Thanks to Leanne for her time today we went through all the issues
surrounding this HVAC issue and how it effects BMC and other building
facilities. I wont bore you with all the details but here are the key
takeaways.
We may be able to pass the owners suggested HVAC with some minor
modifications under the minor renovation rule.
*Noise*.
/The lot owners proposal must be altered to describe the acoustic
insulation used between the outside compressor unit and the balcony
floor / tile/
*Condensate drain
*
/The lot owners proposal must be altered to allow for all waste water
from both the indoor and outdoor units to be plumbed to the existing
legacy HVAC condensate drain and that a pump should be used if such
plumbing was not possible with a gravity feed. No condensate water
should be expelled in any other drain or place. /
*Existing HVAC Plumbing wiring and controllers **
*
The lot owner must agree that the existing HVAC plumbing and wiring
forms part of the building HVAC system under the SMS/BMC and must not be
altered or removed in any way as it will disrupt the buildings existing
HVAC system.
*Removal at cost*
The lot owner must agree to remove and reinstall the outside unit if
requested by the owners corporation at the lot owners expense in the
event the owners corporation needs to paint, renew waterproof membrane
or renew tiles on the balcony attached to the lot.
_Other issues covered as an FYI for the EC._
Any damage to the building waterproofing as result of the install (Minor
renovation) must remedied at the lot owners expense is covered under
existing bylaw.
This clause can not be used by all owners to install a split system as
this specific lot does not have a glass balustrade and as such the
outside unit can not be seen from outside there lot (the street) For
example apartments on the northern side with glass balustrades would not
be eligible as the unit would be visible from outside the lot and as
such it would form a major renovation.
If the owner and the reset of the EC agree to the above we can have a
paper meeting and approve the new owners proposal. If we need to go
through these im happy to have a zoom this week or next if required.
Kind Regards
Matt
On 2021-02-17 11:30, Brook Beves wrote:
>
> I am available with the exception of Thursday evening this week
>
> *From:*ec-bounces at 200william.com [mailto:ec-bounces at 200william.com]
> *On Behalf Of *Leanne Eardley
> *Sent:* Tuesday, 16 February 2021 5:09 PM
> *To:* ec at 200william.com
> *Subject:* Re: [200William-EC SP67851] FW: New Ducted AC at 205/200
> William St Woolloomooloo
>
> Good Afternoon Committee,
>
> The Managing agent has followed me up with regards to an outcome
> today. Would you be happy for me to arrange a
> teleconference/videoconference committee meeting in order to discuss
> and consider this application further so that everyone is on the same
> page?
>
> The installation of a reverse cycle split system air conditioner is
> considered a minor renovation as long as it doesn’t involve structural
> changes, or change the external appearance of a lot (special by-law 6).
>
> Any renovation approvals (especially minor renovations approvals) are
> submitted a letter that stipulates terms and conditions of approval,
> of which the Owner is requested to sign and return prior to the works
> commencing.
>
> Kind Regards,
>
> *Leanne Eardley*
>
> Senior Community Manager
>
> A close up of a logo Description automatically generated
>
>
>
> *t.*(02) 9266 2600
> *d.* (02) 9266 2648
> *e.* leardley at stratatitle.com.au <mailto:leardley at stratatitle.com.au>
> *a.* Suite 2, Level 4, 1 Chandos Street, St Leonards NSW 2065
>
> <https://smartercommunities.com.au/covid-19/>
>
> <https://issuu.com/smartercommunities/docs/0419_scmagazine_4th_edition_final_issuu>
>
> DISCLAIMER: Strata Title Management takes no responsibility for
> content included in this email when relating to a client matter.
> Please view Smarter Communities’ full email communication disclaimer
> smartercommunities.com.au/disclaimer
> <https://smartercommunities.com.au/disclaimer/>
>
> *From:*ec-bounces at 200william.com <mailto:ec-bounces at 200william.com>
> <ec-bounces at 200william.com <mailto:ec-bounces at 200william.com>> *On
> Behalf Of *Edward Sainsbury
> *Sent:* Tuesday, 2 February 2021 10:12 PM
> *To:* Matt Perkins <matt at spectrum.com.au
> <mailto:matt at spectrum.com.au>>; Craig Laforest <cscl at optusnet.com.au
> <mailto:cscl at optusnet.com.au>>; ec at 200william.com
> <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] FW: New Ducted AC at 205/200
> William St Woolloomooloo
>
> *WARNING. This email was received from an external sender. You should
> verify the email address before processing the email.*
>
> Hi EC,
>
> Thanks for the comments. I would like to be balanced to ensure the
> unit can be air conditioned. I do not know the reasons why the
> internal existing A/C unit can not be repaired. Can someone help me
> understand those constraints.
>
> I think the noise issue would be OK, but the adjacent units should
> have a say.
>
> I would be concerned about water dripping. External units need a place
> to expel water, where would this go in relation to this Unit?
>
> From an aesthetic point of view, if the unit was visible from the
> street, I would not be in favour.
>
> The exclusive use requiring an EGM would need to be addressed.
>
> I believe that the unit would need to sign a deed to be responsible
> for any leaks connected to water ingress from the holes cut in the
> main walls and any water damage caused by the unit itself.
>
> Regards,
>
> Ed
>
> Get Outlook for Android <https://aka.ms/ghei36>
>
> ------------------------------------------------------------------------
>
> *From:*ec-bounces at 200william.com <mailto:ec-bounces at 200william.com>
> <ec-bounces at 200william.com <mailto:ec-bounces at 200william.com>> on
> behalf of Matt Perkins <matt at spectrum.com.au
> <mailto:matt at spectrum.com.au>>
> *Sent:* Tuesday, February 2, 2021 7:32:58 PM
> *To:* Craig Laforest <cscl at optusnet.com.au
> <mailto:cscl at optusnet.com.au>>; ec at 200william.com
> <mailto:ec at 200william.com> <ec at 200william.com <mailto:ec at 200william.com>>
> *Subject:* Re: [200William-EC SP67851] FW: New Ducted AC at 205/200
> William St Woolloomooloo
>
> Respectfully Craig i disagree. But im happy to go with the consensus.
>
> Matt
>
> On 2/2/21 7:29 pm, Craig Laforest wrote:
>
> Hello Matt and everyone,
>
> I am one of the people who can speak openly about the problems of
> effective air-conditioning in an apartment – mine. I have spent
> thousands of dollars, as Matt mentioned, to try and get
> air-conditioning which ‘works’ in all options of cool vs heating.
> To no avail. With my A/C on, I still have a very hot apartment
> during the summer.
>
> We are NOT a deluxe, ‘luxury’ building. A building which IS
> deluxe and luxury has a Concierge and pool and sizeable gym and a
> building manager, who is constantly looking at even the smallest
> of problems in the building and acts immediately. Ours doesn’t
> any of these.
>
> No one is going to look up at an air-conditioning unit on one of
> our balconies (even if they can see it) and consider the building
> ‘ugly.’ People need to be kept cool during the hot summer and as
> we are not getting effective A/C cooling from the tower on level
> 8, then we need to look at alternatives for them.
>
> Please, let’s make this simple. This owner wants A/C so that they
> or the tenant can enjoy the apartment. Yes, it may mean a
> compressor is installed on the balcony, however they are extremely
> quiet and as a non-deluxe, non-luxury building, we are NOT in a
> quiet area anyway!
>
> Please consider we have more membrane concerns (level 7 west)
> than a quiet compressor for A/C on any balcony. Dripping water
> on a balcony? Consider again that with rain or humidity the
> balcony will have water on it, at some point, anyway. In that
> situation, the membrane is the question, not water flow.
>
> Can the members of the Body Corporate please come together and get
> this request passed so that the owner/tenant can enjoy their home
> with the A/C they are requesting.
>
> Regards,
>
> Craig Laforest
>
> *From:*ec-bounces at 200william.com
> <mailto:ec-bounces at 200william.com> <ec-bounces at 200william.com>
> <mailto:ec-bounces at 200william.com> *On Behalf Of *Matt Perkins
> *Sent:* Tuesday, 2 February 2021 4:13 PM
> *To:* ec at 200william.com <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] FW: New Ducted AC at
> 205/200 William St Woolloomooloo
>
> I feel like I have been through this 100 times. But hear we go again.
>
> The balcony is common property. An exclusive use bylaw would be
> required by EGM to allow a split system aircon to be installed.
> (EC cant approve)
>
> The building has a cooling tower and as such was designed with a
> cooling tower recirculating water system HVAC with _internal_
> apartment compressor (not external as they note bellow so not the
> same as indicated)
>
> The building waste condensate water is piped from inside the
> apartment directly into internal drains not onto balconys some
> balconies do drain onto others. Unless their aircon guy has looked
> at the Hydraulic plans of the building he would have no idea where
> it drains to.
>
> Dripping water onto balcony may cause leaks in the future.
>
> Vibrations of compressors on the balcony may cause leaks in the
> future and complicate membrane repairs on balcony in the future if
> needed.
>
> Running gas piping between the external compressor and the
> internal fan unit will require penetration between inside and
> outside by removing bricks drilling holes etc. A future area for
> water ingress.
>
> Noise generated by an external compressor (opposed to one inside
> the apartment as it is now) may be transmitted to lower floors.
>
> We do not have council approval in our original D/A for external
> compressors.
>
> External air con units are ugly and not in keeping with the look
> of the building.
>
> Once we have approved one unit a precedent will be set and they
> will appear on all other apartments.
>
> Costs of GAS and Electricity in the BMC are split by the SMS
> taking into account that all apartments use the common use aircon.
> Will this owner demand a strata plan of sub division to change
> there entitlement units as they dont use building HVAC ?
>
> I feel for the owner with costs involved but to be fair we are all
> in the same boat. If you look around the area there are almost no
> external aircon units on balcony's of like buildings. External
> units are common place in less prestige buildings sure But we are
> trying to keep the image of the building high.
>
> Many other owners have replaced their air con units at great cost
> and worked within the rules I know I have 601 has and 401 has
> likely there are more. Elan, Zenith, Horizon, Omnia all have
> cooling tower systems and not external air cons banging away into
> the hot summer night dripping water everywhere. Almost every
> building that was constructed after 2000 in this area does. It's
> not an Auburn 1980's tower block with an aircon out every balcony.
>
> That's my 2c im sure i could go on but you get the picture this is
> a very bad idea and will bite us in the backside one day.
>
> Matt
>
> On 2/2/21 2:53 pm, Leanne Eardley wrote:
>
> Good Afternoon Committee,
>
> The managing agent of unit 205 has been in contact with the
> recommended a/c contractor that services the building (city to
> surf air), and advised that the proposed cost of $10k is not
> an option for the Owner.
>
> As such, they would like the committee to reconsider their a/c
> application for the split system installation, copy attached.
> They have also advised the following:
>
> /Lot 17 balcony is in line with the balcony below & above./
>
> /The balcony is designed as an external area, tiles with a
> floor waste for water next to the compressor location so the
> pipe will run into it not “drip off the balcony”./
>
> /Compressor noise from the Ducted System is no different to a
> Split System compressor. Both use a compressor./
>
> Please review and discuss, this decision will need to be
> documented by way of a formal committee meeting, so if you
> would like me to arrange an online voting committee meeting,
> or a teleconference to discuss and make determination, please
> let me know.
>
> Kind Regards,
>
> *Leanne Eardley*
>
> Senior Community Manager
>
> A close up of a logo Description automatically generated
>
>
>
> *t.*(02) 9266 2600
> *d.* (02) 9266 2648
> *e.* leardley at stratatitle.com.au
> <mailto:leardley at stratatitle.com.au>
> *a.* Suite 2, Level 4, 1 Chandos Street, St Leonards NSW 2065
>
> <https://smartercommunities.com.au/covid-19/>
>
> <https://issuu.com/smartercommunities/docs/0419_scmagazine_4th_edition_final_issuu>
>
> DISCLAIMER: Strata Title Management takes no responsibility
> for content included in this email when relating to a client
> matter.
> Please view Smarter Communities’ full email communication
> disclaimer smartercommunities.com.au/disclaimer
> <https://smartercommunities.com.au/disclaimer/>
>
> *From:*Regal Court Real Estate <general at regalcourt.com.au>
> <mailto:general at regalcourt.com.au>
> *Sent:* Friday, 29 January 2021 2:37 PM
> *To:* Deborah O'Brien <dobrien at stratatitle.com.au>
> <mailto:dobrien at stratatitle.com.au>
> *Cc:* Leanne Eardley <leardley at stratatitle.com.au>
> <mailto:leardley at stratatitle.com.au>
> *Subject:* FW: New Ducted AC at 205/200 William St Woolloomooloo
>
> *WARNING. This email was received from an external sender. You
> should verify the email address before processing the email.*
>
> Dear Deborah,
>
> We have received the email below from the recommended air
> conditioning company. The cost of $10K+ is not an option for
> the owner, especially under the current economic climate with
> COVID-19. The owner has already suffered financial loss due to
> being unable to lease an un-air condition apartment.
>
> The split system that was previously detailed we have had
> installed in many strata buildings with no issues and should
> any arise we would take action to rectify. Could you please
> discuss this with the committee as we now have a tenant who
> needs air conditioning.
>
> Kind Regards
>
> Lili Brzevska
>
> *_Regal Court Real Estate_*
>
> P: 02 9764 6902
>
> *E: *general at regalcourt.com.au <mailto:general at regalcourt.com.au>
>
> A: 142/20-34 Albert Road, Strathfield NSW 2135
>
> The information contained in this email message and any
> accompanying files is or may be confidential. If you are not
> the intended recipient, any use, dissemination, reliance,
> forwarding, printing or copying of this email or any attached
> files is unauthorised. This email is subject to copyright. No
> part of it should be reproduced, adapted or communicated
> without the written consent of the copyright owner. If you
> have received this email in error please advise the sender
> immediately by return email or telephone and delete all
> copies. Regal Court Real Estate does not guarantee the
> accuracy or completeness of any information contained in this
> email or attached files. Internet communications are not
> secure, therefore Regal Court Real Estate does not accept
> legal responsibility for the contents of this message or
> attached files.
>
> *From:*Service City to Surf Air <service at citytosurfair.com.au
> <mailto:service at citytosurfair.com.au>>
> *Sent:* Monday, 25 January 2021 9:06 AM
> *To:* Regal Court Real Estate <general at regalcourt.com.au
> <mailto:general at regalcourt.com.au>>
> *Subject:* Re: New Ducted AC at 205/200 William St Woolloomooloo
>
> Hi Tino,
>
> These a/c units are no longer in production.
>
> A custom made unit will need to be manufactured which has a
> lead time of around 8 weeks.
>
> An estimated cost for supply and installation would be $10K -
> $12K.
>
> If the owner is interested then we can attend site to take the
> required measurements.
>
> If the owner wishes to discuss the situation, please forward
> on my number.
>
> Thank you,
>
> Brendan
>
> Kind Regards,
>
> The Service Team
>
> service at citytosurfair.com.au
> <mailto:accounts at citytosurfair.com.au>
>
> www.citytosurfair.com.au <http://www.citytosurfair.com.au/>
>
> 02 93497956
>
> Image removed by sender.
>
> On Thu, Jan 21, 2021 at 12:24 PM Regal Court Real Estate
> <general at regalcourt.com.au <mailto:general at regalcourt.com.au>>
> wrote:
>
> Good afternoon
>
> We were given your details by strata at 200 William St
> Woolloomooloo as you’ve worked there before.
>
> They are an old model Temperzone ducted system with very
> narrow access.
>
> It’s been removed by someone long ago so a repair isn’t
> possible.
>
> Please quote for a new installation in unit 205.
>
> It’s vacant at the moment so easy access anytime just call
> Tino on 0414 598 973.
>
> Urgently as we have a new tenant moving in soon.
>
> Kind Regards
>
> Tino Brzevski
>
> *_Regal Court Real Estate_*
>
> P: 02 9764 6902
>
> *E: *general at regalcourt.com.au
> <mailto:general at regalcourt.com.au>
>
> A: 142/20-34 Albert Road, Strathfield NSW 2135
>
> The information contained in this email message and any
> accompanying files is or may be confidential. If you are
> not the intended recipient, any use, dissemination,
> reliance, forwarding, printing or copying of this email or
> any attached files is unauthorised. This email is subject
> to copyright. No part of it should be reproduced, adapted
> or communicated without the written consent of the
> copyright owner. If you have received this email in error
> please advise the sender immediately by return email or
> telephone and delete all copies. Regal Court Real Estate
> does not guarantee the accuracy or completeness of any
> information contained in this email or attached files.
> Internet communications are not secure, therefore Regal
> Court Real Estate does not accept legal responsibility for
> the contents of this message or attached files.
>
> _______________________________________________
>
> EC mailing list
>
> EC at 200william.com <mailto:EC at 200william.com>
>
> http://200william.com/mailman/listinfo/ec
>
> --
>
> /* Matt Perkins
>
> Direct 02 8916 8101 Spectrum Networks Ptd. Ltd.
>
> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
>
> ABN 66 090 112 913 Level 6, 350 George Street Sydney 2000
>
> */
>
> --
> /* Matt Perkins
> Direct 02 8916 8101 Spectrum Networks Ptd. Ltd.
> Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>
> ABN 66 090 112 913 Level 6, 350 George Street Sydney 2000
> */
>
> _______________________________________________
> EC mailing list
> EC at 200william.com
> http://200william.com/mailman/listinfo/ec
--
/* Matt Perkins
Direct 02 8916 8101 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
ABN 66 090 112 913 Level 6, 350 George Street Sydney 2000
*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 7860 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0006.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 11747 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0007.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 41109 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0008.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 10687 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0009.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 7870 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0010.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 41108 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0011.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 425 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20210217/90ed45d7/attachment-0001.jpg
More information about the EC
mailing list