Hi Pia,
Further to my conversation with George on that matter. George is going
to engage Sharp cooling to check the ventilation/HVAC Plant for
vibrations. Can you please advice Mr LaForest that George will be
arranging . (give me a call for clarification)
Matt
On 12/06/2015 3:37 pm, Matt Perkins wrote:
> Thanks Pia,
> William form BMFS will be attending 601 to see if he can fell the
> same effect Mr Laforest is feeling. I would say the next step from
> there is to get the building engineer to prepare a report as to what
> if any action we need to take.
>
>
> Matt.
>
> On 12/06/2015 3:22 pm, Pia Cunningham wrote:
>>
>> Hi All,
>>
>> Please see email from electrician:
>>
>> Hi Pia,
>>
>> As you are aware, Craig Laforest called our Glenco office on
>> 21/10/2014 and we listened to his concerns and provided the following
>> opinion based on our own general knowledge. Craig explained that he
>> had concerns about some kind of radiation which he feels is emanating
>> from above his apartment which he says causes him sleeplessness,
>> nausea and irritation. We suggested that “radiation” as such is
>> unlikely and could be caused by RF transmitters or microwave
>> communications equipment etc. On occasion mobile net transmitters and
>> receivers are installed on roof tops under a position lease
>> agreement, owned and serviced by a Telecommunications carrier. Craig
>> indicated that this is not the case for this building.
>>
>> The possibilities which we can speculate which could be the cause or
>> a factor in causing what Craig claims to be experiencing are as follows;
>>
>> *_Vibration_*– vibration from motors through a ducting system could
>> possibly create a low frequency vibration noise. Low frequency sound
>> waves can cause nausea and discomfort.
>>
>> *_Static electricity_*– static electricity is a common problem and
>> can cause discomfort for very sensitive people. This varies with
>> ambient weather conditions and is enhanced by the presence of
>> synthetic materials – carpet, blankets, furniture. Static is felt as
>> an electric charge which builds up and often will be felt as a zap
>> when you touch a metallic object or another person as the charge is
>> released.
>>
>> *_Air pressure_*– I mentioned that sudden variations in air pressure
>> can cause dizziness. This can be observed if you stand with your ear
>> to an elevator door. One ear experiences different pressure to the
>> other which makes you feel giddy. Whether or not the lift shaft could
>> cause such an effect is unknown but I would expect this to be unlikely.
>>
>> *_Summary_*
>>
>> ·Our advice to Craig was to carry out a test by isolating the
>> ventilation system (above his apartment ) and test whether he notices
>> a change. At this per we have not confirm if this is feasible as it
>> may impact on the ventilation operation. If he does notice a change,
>> an air conditioning or ventilation specialist needs to attend to
>> balance the motor & address vibration issues.
>>
>> ·Arrange for a company who are expert in detecting radiation to
>> attend site and carry out relevant testing with appropriate equipment.
>>
>> ·Liaise with electrical engineering company for further evaluation on
>> other possibilities that may be imminent.
>>
>> We are happy to assist in any other way and look forward to hearing
>> from you.
>>
>> Regards,
>>
>> *Glenn Rosen*
>>
>> **
>>
>> *<image003.jpg>* <http://www.glenco.com.au/>
>>
>> **
>>
>> <image004.jpg> <http://www.glenco.com.au/>*<image005.jpg>*
>> <https://www.facebook.com/glencoelectricalservices>***<image006.png>*
>> <https://twitter.com/GlencoES>**<image007.png>
>> <http://www.linkedin.com/pub/glenn-rosen/16/317/6b1>
>>
>> **
>>
>> *Glenco Electrical Services*
>>
>> *Glenco Security and Alarms*
>>
>> *T: (02) 9700 9996 **| F: (02) 9700 9966 | PO Box 7402, Alexandria
>> NSW 2015*
>>
>> *W: **www.glenco.com.au* <http://www.glenco.com.au/>*| E:
>> service at glenco.com.au <mailto:service at glenco.com.au>*
>>
>> This e-mail and any attachments are confidential. If you are not the
>> intended recipient, you must not disclose or use the information
>> contained in it. If you have received this e-mail in error, please
>> contact us immediately and delete all copies. Glenco is not
>> responsible for any changes made to a document other than those made
>> by Glenco, or for the effect on the document's meaning. Before
>> opening or using attachments please check them for viruses.
>>
>> Should you have any queries regarding the above, please do not
>> hesitate to contact me.
>>
>> Have a nice day,
>>
>> **
>>
>> Kind regards,
>>
>> *Pia Cunningham *
>>
>> Strata Manager
>> BMC Manager and
>> Company Title Manager
>>
>> Phone:(02) 9266 2600 | Email:pcunningham at stratatitle.com.au
>> <mailto:northshore at stratatitle.com.au> | Address:PO Box 72,
>> STRAWBERRY HILLS NSW 2012, Level 7, 447 Kent Street, SYDNEY NSW 2000
>>
>> **
>>
>> cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
>> <http://www.stratatitle.com.au/>cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
>> <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
>> <http://www.twitter.com/STMStrata>pinterest.png
>> <http://www.pinterest.com/STMStrata>google_plus.png
>> <http://plus.google.com/+StrataTitleManagemenSydney>
>>
>> **
>>
>> *Emailed Communication / Documents Disclaimer*
>>
>> STM Limited takes no responsibility for content included in this
>> email when relating to a client matter.
>>
>> Please view Vesture’s full email communication disclaimer on our
>> website –www.stratatitle.com.au/disclaimer/
>> <http://www.stratatitle.com.au/disclaimer/>
>>
>> Tile2014_YoungStrataManager_HighCom_S
>>
>> *Important Notice: *Owners should be aware that all correspondence,
>> including letters, facsimile transmissions and emails are retained on
>> the file of your scheme and may be subject to inspection by owners
>> and residents within your scheme, as well as prospective purchasers
>> for any lot that may be for sale within your scheme. As such author
>> discretion is advised.
>>
>> *From:*ec-bounces at 200william.com [mailto:ec-bounces at 200william.com]
>> *On Behalf Of *Ed Sainsbury
>> *Sent:* Thursday, 11 June 2015 9:45 PM
>> *To:* ec at 200william.com
>> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG
>> LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
>>
>> EC,
>>
>> I get a strange magnetic field in my apartment next to the column in
>> the kitchen. If I put a compass there it reacts strongly away from
>> North and is effected by what is in the column. I assume that it is
>> an electrical conduit?
>>
>> Having said that, I would ask that the EC put in writing to Mr
>> Laforest that he gather some kind of evidence as it is a strange type
>> of request. If there is an issue, the strata can look at the facts.
>>
>> Regards,
>> Edward
>>
>> *From:*Barney Kitay [mailto:barnet at kitays.com]
>> *Sent:* Thursday, June 11, 2015 3:04 PM
>> *To:* George Ziri
>> *Cc:* ec at 200william.com <mailto:ec at 200william.com>
>> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG
>> LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
>>
>> I believe that if George is not able to "feel" it, he should get an
>> independent consultant at his own cost to provide evidence of this
>> "power" if something is discovered AND subsequently corrected (by the
>> strata), he can be reimbursed. i don't think we should fund a wild
>> goose chase...
>>
>> ---
>>
>> Kind Regards
>>
>> /Barney/
>> m: +61 (0)400 200 446
>> e:barnet at kitays.com <mailto:barnet at kitays.com>
>> ==================================================
>>
>> On 11-06-2015 14:21, George Ziri wrote:
>>
>> Good afternoon All,
>>
>> I have briefed Matt on this matter and confirm below.
>>
>> Approximently 2 years ago the owner of 601 called me into his
>> apartment to investigate the "feeling of power" over the bed in
>> the main bedroom. When I stood near the bed I was not able to
>> agree or feel the power. The owner insisted it was there.
>>
>> I suggested to the owner to obtain an independent assessment by
>> an electrical enginneer. To date this has not occurred.
>>
>> There may or may not be power circulating the apartment but I
>> have never encounted or heard of this unless one was standing in
>> a room with mains power exceeding 415v.
>>
>> Please advise if you wish for me to arrnage our facilities
>> manager to inspect. And if the matter isnt discovered then how to
>> proceed.
>>
>> *From:*ec-bounces at 200william.com
>> <mailto:ec-bounces at 200william.com>
>> [mailto:ec-bounces at 200william.com] *On Behalf Of *Pia Cunningham
>> *Sent:* Thursday, 11 June 2015 10:17 AM
>> *To:* Matt Perkins; ec at 200william.com <mailto:ec at 200william.com>
>> *Subject:* Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG
>> LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET,
>> WOOLLOOMOOLOO
>>
>> Hi George,
>>
>> Can you please investigate?
>>
>> Have a lovely day,
>>
>> Pia Cunningham
>>
>> Strata Title Management
>>
>> Ph: 9266 2600
>>
>>
>>
>> -------- Original message --------
>> From: Matt Perkins <matt at spectrum.com.au
>> <mailto:matt at spectrum.com.au>>
>> Date: 11/06/2015 9:32 am (GMT+09:30)
>> To: ec at 200william.com <mailto:ec at 200william.com>
>> Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG
>> LAFOREST - ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET,
>> WOOLLOOMOOLOO
>>
>> Hi Pia,
>> I suggest you get George to investigate if this is a strata
>> problem or if he should contact his own Electrician.
>>
>> Matt.
>>
>>
>>
>> /On 11/06/2015 9:16 am, Pia Cunningham wrote:
>>
>> Good Morning All,
>>
>> Please see below email from Craig regarding a power surge in
>> his unit again.
>>
>>
>> Should we send someone to investigate?
>>
>> Should you have any queries regarding the above, please do
>> not hesitate to contact me.
>>
>> Have a nice day,
>>
>> **
>>
>> Kind regards,
>>
>> *Pia Cunningham *
>>
>> Strata Manager
>> BMC Manager and
>> Company Title Manager
>>
>> Phone:(02) 9266 2600 | Email:pcunningham at stratatitle.com.au
>> <mailto:northshore at stratatitle.com.au> | Address:PO Box 72,
>> STRAWBERRY HILLS NSW 2012, Level 7, 447 Kent Street, SYDNEY
>> NSW 2000
>>
>> **
>>
>> cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
>> <http://www.stratatitle.com.au/>cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
>> <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
>> <http://www.twitter.com/STMStrata>pinterest.png
>> <http://www.pinterest.com/STMStrata>google_plus.png
>> <http://plus.google.com/+StrataTitleManagemenSydney>
>>
>> **
>>
>> *Emailed Communication / Documents Disclaimer*
>>
>> STM Limited takes no responsibility for content included in
>> this email when relating to a client matter.
>>
>> Please view Vesture’s full email communication disclaimer on
>> our website –www.stratatitle.com.au/disclaimer/
>> <http://www.stratatitle.com.au/disclaimer/>
>>
>> Tile2014_YoungStrataManager_HighCom_S
>>
>> *Important Notice: *Owners should be aware that all
>> correspondence, including letters, facsimile transmissions
>> and emails are retained on the file of your scheme and may be
>> subject to inspection by owners and residents within your
>> scheme, as well as prospective purchasers for any lot that
>> may be for sale within your scheme. As such author discretion
>> is advised.
>>
>> *From:*CSCL [mailto:cscl at optusnet.com.au]
>> *Sent:* Wednesday, 10 June 2015 1:49 PM
>> *To:* Pia Cunningham
>> *Cc:* traceyquick at hotmail.com <mailto:traceyquick at hotmail.com>
>> *Subject:* MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE
>> FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
>>
>> Hello Pia,
>>
>> I left you a message over the weekend but wanted to contact
>> you as soon as possible about an old concern which has
>> started again. We are still feeling what can be best
>> described as a ‘charge’ in my bedroom particularly ,and the
>> second bedroom partially. It can happen at any time of the
>> day or night.
>>
>> Would you please have this investigated by an expert asap.
>> You’ll remember I sent through an expert’s advice on this
>> matter. This testing will probably take several days/nights
>> to find where this is coming from but it feels like it is
>> directly from the ceiling area/walls above the main bedroom
>> and second bedroom.
>>
>> I look forward to hearing from you at the earliest opportunity.
>>
>> Thanks Pia and best wishes,
>>
>> Craig
>>
>>
>>
>>
>> _______________________________________________
>>
>> EC mailing list
>>
>> EC at 200william.com <mailto:EC at 200william.com>
>>
>> http://200william.com/mailman/listinfo/ec
>>
>>
>>
>>
>> --
>>
>> /* Matt Perkins
>>
>> Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
>>
>> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
>>
>> Level 6, 350 George Street Sydney 2000
>>
>> Spectrum Networks is a member of the Communications Alliance & TIO
>>
>> */
>>
>> _______________________________________________
>>
>> EC mailing list
>>
>> EC at 200william.com <mailto:EC at 200william.com>
>>
>> http://200william.com/mailman/listinfo/ec
>>
>>
>>
>> _______________________________________________
>> EC mailing list
>> EC at 200william.com
>> http://200william.com/mailman/listinfo/ec
>
>
> --
> /* Matt Perkins
> Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
> Office 1300 133 299matt at spectrum.com.au
> Level 6, 350 George Street Sydney 2000
> Spectrum Networks is a member of the Communications Alliance & TIO
> */
>
>
> _______________________________________________
> EC mailing list
> EC at 200william.com
> http://200william.com/mailman/listinfo/ec
--
/* Matt Perkins
Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
Level 6, 350 George Street Sydney 2000
Spectrum Networks is a member of the Communications Alliance & TIO
*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 17026 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0008.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4236 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0009.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3977 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0010.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4502 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0011.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1473 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0012.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1732 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0013.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 60738 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0002.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 35654 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0003.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1493 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0014.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1724 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150612/ae242496/attachment-0015.png
More information about the EC
mailing list