I assume the verdict on this one is a yes. My intent is to vote for the 
engineers recommendation on monday unless I hear otherwise.

Have a good weekend.
Matt

On 28/6/17 11:15 am, Craig Laforest wrote:
>
> Hello Patrick,
>
> Fair enough.  Thanks.
>
> *From:*ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] 
> *On Behalf Of *Patrick Rush
> *Sent:* Wednesday, 28 June 2017 11:03 AM
> *To:* ec at 200william.com
> *Subject:* Re: [200William-EC SP67851] DP 1040255 - Reinstatement of 
> the Correct Operation of Storm Water & Sewer Systems for Approval
>
> Hi Craig,
>
>
> I cannot make a recommendation as am not the Engineer that undertook 
> the inspection, provided the report and reviewed the tenders.
>
>
> AJ Whipps Consulting has provided their recommendation of Rescom 
> Builders from the 3 tenders.
>
> Kind regards,
>
> *Patrick Rush*
>
> Senior Strata Manager
>
> Phone:(02) 9266 2600 |DirectPhone:(02) 9266 2695 | 
> Email:prush at stratatitle.com.au 
> <mailto:northshore at stratatitle.com.au> | Address:PO Box 2727, Taren 
> Point, NSW 2229
>
> **
>
> BSC_STM_logo_4c cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box 
> <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box 
> <http://www.twitter.com/STMStrata>pinterest.png 
> <http://www.pinterest.com/STMStrata>google_plus.png 
> <http://plus.google.com/+StrataTitleManagemenSydney>
>
> **
>
> *Emailed Communication / Documents Disclaimer*
>
> STM Limited takes no responsibility for content included in this email 
> when relating to a client matter.
>
> Please view Vesture’s full email communication disclaimer on our 
> website –www.stratatitle.com.au/disclaimer/ 
> <http://www.stratatitle.com.au/disclaimer/>
>
> *Important Notice: *Owners should be aware that all correspondence, 
> including letters, facsimile transmissions and emails are retained on 
> the file of your scheme and may be subject to inspection by owners and 
> residents within your scheme, as well as prospective purchasers for 
> any lot that may be for sale within your scheme. As such author 
> discretion is advised.
>
> *From:*ec-bounces at 200william.com <mailto:ec-bounces at 200william.com> 
> [mailto:ec-bounces at 200william.com] 
> <mailto:[mailto:ec-bounces at 200william.com]> *On Behalf Of *Craig Laforest
> *Sent:* Wednesday, 28 June 2017 10:57 AM
> *To:* 'Matt Perkins' <matt at spectrum.com.au 
> <mailto:matt at spectrum.com.au>>; ec at 200william.com 
> <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] DP 1040255 - Reinstatement of 
> the Correct Operation of Storm Water & Sewer Systems for Approval
>
> To the EC members:
>
> I have read through the proposals by each of the contractors. The 
> charges are different for each of the main expenses (e.g. A3 – where 
> there is quite a difference).
>
> However, as it is urgent to move forward may I ask you Patrick for 
> your recommendation on which contractor should be used for these 
> works.  If anyone would like to discuss this matter further, please 
> just let me know.  As outlined by Matt, this problem has gone on for 
> too long.
>
> I look forward to hearing responses from other EC members.
>
> Regards,
> Craig Laforest
>
> *From:*ec-bounces at 200william.com <mailto:ec-bounces at 200william.com> 
> [mailto:ec-bounces at 200william.com] *On Behalf Of *Matt Perkins
> *Sent:* Wednesday, 28 June 2017 10:33 AM
> *To:* ec at 200william.com <mailto:ec at 200william.com>
> *Subject:* Re: [200William-EC SP67851] DP 1040255 - Reinstatement of 
> the Correct Operation of Storm Water & Sewer Systems for Approval
>
> That's good news at least. I believe that we have no choice but to go 
> ahead with the engineers recommendation . If everyone else can agree I 
> can make that position known to the BMC.
>
> This has been going on so long with two car spaces and storage cages 
> (peoples property) being unusable. I think both effected parties have 
> been  extremely patient with the process.
>
> Also Avis's car wash is still spewing water into the P4 car park 
> through a garden house.  Patrick can you ask that they do as per the 
> engineers request and get a plumber to plumb it professionally into a 
> drain.
>
> Matt.
>
>
>
>
> On 28/6/17 10:16 am, Patrick Rush wrote:
>
>     Hi Matt,
>
>     The BMC will have more than $220,000.00 as of 15^th July 2017,
>     when both Members will b update with their levy payments, so there
>     shouldn’t be a need for any further special levy.
>
>     See attached BMC DP 1040255’s financial statements.
>
>     Kind regards,
>
>     *Patrick Rush*
>
>     Senior Strata Manager
>
>     Phone:(02) 9266 2600 |DirectPhone:(02) 9266 2695 |
>     Email:prush at stratatitle.com.au
>     <mailto:northshore at stratatitle.com.au> | Address:PO Box 2727,
>     Taren Point, NSW 2229
>
>     **
>
>     BSC_STM_logo_4c cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
>     <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
>     <http://www.twitter.com/STMStrata>pinterest.png
>     <http://www.pinterest.com/STMStrata>google_plus.png
>     <http://plus.google.com/+StrataTitleManagemenSydney>
>
>     **
>
>     *Emailed Communication / Documents Disclaimer*
>
>     STM Limited takes no responsibility for content included in this
>     email when relating to a client matter.
>
>     Please view Vesture’s full email communication disclaimer on our
>     website –www.stratatitle.com.au/disclaimer/
>     <http://www.stratatitle.com.au/disclaimer/>
>
>     *Important Notice: *Owners should be aware that all
>     correspondence, including letters, facsimile transmissions and
>     emails are retained on the file of your scheme and may be subject
>     to inspection by owners and residents within your scheme, as well
>     as prospective purchasers for any lot that may be for sale within
>     your scheme. As such author discretion is advised.
>
>     *From:*ec-bounces at 200william.com
>     <mailto:ec-bounces at 200william.com>
>     [mailto:ec-bounces at 200william.com] *On Behalf Of *Matt Perkins
>     *Sent:* Tuesday, 27 June 2017 6:27 PM
>     *To:* ec at 200william.com <mailto:ec at 200william.com>
>     *Subject:* [200William-EC SP67851] Fwd: DP 1040255 - Reinstatement
>     of the Correct Operation of Storm Water & Sewer Systems for Approval
>
>     Hi All,
>
>       As i suspected the sewer works are quite substantial. Remember 
>     that 20% of this cost will be born by the Commercial strata.
>     Patrick could you comment as to the state of the budget and i
>     assume what will be another Special Levy.
>
>     I have also asked Darren to get a megasealed quote for the leak on
>     balcony 402 which is flooding the bedroom in vlan 302. As its very
>     unlikely there will be any money to fix it permanently at the moment.
>
>     Matt.
>
>
>
>     -------- Forwarded Message --------
>
>     *Subject: *
>
>     	
>
>     DP 1040255 - Reinstatement of the Correct Operation of Storm Water
>     & Sewer Systems for Approval
>
>     *Date: *
>
>     	
>
>     Tue, 27 Jun 2017 08:00:35 +0000
>
>     *From: *
>
>     	
>
>     Patrick Rush <prush at stratatitle.com.au>
>     <mailto:prush at stratatitle.com.au>
>
>     *To: *
>
>     	
>
>     Matt Perkins <matt at spectrum.com.au> <mailto:matt at spectrum.com.au>,
>     'Andrew Veron' <av at charlesstuart.com.au>
>     <mailto:av at charlesstuart.com.au>
>
>     *CC: *
>
>     	
>
>     Ben Mees <ben.mees at bmaus.com.au> <mailto:ben.mees at bmaus.com.au>,
>     Darren Vignes <marquis at bfms.com.au> <mailto:marquis at bfms.com.au>,
>     'Marquis' <marquis at bmaus.com.au> <mailto:marquis at bmaus.com.au>,
>     ec at 200william.com <mailto:ec at 200william.com> <ec at 200william.com>
>     <mailto:ec at 200william.com>
>
>
>
>     Dear BMC Representatives,
>
>     Please see attached the tender documentation and recommendation
>     for the reinstatement of the correct operation of storm water and
>     sewer systems for your consideration.
>
>
>     Below is the table in the etched on page 1, with the
>     recommendation by AJ Whipps Consulting Group on Page 2 for ease of
>     viewing –
>
>     *Contractor*
>
>     	
>
>     *Cost (+ GST)*
>
>     Rescom Builders  Pty Ltd
>
>     	
>
>     $60,518.40
>
>     Hitech Remedial Pty Ltd
>
>     	
>
>     $72,880.00
>
>     Buildcore Constructions
>
>     	
>
>     $81,895.00
>
>     Can you please review the above and contact the Committee Members
>     from the relevant Owners Corporations and advise a decision on if
>     you are happy to proceed with AJ Whipps Group’s recommendation of
>     Rescom Builders? Can you also confirm you are happy to proceed
>     with the contract and administration and supervision of the work
>     by AJ Whipps Consulting Group?
>
>
>     Once an agreement is made, I will send out an agenda to confirm
>     the agreement and then proceed with the necessary work?
>
>     Kind regards,
>
>     *Patrick Rush*
>
>     Senior Strata Manager
>
>     Phone:(02) 9266 2600 |DirectPhone:(02) 9266 2695 |
>     Email:prush at stratatitle.com.au
>     <mailto:northshore at stratatitle.com.au> | Address:PO Box 2727,
>     Taren Point, NSW 2229
>
>     **
>
>     BSC_STM_logo_4c cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
>     <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
>     <http://www.twitter.com/STMStrata>pinterest.png
>     <http://www.pinterest.com/STMStrata>google_plus.png
>     <http://plus.google.com/+StrataTitleManagemenSydney>
>
>     **
>
>     *Emailed Communication / Documents Disclaimer*
>
>     STM Limited takes no responsibility for content included in this
>     email when relating to a client matter.
>
>     Please view Vesture’s full email communication disclaimer on our
>     website –www.stratatitle.com.au/disclaimer/
>     <http://www.stratatitle.com.au/disclaimer/>
>
>     *Important Notice: *Owners should be aware that all
>     correspondence, including letters, facsimile transmissions and
>     emails are retained on the file of your scheme and may be subject
>     to inspection by owners and residents within your scheme, as well
>     as prospective purchasers for any lot that may be for sale within
>     your scheme. As such author discretion is advised.
>
>     *From:*Behrang Dehestani [mailto:bdehestani at ajwhipps.com.au]
>     *Sent:* Friday, 16 June 2017 8:50 AM
>     *To:* Patrick Rush <prush at stratatitle.com.au>
>     <mailto:prush at stratatitle.com.au>; Raeleen Marsh
>     <rmarsh at stratatitle.com.au> <mailto:rmarsh at stratatitle.com.au>
>     *Cc:* Jess Heaton <jheaton at ajwhipps.com.au>
>     <mailto:jheaton at ajwhipps.com.au>; 'Marquis' <Marquis at bfms.com.au>
>     <mailto:Marquis at bfms.com.au>
>     *Subject:* RE: DP 1040255 - WO
>
>     Hi Patrick,
>
>     Please see attached tender review for 200 William Street,
>     Woolloomooloo.
>
>
>     I recommend that we arrange a time to meet with the recommended
>     contractor, building management and any Owners committee members
>     to discuss the particulars prior to preparing contracts. This work
>     will be charged at 4 hours.
>
>     Further to this, we require a work order approval for Stage 2
>     (construction) of AJ Whipps fee dated 31 March 2017. This will
>     permit us to supervise and project co-ordinate the works.
>
>     Look forward to delivering a successful project.
>
>     Regards,
>
>     *Behrang Dehestani *
>     Senior Remedial Project Engineer
>     Forensic Analysis Remedial Engineering
>
>     *AJ Whipps Consulting Group*
>     2/101 Union Street
>     McMahons Point, NSW 2060
>     *t*    02 8923 8444*
>     **f*    02 8923 8484
>     *e*bdehestani at ajwhipps.com.au
>     <mailto:bdehestani at ajwhipps.com.au%0b>
>     www.ajwhipps.com.au <http://ajwhipps.com.au/>
>
>     	
>
>     http://ajwhipps.com.au/wp-content/uploads/Whipps_Logo_Portrait_Tag.gif
>
>     http://ajwhipps.com.au/wp-content/uploads/whipps_linkedin.png
>     <http://www.linkedin.com/company/aj-whipps-consulting-group>http://ajwhipps.com.au/wp-content/uploads/whipps_facebook.png
>     <https://www.facebook.com/ajwhipps>http://ajwhipps.com.au/wp-content/uploads/whipps_instagram.png
>     <http://instagram.com/aj_whipps_consulting_group>
>
>     This electronic mail is solely for the use of the addressee and
>     may contain information which is confidential. Unauthorized use of
>     any information contained in this email is strictly prohibited. If
>     you receive this electronic mail in error, please delete it from
>     your system immediately and notify the sender by electronic mail
>     or using any of the above contact details.
>
>     _______________________________________________
>
>     EC mailing list
>
>     EC at 200william.com <mailto:EC at 200william.com>
>
>     http://200william.com/mailman/listinfo/ec
>
> -- 
> /* Matt Perkins
>          Direct 1300 137 379        Spectrum Networks Ptd. Ltd.
>          Office 1300 133 299matt at spectrum.com.au <mailto:matt at spectrum.com.au>  
>                                     Level 6, 350 George Street Sydney 2000
>          Spectrum Networks is a member of the Communications Alliance & TIO
> */
>
>
> _______________________________________________
> EC mailing list
> EC at 200william.com
> http://200william.com/mailman/listinfo/ec


-- 
/* Matt Perkins
         Direct 1300 137 379        Spectrum Networks Ptd. Ltd.
         Office 1300 133 299        matt at spectrum.com.au
                                    Level 6, 350 George Street Sydney 2000
         Spectrum Networks is a member of the Communications Alliance & TIO
*/

-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0001.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3125 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0001.jpg 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 4236 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0009.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3977 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0010.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 4502 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0011.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1488 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0012.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1725 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0013.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 7103 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0014.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 494 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0015.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 402 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0016.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 585 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20170630/a1e412a6/attachment-0017.png 


More information about the EC mailing list