[200William-EC] MARQUIS - NORTH FACING APARTMENTS
Matt Perkins
matt at spectrum.com.au
Tue Apr 9 13:45:34 EST 2013
Are you sure this is a fire door. It's glass. I thought a fire door had
to be fire rated. This sounds more like a smoke door or some other sort
of special arrangement.
Can we get the rest of this document I would like to take a look at it.
Is it the building code of Australia. Shane do you have access to that.
Matt.
On 9/04/13 12:57 PM, George Ziri wrote:
>
> No attack taken...
>
> Council have picked up that C3.6 is absent from the statement. They
> have provided 14 days to have rectified otherwise they will impose
> fines. If this measure isn't corrected then they will enforce a fire
> order on the building.
>
> I thought the sticker option would be the cheaper and quickest measure
> around this.
>
> The second option would be to install an audible device and a flashing
> light. This would take a bit longer considering the work involved and
> more expensive. If this measure was approved then the conduit would run:
>
> 1.From the FIP room on Dowling st and through AVIS car park to the laneway
>
> 2.Run up the wall between the 01 and 02 balcony dividing walls
>
> 3.At each balcony a conduit will be fixed to the face of the wall
> where the audible siren and alarm will be placed. The size of these
> items would be no more than 100mm in diameter.
>
> I have asked the fire company to provide a quote.
>
> C3.6 Sliding fire doors
>
> (a) If a doorway in a fire wall is fitted with a sliding fire door
> which is open when the
>
> building is in use-
>
> (i) it must be held open with an electromagnetic device, which when
> de-activated
>
> in accordance with (b), allows the door to be fully closed not less than
>
> 20 seconds, and not more than 30 seconds, after release; and
>
> (ii) in the event of power failure to the door-the door must fail safe
> in the closed
>
> position in accordance with (i); and
>
> (iii) an audible warning device must be located near the doorway and a red
>
> flashing warning light of adequate intensity on each side of the
> doorway must
>
> be activated in accordance with (b); and
>
> Building Code of Australia---Volume One---PART C3 Page 75
>
> (iv) signs must be installed on each side of the doorway located
> directly over the
>
> opening stating-
>
> WARNING-SLIDING FIRE DOOR
>
> in capital letters not less than 50 mm high in a colour contrasting
> with the
>
> background.
>
> ________________________________________________________
> *George Ziri | Operations*
>
> **
>
> *Building Facilities Management Solutions Pty Ltd*
>
> Direct: 0400 300 242 | Facsimile: 9547 3132 | PO BOX A2319 SYDNEY
> SOUTH NSW 1235
>
> visit us www.bfms.com.au <http://www.bfms.com.au>
>
> *From:*ec-bounces at 200william.com [mailto:ec-bounces at 200william.com]
> *On Behalf Of *Matt Perkins
> *Sent:* Tuesday, 9 April 2013 10:31 AM
> *To:* ec at 200william.com
> *Subject:* Re: [200William-EC] MARQUIS - NORTH FACING APARTMENTS
>
> Hi George,
> Let me provide a more considered response now that I have thought
> about it a bit. Firstly I would like to declare a conflict of
> interest in that my property is one of the effected apartments and I
> believe that a sign of this nature will directly effect the resale
> value of my apartment. Through obstruction of the view and esthetics
> with it's positioning. Secondly it brings to the attention of any
> perspective buyers that there is something not quite normal with our
> apartment. That being the 10,000L of ULP under the ramp in the basement.
>
> Also George please dont think this is directed at you. We appreciate
> you are getting all the facts together for us and understand your on
> the clock.
>
>
> Can you please provide the relevant legislation/act/decree that
> stipulates this sign.
> Can you also give us an idea of the ramifications of not complying .
> Im guessing we will not get a fire compliance certificate and will be
> fined (that is the owners corp will be fined)
> Is there any sort of appeal process or area where special
> consideration can be given.
> Can we ask the building architect/engineer for other options that
> comply with the legislation/act/decree
>
> Just to let you know my kitchen does not back on to this door. I have
> two doors one is in the middle of the lounge room the other is in a
> bedroom. The bedroom door does not have a single segment larger then
> 700mm so a 730mm sign simply would not fit. The longe one has a
> curtain pelmet and could not be seen anyway at the top.
>
> Matt.
>
>
>
> On 8/04/13 5:50 PM, George Ziri wrote:
>
> Good Afternoon All,
>
> The north Facing apartments shown below have an automatic sliding
> door which activates (closes) when the fire alarm activates. The
> reason only the North facing sliding doors are equipped with this
> is due to AVIS's on site fuel situation.
>
> As part of the fire safety statement Council has picked up that
> measure C3.6 is required to be certified and have given us until
> the 14.4.13. What is required is a sign to be "displayed at both
> sides of the door entry". This is to remind residents that the
> door may shut at anytime (fire alarm activation)
>
> In most cases the kitchen backs on to the sliding door and will be
> impossible to have it close to the door. I have suggested to place
> on each side of glass to each door.
>
> Your thoughts please. The signs need to be up by the 14^th of this
> month. Therefore require a agreement by Wednesday this week.
>
> 101,102,201,202,301,302,401,402,501,502
>
> ________________________________________________________
> *George Ziri | Operations*
>
> **
>
> *Building Facilities Management Solutions Pty Ltd*
>
> Direct: 0400 300 242 | Facsimile: 9547 3132 | PO BOX A2319 SYDNEY
> SOUTH NSW 1235
>
> visit us www.bfms.com.au <http://www.bfms.com.au>
>
> *From:*Thurston Signs [mailto:thurstonsigns at bigpond.com]
> *Sent:* Monday, 8 April 2013 3:31 PM
> *To:* George Ziri
> *Subject:* Thurston Signs
>
> Hi George,
> Please see attached file, 2 stickers, BACK TO BACK.
>
> Kind Regards Lee
>
> On 5/04/2013 4:50 PM, George Ziri wrote:
>
> Hi Lee,
>
> I need a sticker with the txt below. I will be placing on a
> glass sliding door and the text needs to be visible on both
> sides of the door.
>
> WARNING-SLIDING FIRE DOOR
>
> in capital letters not less than 50 mm high in a colour
> contrasting with the
>
> background.
>
> ________________________________________________________
> *George Ziri | Operations*
>
> **
>
> *Building Facilities Management Solutions Pty Ltd*
>
> Direct: 0400 300 242 | Facsimile: 9547 3132 | PO BOX A2319
> SYDNEY SOUTH NSW 1235
>
> visit us www.bfms.com.au <http://www.bfms.com.au>
>
> *From:*NFS Vadim [mailto:vadim at newsound.com.au]
> *Sent:* Friday, 5 April 2013 7:46 AM
> *To:* George Ziri
> *Subject:* RE: 200 WIlliam
>
> Yes sticker is fine as per below dimensions.
>
> Best Regards
>
> Vadim
>
> *From:*George Ziri [mailto:Georgeziri at bfms.com.au]
> *Sent:* Thursday, 4 April 2013 7:55 PM
> *To:* NFS Vadim
> *Subject:* RE: 200 WIlliam
>
> Thanks Vadim.
>
> Can we make a sticker and place it on either side of the door?
>
> ________________________________________________________
> *George Ziri | Operations*
>
> **
>
> *Building Facilities Management Solutions Pty Ltd*
>
> Direct: 0400 300 242 | Facsimile: 9547 3132 | PO BOX A2319
> SYDNEY SOUTH NSW 1235
>
> visit us www.bfms.com.au <http://www.bfms.com.au>
>
> *From:*NFS Vadim [mailto:vadim at newsound.com.au]
> *Sent:* Thursday, 4 April 2013 3:00 PM
> *To:* George Ziri
> *Subject:* 200 WIlliam
>
> Hi George,
>
> Since council is only request for fire safety measure --
> Warning Operational Signs we only need to install sign that
> complies to C3.6
>
> *From BCA:*
>
> signs must be installed on each side of the doorway located
> directly over the
>
> opening stating-
>
> WARNING-SLIDING FIRE DOOR
>
> in capital letters not less than 50 mm high in a colour
> contrasting with the
>
> background.
>
> Are these signs installed on site? If so can you take a photo
> then I can certify the signs. If not we need to install them.
>
> Costs per sign around $120+GST minimum amount to be charged
> $200+GST
>
> Should you have any further questions or queries please do not
> hesitate to contact us.
>
> Regards,
>
> /Vadim Shargorodsky
> /Operations Manager
>
> *Newsound Fire Services Pty Ltd*
> 3 Raymond St East, P.O. Box 249 Lidcombe NSW 2141
>
> *P: (02) 9646 2455
> F: (02) 9749 1059
> M:+61 425 309 741
> **www.newsound.com.au* <http://www.newsound.com.au/>
>
> The information contained in these documents may be privileged
> and confidential and is intended for the exclusive use of the
> addressee designated above. If you are not the addressee, you
> are hereby notified that any disclosure, reproduction,
> distribution, or other dissemination or use of this
> communication is strictly prohibited. If you have received
> this transmission in error, please inform us and destroy the
> original message. The opinions expressed in this
> correspondence are not necessarily those of Newsound Fire
> Services Pty. Ltd.
>
>
>
>
> _______________________________________________
>
> EC mailing list
>
> EC at 200william.com <mailto:EC at 200william.com>
>
> http://200william.com/mailman/listinfo/ec
>
>
>
>
> --
> /* Matt Perkins
> Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
> Fax 1300 133 255 Level 6, 350 George Street Sydney 2000
> SIP1300137379 at sip.spectrum.com.au <mailto:1300137379 at sip.spectrum.com.au>
> PGP/GNUPG Public Key can be found athttp://pgp.mit.edu
> */
--
/* Matt Perkins
Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
Fax 1300 133 255 Level 6, 350 George Street Sydney 2000
SIP 1300137379 at sip.spectrum.com.au
PGP/GNUPG Public Key can be found at http://pgp.mit.edu
*/