[200William-EC SP67851] FW: SP 67851 - Responses Owners Queries About Top Level Rectification Due to Water Ingress
Patrick Rush
prush at stratatitle.com.au
Wed Feb 22 11:22:40 AEDT 2017
Dear Committee,
Please see the below response from Prestech in relation to the approved work to Level 7 to stop any further water ingress to the top level Lots.
Can you please confirm you agree with the below and advise on each matter if you agree?
In relation to the plants please confirm if you would like the removed plants taken away and the Owners Corporation then have landscaper quote on planting of non-invasive alternate plants when the other rectification work by Prestech is completed?
Kind regards,
Patrick Rush
Strata Manager
Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice: Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.
From: Paul McKay [mailto:paul.mckay at costinroe.com.au]
Sent: Tuesday, 14 February 2017 3:15 PM
To: Patrick Rush <prush at stratatitle.com.au>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au>; Tanaz Dhondy <tanaz.dhondy at costinroe.com.au>
Subject: RE: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Hi Patrick,
I have emailed and subsequently spoken to Preservation Technology.
1) There is no change in cost in regards to the full removal of the plants versus keeping them on site and reinstating them.
2) Due to their present work load (busy) they are not in a position to lower their cost.
3) Based on contract execution of 15/03/2017, their start date would be early May.
Can you advise if we should proceed based on their submitted tender cost of $182,149 (incl. GST) and start date in early May?
Regards,
Paul
From: Patrick Rush [mailto:prush at stratatitle.com.au]
Sent: Wednesday, 8 February 2017 1:18 PM
To: Paul McKay <paul.mckay at costinroe.com.au<mailto:paul.mckay at costinroe.com.au>>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au<mailto:edelacruz at stratatitle.com.au>>; Tanaz Dhondy <tanaz.dhondy at costinroe.com.au<mailto:tanaz.dhondy at costinroe.com.au>>
Subject: RE: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Importance: High
Hi Paul,
I am happy to be led by you as the Engineer for the project and agree with another contractor completing the landscaping and only the soil being replaced by Prestech.
On the membrane matter, please advise the best option and approach Prestech and advise on their responses so that I can finalise the work and issue work orders for Prestech to undertake the rectification as well as agreement for you to Project Manage the rectifications?
Kind regards,
Patrick Rush
Strata Manager
Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice: Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.
From: Paul McKay [mailto:paul.mckay at costinroe.com.au]
Sent: Friday, 3 February 2017 5:24 PM
To: Patrick Rush <prush at stratatitle.com.au<mailto:prush at stratatitle.com.au>>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au<mailto:edelacruz at stratatitle.com.au>>; Tanaz Dhondy <tanaz.dhondy at costinroe.com.au<mailto:tanaz.dhondy at costinroe.com.au>>
Subject: RE: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Hi Patrick,
Thank you for your email. My response in red below:
I can confirm the Owners Corporation would like you to approach Prestech for the 2 below points but would also like you to confirm that it is necessary to remove all tiles from above Unit 602?
In relation to my point in the previous email:
1) The tender document states:
"Reinstate the existing plants and soil" - This means that if the Owners Corporation would like to have new plants placed in the planter boxes it would cost more as this was not included in the tender. We can revise the contract to say, contractor to reinstate the soil, landscaping by other. Please advise? A minor cost saving.
2) The Andersal Warranty Extension Clause states: "warranty of workmanship period to 10 years for structural work". As stated in Tanaz previous email on the 8/12/2016, this warranty will not extend to this type of work as it is non structural.
3) We have recommended that the tiles to terrace area above 602 are replaced following the flood testing of this area. Although no water leaks were found within the unit, water is entering the cavity of the wall and onto the face via the weep holes. The condition of the membrane and age is unknown, but I would suspect it was done at a similar time to the podium over unit 601 which showed water ingress when flood tested. It will be a matter of time before it degrades further over unit 602. Water in the cavity wall will affect the durability of wall ties/brick, there is a lot of water entering the cavity, this is not ideal.
To address the above we have 2 options:
1) Go with the original contract and amend to reinstate the soil only.
2) Add the membrane repair over unit 602 as a Provisional sum and put an allowance in for the contractor to lift some perimeter tiles and for us to inspect the membrane.
1 is the preferred, option 2 would be good if we suspected the membrane to be in good condition however in our opinion it is very likely to be degraded based on the flood testing.
At this stage, we can contact Prestech as the preferred contractor and provide a revised Schedule of Prices they can amend easily.
Please advise on the above and below and confirm when Prestech will be able to confirm if I can execute the contract on the 15/03/2017 ad provide financial statements so they can organise the HOWi?
Once the above is confirmed I will get onto Prestech early next week.
Please feel free to call and discuss.
Kind regards,
Paul
From: Patrick Rush [mailto:prush at stratatitle.com.au]
Sent: Friday, 3 February 2017 1:50 PM
To: Paul McKay <paul.mckay at costinroe.com.au<mailto:paul.mckay at costinroe.com.au>>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au<mailto:edelacruz at stratatitle.com.au>>; Tanaz Dhondy <tanaz.dhondy at costinroe.com.au<mailto:tanaz.dhondy at costinroe.com.au>>
Subject: RE: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Importance: High
Hi Paul,
Apologies, just been flat out this week.
The Owners Corporation agreed to proceed with Presetech to carry out the necessary repairs and the time for the work to be undertaken has already passed as per the NCAT Orders so if the rectification can be organised as soon as possible.
The Owners Corporation will have the funds in full by 15/03/2017 when the 1st part of the special levy is due.
I can confirm the Owners Corporation would like you to approach Prestech for the 2 below points but would also like you to confirm that it is necessary to remove all tiles from above Unit 602?
Please advise on the above and below and confirm when Prestech will be able to confirm if I can execute the contract on the 15/03/2017 ad provide financial statements so they can organise the HOWi?
Kind regards,
Patrick Rush
Strata Manager
Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice: Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.
From: Paul McKay [mailto:paul.mckay at costinroe.com.au]
Sent: Thursday, 2 February 2017 12:46 PM
To: Patrick Rush <prush at stratatitle.com.au<mailto:prush at stratatitle.com.au>>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au<mailto:edelacruz at stratatitle.com.au>>; Tanaz Dhondy <tanaz.dhondy at costinroe.com.au<mailto:tanaz.dhondy at costinroe.com.au>>
Subject: RE: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Hi Patrick,
I called to discuss the outcome of the meeting which took place on Tuesday.
My main points taken from the meeting were:
1) Any plants re-introduced will need to have non-invasive roots (easier said than done),
2) If the committee want to proceed with my recommendation of Prestech they would like to know if they offer 10yrs extended warranty if invoices are paid on time as this was seen as a big positive with the Andersal tender. They would also like to see if Prestech are willing to match the Andersal tender price.
Can you advise me of the date the NCAT order to fix the leaks into 601 are required to be completed by?
Can you please provide me with an update on the outcome and direction the committee would like to proceed in?
Kind regards,
Paul
From: Patrick Rush [mailto:prush at stratatitle.com.au]
Sent: Monday, 30 January 2017 10:45 AM
To: Paul McKay <paul.mckay at costinroe.com.au<mailto:paul.mckay at costinroe.com.au>>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au<mailto:edelacruz at stratatitle.com.au>>
Subject: RE: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Hi Paul,
I can confirm that the Committee agreed to have you present at the meeting tomorrow in the main foyer entrance at 6:30pm.
Please confirm that you will be in attendance?
Kind regards,
Patrick Rush
Strata Manager
Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice: Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.
From: Patrick Rush
Sent: Sunday, 29 January 2017 7:20 PM
To: Paul McKay <paul.mckay at costinroe.com.au<mailto:paul.mckay at costinroe.com.au>>
Cc: EJ Dela Cruz <edelacruz at stratatitle.com.au<mailto:edelacruz at stratatitle.com.au>>
Subject: SP 67851 - Owners Queries About Top Level Rectification Due to Water Ingress
Importance: High
Hi Paul,
Can you please provide a response to the below email about the proposed works on the top level podium, including waterproofing and tiling so that I can provide a response by close of business, Monday 30th January 2017?
I will also confirm with you by 12:00pm, Monday if the Committee have approved you attending the meeting at 6:30pm on Tuesday 31st January 2017 on site.
Kind regards,
Patrick Rush
Strata Manager
Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au<mailto:prush at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice: Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.
-----Original Message-----
From: Ken West [mailto:ennvvest at gmail.com]
Sent: Wednesday, 25 January 2017 1:15 PM
To: Patrick Rush
Cc: EJ Dela Cruz; info at bfms.com.au<mailto:info at bfms.com.au>; Cathy Rechichi
Subject: Re: SP 67851 - EGM Notice 31 January 2017
Thanks Patrick.
I still do not understand why tiles need replacing. Water can only travel to the edges so I cannot see why the entire area would need replacing.
It seems a bit lazy at our expense.
It would make more sense to do the obvious work and reseal the borders before just ripping up the entire deck.
Also Cathy and I would like to know what Avis pays for its use of the building and signage rights.
Would it make more sense to have the meeting on the roof area instead of foyer??
Thanks,
Ken West
> On 25 Jan 2017, at 12:57 PM, Patrick Rush <prush at stratatitle.com.au<mailto:prush at stratatitle.com.au>> wrote:
>
> <SP 67851 - Unit 601 Level 7 Terrace Flood Testing Report - 14.09.2016.pdf>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20170222/01b62b1b/attachment-0001.html
More information about the EC
mailing list