Matt.
On 24/06/2015 5:49 pm, George Ziri wrote:
>
> Good afternoon All
>
> Please find attached the review of the cooling tower.
>
> If there is no objection within 72 hours I will issue Sharp Cooling a
> work order.
>
> *From:*ec-bounces at 200william.com [mailto:ec-bounces at 200william.com]
> *On Behalf Of *Matt Perkins
> *Sent:* Friday, 12 June 2015 4:03 PM
> *To:* ec at 200william.com; Pia Cunningham
> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST
> - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
>
> Hi Pia,
> Further to my conversation with George on that matter. George is
> going to engage Sharp cooling to check the ventilation/HVAC Plant for
> vibrations. Can you please advice Mr LaForest that George will be
> arranging . (give me a call for clarification)
>
> Matt
>
>
>
> On 12/06/2015 3:37 pm, Matt Perkins wrote:
>
> Thanks Pia,
> William form BMFS will be attending 601 to see if he can fell
> the same effect Mr Laforest is feeling. I would say the next step
> from there is to get the building engineer to prepare a report as
> to what if any action we need to take.
>
>
> Matt.
>
> On 12/06/2015 3:22 pm, Pia Cunningham wrote:
>
> Hi All,
>
> Please see email from electrician:
>
>
> Hi Pia,
>
> As you are aware, Craig Laforest called our Glenco office on
> 21/10/2014 and we listened to his concerns and provided the
> following opinion based on our own general knowledge. Craig
> explained that he had concerns about some kind of radiation
> which he feels is emanating from above his apartment which he
> says causes him sleeplessness, nausea and irritation. We
> suggested that “radiation” as such is unlikely and could be
> caused by RF transmitters or microwave communications
> equipment etc. On occasion mobile net transmitters and
> receivers are installed on roof tops under a position lease
> agreement, owned and serviced by a Telecommunications carrier.
> Craig indicated that this is not the case for this building.
>
> The possibilities which we can speculate which could be the
> cause or a factor in causing what Craig claims to be
> experiencing are as follows;
>
> *_Vibration_*– vibration from motors through a ducting system
> could possibly create a low frequency vibration noise. Low
> frequency sound waves can cause nausea and discomfort.
>
> *_Static electricity_*– static electricity is a common problem
> and can cause discomfort for very sensitive people. This
> varies with ambient weather conditions and is enhanced by the
> presence of synthetic materials – carpet, blankets, furniture.
> Static is felt as an electric charge which builds up and often
> will be felt as a zap when you touch a metallic object or
> another person as the charge is released.
>
> *_Air pressure_*– I mentioned that sudden variations in air
> pressure can cause dizziness. This can be observed if you
> stand with your ear to an elevator door. One ear experiences
> different pressure to the other which makes you feel giddy.
> Whether or not the lift shaft could cause such an effect is
> unknown but I would expect this to be unlikely.
>
> *_Summary_*
>
> ·Our advice to Craig was to carry out a test by isolating the
> ventilation system (above his apartment ) and test whether he
> notices a change. At this per we have not confirm if this is
> feasible as it may impact on the ventilation operation. If he
> does notice a change, an air conditioning or ventilation
> specialist needs to attend to balance the motor & address
> vibration issues.
>
> ·Arrange for a company who are expert in detecting radiation
> to attend site and carry out relevant testing with appropriate
> equipment.
>
> ·Liaise with electrical engineering company for further
> evaluation on other possibilities that may be imminent.
>
> We are happy to assist in any other way and look forward to
> hearing from you.
>
> Regards,
>
> *Glenn Rosen*
>
> **
>
> *<image003.jpg>* <http://www.glenco.com.au/>
>
> **
>
> <image004.jpg> <http://www.glenco.com.au/>*<image005.jpg>*
> <https://www.facebook.com/glencoelectricalservices>***<image006.png>*
> <https://twitter.com/GlencoES>**<image007.png>
> <http://www.linkedin.com/pub/glenn-rosen/16/317/6b1>
>
> **
>
> *Glenco Electrical Services*
>
> *Glenco Security and Alarms*
>
> *T: (02) 9700 9996 **|** F: (02) 9700 9966 | PO Box 7402,
> Alexandria NSW 2015*
>
> *W: **www.glenco.com.au* <http://www.glenco.com.au/>*| E:
> service at glenco.com.au <mailto:service at glenco.com.au>*
>
> This e-mail and any attachments are confidential. If you are
> not the intended recipient, you must not disclose or use the
> information contained in it. If you have received this e-mail
> in error, please contact us immediately and delete all copies.
> Glenco is not responsible for any changes made to a document
> other than those made by Glenco, or for the effect on the
> document's meaning. Before opening or using attachments please
> check them for viruses.
>
> Should you have any queries regarding the above, please do not
> hesitate to contact me.
>
> Have a nice day,
>
> **
>
> Kind regards,
>
> *Pia Cunningham *
>
> Strata Manager
> BMC Manager and
> Company Title Manager
>
> Phone:(02) 9266 2600 | Email:pcunningham at stratatitle.com.au
> <mailto:northshore at stratatitle.com.au> | Address:PO Box 72,
> STRAWBERRY HILLS NSW 2012, Level 7, 447 Kent Street, SYDNEY
> NSW 2000
>
> **
>
> cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
> <http://www.stratatitle.com.au/>cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
> <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
> <http://www.twitter.com/STMStrata>pinterest.png
> <http://www.pinterest.com/STMStrata>google_plus.png
> <http://plus.google.com/+StrataTitleManagemenSydney>
>
> **
>
> *Emailed Communication / Documents Disclaimer*
>
> STM Limited takes no responsibility for content included in
> this email when relating to a client matter.
>
> Please view Vesture’s full email communication disclaimer on
> our website –www.stratatitle.com.au/disclaimer/
> <http://www.stratatitle.com.au/disclaimer/>
>
> Tile2014_YoungStrataManager_HighCom_S
>
> *Important Notice: *Owners should be aware that all
> correspondence, including letters, facsimile transmissions and
> emails are retained on the file of your scheme and may be
> subject to inspection by owners and residents within your
> scheme, as well as prospective purchasers for any lot that may
> be for sale within your scheme. As such author discretion is
> advised.
>
> *From:*ec-bounces at 200william.com
> <mailto:ec-bounces at 200william.com>
> [mailto:ec-bounces at 200william.com] *On Behalf Of *Ed Sainsbury
> *Sent:* Thursday, 11 June 2015 9:45 PM
> *To:* ec at 200william.com <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG
> LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET,
> WOOLLOOMOOLOO
>
> EC,
>
> I get a strange magnetic field in my apartment next to the
> column in the kitchen. If I put a compass there it reacts
> strongly away from North and is effected by what is in the
> column. I assume that it is an electrical conduit?
>
> Having said that, I would ask that the EC put in writing to Mr
> Laforest that he gather some kind of evidence as it is a
> strange type of request. If there is an issue, the strata can
> look at the facts.
>
> Regards,
> Edward
>
> *From:*Barney Kitay [mailto:barnet at kitays.com]
> *Sent:* Thursday, June 11, 2015 3:04 PM
> *To:* George Ziri
> *Cc:* ec at 200william.com <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG
> LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET,
> WOOLLOOMOOLOO
>
> I believe that if George is not able to "feel" it, he should
> get an independent consultant at his own cost to provide
> evidence of this "power" if something is discovered AND
> subsequently corrected (by the strata), he can be reimbursed.
> i don't think we should fund a wild goose chase...
>
> ---
>
> Kind Regards
>
>
>
> /Barney/
>
> m: +61 (0)400 200 446
>
> e:barnet at kitays.com <mailto:barnet at kitays.com>
>
> ==================================================
>
> On 11-06-2015 14:21, George Ziri wrote:
>
> Good afternoon All,
>
> I have briefed Matt on this matter and confirm below.
>
> Approximently 2 years ago the owner of 601 called me into
> his apartment to investigate the "feeling of power" over
> the bed in the main bedroom. When I stood near the bed I
> was not able to agree or feel the power. The owner
> insisted it was there.
>
> I suggested to the owner to obtain an independent
> assessment by an electrical enginneer. To date this has
> not occurred.
>
> There may or may not be power circulating the apartment
> but I have never encounted or heard of this unless one was
> standing in a room with mains power exceeding 415v.
>
> Please advise if you wish for me to arrnage our facilities
> manager to inspect. And if the matter isnt discovered then
> how to proceed.
>
> *From:*ec-bounces at 200william.com
> <mailto:ec-bounces at 200william.com>
> [mailto:ec-bounces at 200william.com] *On Behalf Of *Pia
> Cunningham
> *Sent:* Thursday, 11 June 2015 10:17 AM
> *To:* Matt Perkins; ec at 200william.com
> <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM
> CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM
> STREET, WOOLLOOMOOLOO
>
> Hi George,
>
> Can you please investigate?
>
> Have a lovely day,
>
> Pia Cunningham
>
> Strata Title Management
>
> Ph: 9266 2600
>
>
>
> -------- Original message --------
> From: Matt Perkins <matt at spectrum.com.au
> <mailto:matt at spectrum.com.au>>
> Date: 11/06/2015 9:32 am (GMT+09:30)
> To: ec at 200william.com <mailto:ec at 200william.com>
> Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM
> CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM
> STREET, WOOLLOOMOOLOO
>
> Hi Pia,
> I suggest you get George to investigate if this is a
> strata problem or if he should contact his own Electrician.
>
> Matt.
>
>
>
> /On 11/06/2015 9:16 am, Pia Cunningham wrote:
>
> Good Morning All,
>
> Please see below email from Craig regarding a power
> surge in his unit again.
>
>
> Should we send someone to investigate?
>
> Should you have any queries regarding the above,
> please do not hesitate to contact me.
>
> Have a nice day,
>
> **
>
> Kind regards,
>
> *Pia Cunningham *
>
> Strata Manager
> BMC Manager and
> Company Title Manager
>
> Phone:(02) 9266 2600 |
> Email:pcunningham at stratatitle.com.au
> <mailto:northshore at stratatitle.com.au> | Address:PO
> Box 72, STRAWBERRY HILLS NSW 2012, Level 7, 447 Kent
> Street, SYDNEY NSW 2000
>
> **
>
> cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
> <http://www.stratatitle.com.au/>cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
> <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
> <http://www.twitter.com/STMStrata>pinterest.png
> <http://www.pinterest.com/STMStrata>google_plus.png
> <http://plus.google.com/+StrataTitleManagemenSydney>
>
> **
>
> *Emailed Communication / Documents Disclaimer*
>
> STM Limited takes no responsibility for content
> included in this email when relating to a client matter.
>
> Please view Vesture’s full email communication
> disclaimer on our website
> –www.stratatitle.com.au/disclaimer/
> <http://www.stratatitle.com.au/disclaimer/>
>
> Tile2014_YoungStrataManager_HighCom_S
>
> *Important Notice: *Owners should be aware that all
> correspondence, including letters, facsimile
> transmissions and emails are retained on the file of
> your scheme and may be subject to inspection by owners
> and residents within your scheme, as well as
> prospective purchasers for any lot that may be for
> sale within your scheme. As such author discretion is
> advised.
>
> *From:*CSCL [mailto:cscl at optusnet.com.au]
> *Sent:* Wednesday, 10 June 2015 1:49 PM
> *To:* Pia Cunningham
> *Cc:* traceyquick at hotmail.com
> <mailto:traceyquick at hotmail.com>
> *Subject:* MESSAGE FROM CRAIG LAFOREST - ELECTRIC
> CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
>
> Hello Pia,
>
> I left you a message over the weekend but wanted to
> contact you as soon as possible about an old concern
> which has started again. We are still feeling what
> can be best described as a ‘charge’ in my bedroom
> particularly ,and the second bedroom partially. It
> can happen at any time of the day or night.
>
> Would you please have this investigated by an expert
> asap. You’ll remember I sent through an expert’s
> advice on this matter. This testing will probably
> take several days/nights to find where this is coming
> from but it feels like it is directly from the ceiling
> area/walls above the main bedroom and second bedroom.
>
> I look forward to hearing from you at the earliest
> opportunity.
>
> Thanks Pia and best wishes,
>
> Craig
>
>
>
>
>
> _______________________________________________
>
> EC mailing list
>
> EC at 200william.com <mailto:EC at 200william.com>
>
> http://200william.com/mailman/listinfo/ec
>
>
>
>
>
> --
>
> /* Matt Perkins
>
> Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
>
> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
>
> Level 6, 350 George Street Sydney 2000
>
> Spectrum Networks is a member of the Communications Alliance & TIO
>
> */
>
> _______________________________________________
>
> EC mailing list
>
> EC at 200william.com <mailto:EC at 200william.com>
>
> http://200william.com/mailman/listinfo/ec
>
>
>
>
> _______________________________________________
>
> EC mailing list
>
> EC at 200william.com <mailto:EC at 200william.com>
>
> http://200william.com/mailman/listinfo/ec
>
>
>
>
> --
>
> /* Matt Perkins
>
> Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
>
> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
>
> Level 6, 350 George Street Sydney 2000
>
> Spectrum Networks is a member of the Communications Alliance & TIO
>
> */
>
>
>
>
> _______________________________________________
>
> EC mailing list
>
> EC at 200william.com <mailto:EC at 200william.com>
>
> http://200william.com/mailman/listinfo/ec
>
>
>
>
> --
> /* Matt Perkins
> Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
> Level 6, 350 George Street Sydney 2000
> Spectrum Networks is a member of the Communications Alliance & TIO
> */
--
/* Matt Perkins
Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
Level 6, 350 George Street Sydney 2000
Spectrum Networks is a member of the Communications Alliance & TIO
*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 35654 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0002.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 17026 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0008.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4236 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0009.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3977 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0010.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4502 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0011.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1473 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0012.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1732 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0013.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 60738 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0003.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1493 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0014.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1724 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/73858314/attachment-0015.png
More information about the EC
mailing list