  1.  The foam insulation is not required on Unit 601’s side of the rectification work as the terrace above Unit 601 is not being rectified, only the podium and planter boxes. It was only agreed to do this amount of rectification work above Unit 601. This confirms your attached point Ken!



  1.  At this stage the builder doesn’t believe there should be any further variations but cannot 100% confirm this. This is the reason the builder has been waiting on approval of this final variation before they recommence the rectification work.

If there are no further comments or questions before 1:00pm Tuesday 31st October 2017, I will approve the final variation and ask for a recommencement date of the required Level 7 rectification.


Kind regards,
Patrick Rush
Senior Community Manager

Phone: (02) 9266 2600 | Direct Phone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

[BSC_STM_logo_4c]    [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture’s full email communication disclaimer on our website – www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf Of Matt Perkins
Sent: Monday, 30 October 2017 12:07 PM
To: ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Approval of Additional Insulation Variation on Podium and Planter Box Waterproofing

Sorry to put this in two emails. Also Patrick do we have any choice with not fitting insulation at all on 602 as it's existing dont we need to have a special resolution to change it.  If that's the case the only real question is do we do same on 601. Am i reading this situation correctly.

Matt.


On 30/10/17 12:00 pm, Matt Perkins wrote:
Patrick. Have you sent the cost for the work on both sides. I only think i saw the cost for 602.

Matt


On 30/10/17 11:58 am, Patrick Rush wrote:
Dear Committee,

As there is some ambiguity in the below email responses, can I please ask for each Committee Member to respond yes or not the below request –


  1.  Please confirm approval for both sides to have the foam installed at the cost of the Owners Corporation?


I understand that some Committee Members are of the belief that Preservation Technologies should absorb the cost but I have confirmed with Strata Engineering Solutions that this will, not be the  case and until a decision is provided on the above question work will not recommence.

Please provide an urgent response to the above query?


Kind regards,
Patrick Rush
Senior Community Manager

Phone: (02) 9266 2600 | DirectPhone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

[BSC_STM_logo_4c]    [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture’s full email communication disclaimer on our website –www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com] On Behalf Of Craig Laforest
Sent: Friday, 27 October 2017 3:13 PM
To: 'Matt Perkins' <matt at spectrum.com.au><mailto:matt at spectrum.com.au>; 'Ken West' <ennvvest at gmail.com><mailto:ennvvest at gmail.com>; 'Robin Patrick' <robin.j.patrick at gmail.com><mailto:robin.j.patrick at gmail.com>
Cc: ec at 200william.com<mailto:ec at 200william.com>; 'John Burney' <john.burney at humanchemistry.com><mailto:john.burney at humanchemistry.com>
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Approval of Additional Insulation Variation on Podium and Planter Box Waterproofing


Dear Patrick,

Please proceed to get Preservation Technologies to recommence the works as soon as possible and advise a date when they will start. After last night’s downpour I have continual water dripping through from level 7 onto my terrace.

The foam is a moot point.  When each company was asked to provide us with a quote they each allowed a contingency for on the spot additional items.  They could not have possibly known what was under the tiles.  They were not asked to pull up a tile to determine this.

I would advise the EC that this matter has dragged on again too long and I have no hesitation in going back to the Tribunal asap to get the works completed.  This time the Tribunal will frown on a third order having to be raised to have the works completed. In addition, the EC will receive an enormous fine.

Craig Laforest


From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com] On Behalf Of Matt Perkins
Sent: Friday, 27 October 2017 1:25 PM
To: Ken West; Robin Patrick
Cc: ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Approval of Additional Insulation Variation on Podium and Planter Box Waterproofing

Agreed Ken.

Matt


On 27/10/17 1:22 pm, Ken West wrote:
Hi all,

Sorry for the delay. Just back from Melbourne.

I have checked the roof and it seems to be draining well after the big storm overnight, so thats good news.

After new inspection the foam will be needed as they need to match both sides and the height issues are obvious.

However, they quoted for the job and should have known that the insulation was there in the first place so they should absorb that cost.

Additionally they knew this 3 months ago when they pulled up the tiles and didn’t bring it up then so not impressed.

It is crazy that no work at all is being done still with no start or end in sight.

I hope they are not being paid in advance as they seen to not care about completing this job.

In short lets get this done and finished.

Regards,

Ken and Cathy
On 24 Oct 2017, at 4:46 PM, Robin Patrick <robin.j.patrick at gmail.com<mailto:robin.j.patrick at gmail.com>> wrote:

Agreed as per Mat's email.

On Tue, Oct 24, 2017 at 4:41 PM, Matt Perkins <matt at spectrum.com.au<mailto:matt at spectrum.com.au>> wrote:
Hi Patrick/All
 That's a lot of info thanks.  Here's my comments/votes on the bellow.

1. I think it would be best to make both 601 & 602 the same as they seem to be effected by the same issues. To that end I would like to at least see the quote for both.

2. Given that the BBQ area must be stay or special resolution passed. I think best to leave to we are finished and then get a quote to put some rubber seals on the doors and a lock so it can not be opened. There is nothing in that area that BBQ users need to access.  I know some would like the BBQ removed. But as that is not in the EC's power lets leave that debate for the appropriate time.

3. I will leave Cathy and Ken to comment on the break down.

Matt.


On 24/10/17 4:26 pm, Patrick Rush wrote:
Dear Committee,


  1.  I have been provided with the attached report, which includes 1 further variation for the installation of insulation above Unit 602.


I believe this variation requires approval as Unit 602 had such insulation and the Owners Corporation are required to repair and amanitin the current common property, being the insulation, with the details and the cost below –


The variation cost to supply and install Kingspan XPS N 300 Insulation (50mm) to terrace area only above unit 602 would be $5200 <tel:+445200> + GST.


This was not initially included in the initial scope as we were not aware there was insulation under the tiles. Re-installing insulation above unit 602 is recommended to control the internal temperature.


Since the podium and steps previously did not have any insulation we will not be placing insulation on those areas. Therefore the quote above is only for the terrace area above unit 602.


Please approve the above variation so that Preservation Technologies can recommence the rectification and complete this prior to the Christmas break?


Please also advise if you would like such insulation installed above unit 601 and I can obtain a quote for this variation?



  1.  See the below comments in relation to works that will be required to seal the BBQ area, that I can request a quote from Preservation Technologies, Please advise if you would like Preservation Technologies to quote on this as well as cleaning the blocked drainage on the Terrace which is requiem or would you like Darren to organise?


The doors below the BBQ is of concern as they do not seal adequately, which could let water into the enclosed cabinets under the BBQ, photos attached. >From my site inspections we do not believe this a pressing issue, as we are unsure if water enters the area under the BBQ during rain events.


The SC could consider;

Install seals around the door – Can be included as a variation by Prestech or through engagement of another contractor after the completion of this work (recommended)

Screed area to create a fall to a drainage point and waterproof the internal of the BBQ area


As previously discussed, the SC also need to consider cleaning the blocked drainage on the terrace.



  1.  Finally, please see the breakdown of cost and materials for the waterproofing of the terraces above both Unit 601 & 5602 that was requested at the AGM for your information. No action on this matter is required!


<image010.png>Breakdown of which is as follows;

<image011.png>




Kind regards,
Patrick Rush
Senior Community Manager

Phone: (02) 9266 2600 | DirectPhone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

<image001.jpg>    <image002.png><http://www.facebook.com/StrataTitleManagement>    <image003.png> <http://www.linkedin.com/company/strata-title-management-stm>    <image004.png><http://www.twitter.com/STMStrata>    <image005.png><http://www.pinterest.com/STMStrata>    <image006.png><http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture’s full email communication disclaimer on our website –www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.






_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec


--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/

_______________________________________________
EC mailing list
EC at 200william.com<mailto:EC at 200william.com>
http://200william.com/mailman/listinfo/ec

_______________________________________________
EC mailing list
EC at 200william.com<mailto:EC at 200william.com>
http://200william.com/mailman/listinfo/ec




--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/




_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec



--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/




_______________________________________________

EC mailing list

EC at 200william.com<mailto:EC at 200william.com>

http://200william.com/mailman/listinfo/ec



--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0001.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3125 bytes
Desc: image001.jpg
Url : http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0001.jpg 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 4236 bytes
Desc: image002.png
Url : http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0005.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3977 bytes
Desc: image003.png
Url : http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0006.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 4502 bytes
Desc: image004.png
Url : http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0007.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1488 bytes
Desc: image005.png
Url : http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0008.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1725 bytes
Desc: image006.png
Url : http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0009.png 
-------------- next part --------------
An embedded message was scrubbed...
From: Craig Laforest <cscl at optusnet.com.au>
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Approval of
	Additional Insulation Variation on Podium and Planter Box	Waterproofing
Date: Mon, 30 Oct 2017 01:09:39 +0000
Size: 115472
Url: http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0002.mht 
-------------- next part --------------
An embedded message was scrubbed...
From: Ken West <ennvvest at gmail.com>
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Approval of
 Additional Insulation Variation on Podium and Planter Box Waterproofing
Date: Mon, 30 Oct 2017 01:26:32 +0000
Size: 102602
Url: http://200william.com/mailman/private/ec/attachments/20171030/a415c5fc/attachment-0003.mht 


More information about the EC mailing list