[200William-EC SP67851] Marquis Re: External Facade Rainwater Leaks
Marquis
Marquis at bfms.com.au
Tue May 3 13:33:34 AEST 2022
Hi Leanne,
Apt 104 reported 2 separate issues:
1. Loungeroom Leak - This was repaired as part of the McElhone St External Facade repairs. Attached invoice 522. (Completed)
1. Bedroom Leak - Water has penetrated the bedroom ceiling next to the external wall. The same issue was addressed several years ago by installing a metal flashing across the top of the external facade wall. Over time the flashing has lifted, and the metal corner angles have rusted and broken apart the external wall. To repair/reseal the existing flashing, remove/replace the rusted metal angle via abseil will cost $3,000.00 + GST. This will be listed on the updated quotation available from tomorrow. (Pending Approval)
Completed Repairs
Repair 1.
Apt 602 Bedroom Ceiling Leak - The cost to complete this work came to $4,000.00 + GST. Invoice 523 attached for reference. Our plan is to monitor the bedroom of Apt 602 during rain periods to ensure the repairs were successful before repairing the ceiling but with Ken passing away recently Cathy has not been staying at the apartment.
If the leak is confirmed as still active further repairs quoted at $3,000.00 + GST are recommended. This will be listed on the updated quotation.
Repair 2.
Dowling St External Facade Repairs - Replacement expansion joints causing leaking into the AVIS reception area. The cost to complete the work came to $2,750.00 + GST. Invoice 521 attached for reference.
Repair 3.
Awning Drainage Clean & Seal Replacement - The glass awnings overhanging the William St facade were blocked causing water to pool and penetrate failed seals between the building facade and awning frame. The water was leaking into the AVIS reception area. The cost to complete these repairs was $2,000.00 + GST. The invoice is yet to be received.
I hope this makes sense but if you require more information, please let me know. Thanks
Kind regards,
Darren Vignes
Building Manager
[cid:a2bb9c9c-2d3c-4d95-bd34-8e8ab673491f]
Building Facilities Management Solutions
200 William Street, Woolloomooloo NSW 2111
T: 0488 388 313
Email: marquis at bfms.com.au<mailto:marquis at bfms.com.au>
bfms.com.au
Please consider the environment before printing this email.
The content of this e-mail is solely intended for the addressee, and its attachments are confidential and may be subject to legal professional privilege and copyright. It is intended solely for the addressee. Access to this e-mail and its attachment by anyone else is unauthorised. No representation is made that this e-mail or any attachment is free of viruses and other defects. Virus scanning is recommended and is the responsibility of the recipient. If you are not the intended addressee, any disclosure, usage, copying, distribution or any action taken or omitted to be taken in reliance on it, is prohibited. If you have received this communication in error, please advise the sender immediately by reply e-mail and delete this message from your computer. Thank you for your cooperation.
[cid:c1b3cee4-3138-49bb-97d7-fc4bff205068]
________________________________
From: Leanne Eardley <leardley at stratatitle.com.au>
Sent: 03 May 2022 12:17
To: Marquis <Marquis at bfms.com.au>; ec at 200william.com <ec at 200william.com>
Cc: Leanne Eardley <leardley at stratatitle.com.au>
Subject: EXT - RE: Marquis Re: External Facade Rainwater Leaks
Thanks Darren
Can you please confirm which items have been completed already?
Unit 104 is demanding an update on their water ingress issue.
Kind Regards,
Leanne Eardley
Senior Community Manager
[cid:image001.png at 01D85EE7.BC0A2F30]
STRATA TITLE MANAGEMENT
t. (02) 9266 2600
d. (02) 9266 2648
e. leardley at stratatitle.com.au<mailto:name at stratatitle.com.au>
a. Suite 2, Level 4, 1 Chandos Street, St Leonards NSW 2065
[cid:image002.png at 01D85EE7.BC0A2F30]<https://smartercommunities.com.au/covid-19/>
[cid:image003.png at 01D85EE7.BC0A2F30]<https://issuu.com/smartercommunities/docs/0121_scmagazine_final_issuu>
[cid3266202371*image006.png at 01D80635.C2FB44B0]<https://aus01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fnsw.strata.community%2F2021-strata-community-awards-finalists%2F&data=04%7C01%7Cleardley%40stratatitle.com.au%7C7b1d83e1e0d749bbd38f08d9d4000d4f%7C2579fdbe9584475e914839b6bc70b75d%7C0%7C0%7C637773918959270129%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=48Qko8dMtVwUzkX6lddjbgCf5CRxN%2FwXkYj2gExnuIs%3D&reserved=0>
[cid:image005.png at 01D85EE7.BC0A2F30]
DISCLAIMER: Liability limited by a scheme approved under Professional Standards Legislation. Strata Title Management Group Pty Ltd takes no responsibility for content included in this email when relating to a client matter. Please view Smarter Communities’ full email communication disclaimer smartercommunities.com.au/disclaimer<https://smartercommunities.com.au/disclaimer/>
From: Marquis <Marquis at bfms.com.au>
Sent: Tuesday, 3 May 2022 10:39 AM
To: Leanne Eardley <leardley at stratatitle.com.au>; ec at 200william.com
Subject: Re: Marquis Re: External Facade Rainwater Leaks
WARNING. This email was received from an external sender. You should verify the email address before processing the email.
Hi Leanne,
We have been forced to complete some of the works so I have asked the contractor to provide an updated written quotation for the remaining. Should have it by tomorrow. Thanks
Kind regards,
Darren Vignes
Building Manager
[cid:image007.png at 01D85EE7.BC0A2F30]
Building Facilities Management Solutions
200 William Street, Woolloomooloo NSW 2111
T: 0488 388 313
Email: marquis at bfms.com.au<mailto:marquis at bfms.com.au>
bfms.com.au
Please consider the environment before printing this email.
The content of this e-mail is solely intended for the addressee, and its attachments are confidential and may be subject to legal professional privilege and copyright. It is intended solely for the addressee. Access to this e-mail and its attachment by anyone else is unauthorised. No representation is made that this e-mail or any attachment is free of viruses and other defects. Virus scanning is recommended and is the responsibility of the recipient. If you are not the intended addressee, any disclosure, usage, copying, distribution or any action taken or omitted to be taken in reliance on it, is prohibited. If you have received this communication in error, please advise the sender immediately by reply e-mail and delete this message from your computer. Thank you for your cooperation.
[cid:image008.png at 01D85EE7.BC0A2F30]
________________________________
From: Leanne Eardley <leardley at stratatitle.com.au<mailto:leardley at stratatitle.com.au>>
Sent: 02 May 2022 16:32
To: Marquis <Marquis at bfms.com.au<mailto:Marquis at bfms.com.au>>; ec at 200william.com<mailto:ec at 200william.com> <ec at 200william.com<mailto:ec at 200william.com>>
Cc: Leanne Eardley <leardley at stratatitle.com.au<mailto:leardley at stratatitle.com.au>>
Subject: EXT - RE: Marquis Re: External Facade Rainwater Leaks
Afternoon Darren
Can you please send me through the formal quote from updown access.
>From doing a rough calculation on the below email, works in total are over $30k in value, and therefore HOWI would need to be entered into which would require it to be formally accepted at a committee meeting to authorise our office to sign the contract on behalf of the strata scheme.
Are you obtaining a further quote?
Kind Regards,
Leanne Eardley
Senior Community Manager
[cid:image001.png at 01D85EE7.BC0A2F30]
STRATA TITLE MANAGEMENT
t. (02) 9266 2600
d. (02) 9266 2648
e. leardley at stratatitle.com.au<mailto:name at stratatitle.com.au>
a. Suite 2, Level 4, 1 Chandos Street, St Leonards NSW 2065
[cid:image002.png at 01D85EE7.BC0A2F30]<https://aus01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fsmartercommunities.com.au%2Fcovid-19%2F&data=05%7C01%7Cleardley%40stratatitle.com.au%7Cc9518fa564fd430a1e9008da2c9d55a3%7C2579fdbe9584475e914839b6bc70b75d%7C0%7C0%7C637871351521072465%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=3yDlpETx6ZTwE%2BOTqXYpwEbpcSoJoxD%2FrReU1oGYw0g%3D&reserved=0>
[cid:image003.png at 01D85EE7.BC0A2F30]<https://aus01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fissuu.com%2Fsmartercommunities%2Fdocs%2F0121_scmagazine_final_issuu&data=05%7C01%7Cleardley%40stratatitle.com.au%7Cc9518fa564fd430a1e9008da2c9d55a3%7C2579fdbe9584475e914839b6bc70b75d%7C0%7C0%7C637871351521072465%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=tCneNFaHW%2BYKeWUnUC8%2FclW7KYhO0X4d3bV3%2F3XerPk%3D&reserved=0>
[cid3266202371*image006.png at 01D80635.C2FB44B0]<https://aus01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fnsw.strata.community%2F2021-strata-community-awards-finalists%2F&data=05%7C01%7Cleardley%40stratatitle.com.au%7Cc9518fa564fd430a1e9008da2c9d55a3%7C2579fdbe9584475e914839b6bc70b75d%7C0%7C0%7C637871351521228702%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=EPYwP%2F%2BQdRZJsfr1azIBxOk0S0KV11%2BjZI0jwNkMsFs%3D&reserved=0>
[cid:image005.png at 01D85EE7.BC0A2F30]
DISCLAIMER: Liability limited by a scheme approved under Professional Standards Legislation. Strata Title Management Group Pty Ltd takes no responsibility for content included in this email when relating to a client matter. Please view Smarter Communities’ full email communication disclaimer smartercommunities.com.au/disclaimer<https://aus01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fsmartercommunities.com.au%2Fdisclaimer%2F&data=05%7C01%7Cleardley%40stratatitle.com.au%7Cc9518fa564fd430a1e9008da2c9d55a3%7C2579fdbe9584475e914839b6bc70b75d%7C0%7C0%7C637871351521228702%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=JHiPGd6gKXe09nufZmoIRaBEZDyV0R%2F3JPGEmIVst0U%3D&reserved=0>
From: Marquis <Marquis at bfms.com.au<mailto:Marquis at bfms.com.au>>
Sent: Wednesday, 20 April 2022 2:48 PM
To: ec at 200william.com<mailto:ec at 200william.com>
Cc: Leanne Eardley <leardley at stratatitle.com.au<mailto:leardley at stratatitle.com.au>>
Subject: Marquis Re: External Facade Rainwater Leaks
WARNING. This email was received from an external sender. You should verify the email address before processing the email.
Good afternoon all,
The recent rainstorms have caused leaking issues throughout the building. The following is a breakdown and costing to address each issue.
Apt 602 Bedroom Ceiling Leak
Water has again penetrated the bedroom ceiling in the same location that was identified during the eastern terrace waterproofing work back in 2018. Photo attached for reference. At the time, we water tested the new membrane for leaks and found water was penetrating the podium wall and tracking down through a hole above Apt 602 bedroom. The issue was resolved by sealing up cracks around the external podium wall.
Recent investigation during a rainstorm identified the water to be dripping from this same hole indicating that water is again getting into the podium wall. The external podium wall was checked, and no new cracks or failed repairs could be found. The top of the podium wall had some new cracks and two previously repairs had holes due to birds picking at the seals. The parapet wall that joins adjoins the podium wall had rusted angles which had broken apart. The expansion joints between the parapet and podium walls on the external facade had failed. The seal between the external parapet wall and the slab had also failed.
Updown Access was urgently engaged to reseal the new cracks and previous repairs on the top of the podium wall. Cut out and remove the rusted metal angles on the parapet wall, replace with new plastic angles and render. Replace the failed expansion joints on the parapet wall and reseal the handrail posts on the top of the parapet wall. The cost to complete this work came to $4,000.00 + GST. We plan to monitor the bedroom of Apt 602 during the next rain period to ensure the repairs were successful before repairing the ceiling.
Another section of parapet wall between the small parapet wall and the Gym wall has obvious signs of water penetration. The metal angles have also rusted and exposed the wall to potential water penetration. Updown Access have quoted $3,000.00 + GST to repair this wall if leaking is identified around this section.
Attached is a plan of the William St external facade with the red section outlining the completed repairs and the green section outlining the recommended parapet wall repairs.
Apt 104 Bedroom Ceiling Leak
Water has penetrated the bedroom ceiling next to the external wall. The same issue was addressed several years ago by installing a metal flashing across the top of the external facade wall. Over time the flashing has lifted, and the metal corner angles have rusted and broken apart the external wall. Location marked in yellow on the attached William St facade plan. To repair/reseal the existing flashing, remove/replace the rusted metal angle via abseil will cost $3,000.00 + GST.
Apt 403
Rainwater is penetrating the top of the rounded windows. Marked on the attached William St Facade in aqua. Updown Access have quoted $2,000.00 + GST to remove and replace the existing seals.
Apt 602 Living Room Leak
Water has penetrated the living area of Apartment 602 around the sliding doors. Inspection and testing found water is getting into the external wall and coming out around the skirting. The parapet wall was checked, and some cracking and bubbling paint was identified. The seal between the parapet wall and metal awning has failed and requires replacement. A substantial amount of water has built up under a section of the planter box membrane. To rectify this issue, we propose to drill drainage holes in the external parapet wall to allow the water build up under the planter box membrane to drain. Repair the cracks and drainage holes on the parapet wall. Apply waterproofing membrane to the parapet wall, planter box walls and handrail posts. Repaint the sections of waterproofing membrane to suit existing. Updown Access have quoted $8,200.00 + GST to repair.
Attached is a plan of the eastern terrace and rear external facade with the blue and orange sections outlining the locations of the proposed repairs.
Dowling St External Facade Leaks
Apt 201
Rainwater has penetrated the external bedroom wall. Water drips from the ceiling and is tripping out their power point. Above the leak location is two expansion joints in poor condition, metal corner angles that have rusted and broken apart and a very dark stain under the rainwater head on the corner of Craig's terrace. Attached is a plan for reference with the areas marked in pink. I had a plumber onsite to investigate a leak in Craig's ensuite, so I had them also look at the rainwater head and they have confirmed the seals around it require replacement. To address the other issues Updown access have quoted $5,000.00 + GST.
Apt 106 Window Leak
Rainwater is penetrating the top of the rounded windows. Marked on the attached in light blue. Updown Access have quoted $2,000.00 + GST to remove and replace the existing seals.
AVIS reception
Rainwater is penetrating the Dowling St external wall. We have since removed and replaced the expansion joints in the section of external wall marked in purple on the attached for $2,500.00 + GST. But we suspect the seal around the external awning has failed as water is still dripping from the base of the entire awning. To remove and replace the seal marked in orange on the attached is $2,000.00 + GST.
Willam St Ground Floor Facade
The William St ground floor facade is looking very poor due to rain penetrating the external walls and we have received several complaints about the building's presentation. To permanently fix the issue the whole building facade requires extensive repairs so instead we have obtained a quotation for $1,580.00 + GST for the following:
Scrape back all the damaged paint work and expose the metal trims that have corrosion.
Treat corrosion to trims.
Apply setting compounds to facades.
Prime and paint facade repairs.
Remove and replace 2 x broken wall tiles.
I would assume this would be a BMC expense, but Leanne will need to confirm.
I hope all this makes sense but if you have questions, please let me know. Thanks
Kind regards,
Darren Vignes
Building Manager
[cid:image009.png at 01D85EE7.BC0A2F30]
Building Facilities Management Solutions
200 William St Woolloomooloo NSW 2011
M: 0488 388 313
Email: marquis at bfms.com.au<mailto:marquis at bfms.com.au>
www.bfms.com.au<https://aus01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bfms.com.au%2F&data=05%7C01%7Cleardley%40stratatitle.com.au%7Cc9518fa564fd430a1e9008da2c9d55a3%7C2579fdbe9584475e914839b6bc70b75d%7C0%7C0%7C637871351521228702%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2Brk8iozTzOMu6NmowifL%2Bgx0tOCBpUfo5LPzRVCzvAE%3D&reserved=0>
Please consider the environment before printing this e-mail
The contents of this e-mail and its attachments are confidential and may be subject to legal professional privilege and copyright. It is intended solely for the addressee. Access to this e-mail and its attachment by anyone else is unauthorised. No representation is made that this e-mail or any attachment is free of viruses and other defects. Virus scanning is recommended and is the responsibility of the recipient. If you are not the intended addressee, any disclosure, usage, copying, distribution or any action taken or omitted to be taken in reliance on it, is prohibited. If you have received this communication in error, please advise the sender immediately by reply e-mail and delete this message from your computer.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3087 bytes
Desc: image001.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0010.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 4862 bytes
Desc: image002.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0011.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 203688 bytes
Desc: image003.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0012.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 170252 bytes
Desc: image004.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0013.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 38093 bytes
Desc: image005.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0014.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 28956 bytes
Desc: image007.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0015.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 169948 bytes
Desc: image008.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0016.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 24383 bytes
Desc: image009.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0017.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-b2tt5hdy.png
Type: image/png
Size: 28956 bytes
Desc: Outlook-b2tt5hdy.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0018.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-ms32tl1q.png
Type: image/png
Size: 169948 bytes
Desc: Outlook-ms32tl1q.png
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0019.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: SP67851 Marquis 22Apr Inv522 Updown Access McElhone St External Facade Repairs.pdf
Type: application/pdf
Size: 218656 bytes
Desc: SP67851 Marquis 22Apr Inv522 Updown Access McElhone St
External Facade Repairs.pdf
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0002.pdf
-------------- next part --------------
A non-text attachment was scrubbed...
Name: SP67851 Marquis 22Apr Inv523 Updown Access William St External Facade Repairs.pdf
Type: application/pdf
Size: 218116 bytes
Desc: SP67851 Marquis 22Apr Inv523 Updown Access William St
External Facade Repairs.pdf
Url : http://200william.com/mailman/private/ec/attachments/20220503/ed710f46/attachment-0003.pdf
More information about the EC
mailing list