Hi Craig,

I will follow up the commercial representative with an email and phone call today and request urgent approval or a response as to why they have not agreed to proceed with the rectification work.


Kind regards,
Patrick Rush
Senior Community Manager

Phone: (02) 9266 2600 | Direct Phone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

[BSC_STM_logo_4c]    [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf Of Craig Laforest
Sent: Friday, 4 August 2017 10:55 AM
To: ec at 200william.com
Subject: [200William-EC SP67851] FW: DP 1040255 - Reinstatement of the Correct Operation of Storm Water & Sewer Systems for Approval

Hello again Patrick,
I refer to my email of July 31.  Would you kindly respond.

Robin and I have been without our spaces and storage for a very long time.  Would you kindly explain something for me.  I am paying the levies for my car space and storage affected by the water penetration.  Is the commercial side paying anything? Why do I have to wait for their acceptance?

Please advise on the points below as well (in yellow).

Craig Laforest

From: Craig Laforest [mailto:cscl at optusnet.com.au]
Sent: Monday, 31 July 2017 2:32 PM
To: 'Patrick Rush'; 'ec at 200william.com'
Subject: RE: [200William-EC SP67851] DP 1040255 - Reinstatement of the Correct Operation of Storm Water & Sewer Systems for Approval

Thank you.  When owner's spaces are having a problem (in this case the water), please explain why the BMC needs to authorize the works. Is it because of the sewerage factor which also affects the commercial side? Are they up for a percentage of the charge to repair? Anything else?


From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com]<mailto:[mailto:ec-bounces at 200william.com]> On Behalf Of Patrick Rush
Sent: Monday, 31 July 2017 2:07 PM
To: ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] DP 1040255 - Reinstatement of the Correct Operation of Storm Water & Sewer Systems for Approval

Hi Craig,

I have yet to have a response from Andrew Veron, the BMC Representative of SP 67850 (Commercial) and until then I cannot proceed.

I have left a voicemail and will send a follow up email for Andrew to response urgently.

I am waiting on the amended quote for removal of the soil and plants and waterproofing only. I should have this in the next few days for the Committee to review and decide on a way forward.


Kind regards,
Patrick Rush
Senior Community Manager

Phone: (02) 9266 2600 | Direct Phone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

[BSC_STM_logo_4c]    [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com]<mailto:[mailto:ec-bounces at 200william.com]> On Behalf Of Craig Laforest
Sent: Monday, 31 July 2017 10:00 AM
To: ec at 200william.com<mailto:ec at 200william.com>
Subject: [200William-EC SP67851] FW: DP 1040255 - Reinstatement of the Correct Operation of Storm Water & Sewer Systems for Approval
Importance: High

Hello Patrick,

Would you please advise where we stand with the P4 repairs.  At the bottom of your July 11 email, you stated:

"Once an agreement is made, I will send out an agenda to confirm the agreement and then proceed with the necessary work?"

Also, any update on what is happening to the repairs to level 7.  Who from the EC hasn't responded please for the extra works being carried out to remove all the plants and soil?

Thank you and regards,
Craig Laforest

From: ec-bounces at 200william.com<mailto:ec-bounces at 200william.com> [mailto:ec-bounces at 200william.com] On Behalf Of Patrick Rush
Sent: Wednesday, 19 July 2017 7:32 PM
To: 'Matt Perkins'; 'Andrew Veron'
Cc: Ben Mees; Darren Vignes; 'Marquis'; ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: [200William-EC SP67851] DP 1040255 - Reinstatement of the Correct Operation of Storm Water & Sewer Systems for Approval
Importance: High

Hi Andrew,

Can you urgently respond on the below as SP 67851 are happy to proceed with the tender recommendation of Rescom Builders from AJ Whipps Consulting, with the proposal for them to Project Manage the rectification?

Please urgently respond on this matter?


Kind regards,
Patrick Rush
Senior Community Manager

Phone: (02) 9266 2600 | Direct Phone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

[BSC_STM_logo_4c]    [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website - www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: Matt Perkins [mailto:matt at spectrum.com.au]<mailto:[mailto:matt at spectrum.com.au]>
Sent: Tuesday, 4 July 2017 8:53 AM
To: Patrick Rush <prush at stratatitle.com.au<mailto:prush at stratatitle.com.au>>; 'Andrew Veron' <av at charlesstuart.com.au<mailto:av at charlesstuart.com.au>>
Cc: Ben Mees <ben.mees at bmaus.com.au<mailto:ben.mees at bmaus.com.au>>; Darren Vignes <marquis at bfms.com.au<mailto:marquis at bfms.com.au>>; 'Marquis' <marquis at bmaus.com.au<mailto:marquis at bmaus.com.au>>; ec at 200william.com<mailto:ec at 200william.com>
Subject: Re: DP 1040255 - Reinstatement of the Correct Operation of Storm Water & Sewer Systems for Approval

Hi All,
The EC of the the SP67851 have authorised me to agree with the engineers recommendation of Rescom and go ahead with the repair.

Kind Regards
Matt.


On 27/6/17 6:00 pm, Patrick Rush wrote:
Dear BMC Representatives,

Please see attached the tender documentation and recommendation for the reinstatement of the correct operation of storm water and sewer systems for your consideration.

Below is the table in the etched on page 1, with the recommendation by AJ Whipps Consulting Group on Page 2 for ease of viewing -

Contractor

Cost (+ GST)

Rescom Builders  Pty Ltd

$60,518.40

Hitech Remedial Pty Ltd

$72,880.00

Buildcore Constructions

$81,895.00



Can you please review the above and contact the Committee Members from the relevant Owners Corporations and advise a decision on if you are happy to proceed with AJ Whipps Group's recommendation of Rescom Builders? Can you also confirm you are happy to proceed with the contract and administration and supervision of the work by AJ Whipps Consulting Group?

Once an agreement is made, I will send out an agenda to confirm the agreement and then proceed with the necessary work?


Kind regards,
Patrick Rush
Senior Strata Manager

Phone: (02) 9266 2600 | DirectPhone: (02) 9266 2695 | Email: prush at stratatitle.com.au<mailto:northshore at stratatitle.com.au> | Address: PO Box 2727, Taren Point, NSW 2229

[BSC_STM_logo_4c]    [cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box] <http://www.facebook.com/StrataTitleManagement>     [cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box]  <http://www.linkedin.com/company/strata-title-management-stm>    [cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box] <http://www.twitter.com/STMStrata>     [pinterest.png] <http://www.pinterest.com/STMStrata>     [google_plus.png] <http://plus.google.com/+StrataTitleManagemenSydney>

Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when relating to a client matter.
Please view Vesture's full email communication disclaimer on our website -www.stratatitle.com.au/disclaimer/<http://www.stratatitle.com.au/disclaimer/>
Important Notice:  Owners should be aware that all correspondence, including letters, facsimile transmissions and emails are retained on the file of your scheme and may be subject to inspection by owners and residents within your scheme, as well as prospective purchasers for any lot that may be for sale within your scheme. As such author discretion is advised.

From: Behrang Dehestani [mailto:bdehestani at ajwhipps.com.au]
Sent: Friday, 16 June 2017 8:50 AM
To: Patrick Rush <prush at stratatitle.com.au><mailto:prush at stratatitle.com.au>; Raeleen Marsh <rmarsh at stratatitle.com.au><mailto:rmarsh at stratatitle.com.au>
Cc: Jess Heaton <jheaton at ajwhipps.com.au><mailto:jheaton at ajwhipps.com.au>; 'Marquis' <Marquis at bfms.com.au><mailto:Marquis at bfms.com.au>
Subject: RE: DP 1040255 - WO

Hi Patrick,

Please see attached tender review for 200 William Street, Woolloomooloo.

I recommend that we arrange a time to meet with the recommended contractor, building management and any Owners committee members to discuss the particulars prior to preparing contracts. This work will be charged at 4 hours.

Further to this, we require a work order approval for Stage 2 (construction) of AJ Whipps fee dated 31 March 2017. This will permit us to supervise and project co-ordinate the works.

Look forward to delivering a successful project.

Regards,

Behrang Dehestani
Senior Remedial Project Engineer
Forensic Analysis Remedial Engineering

AJ Whipps Consulting Group
2/101 Union Street
McMahons Point, NSW 2060
t    02 8923 8444
f    02 8923 8484
e  bdehestani at ajwhipps.com.au
<mailto:bdehestani at ajwhipps.com.au%0b>
www.ajwhipps.com.au<http://ajwhipps.com.au/>

[http://ajwhipps.com.au/wp-content/uploads/Whipps_Logo_Portrait_Tag.gif]

[http://ajwhipps.com.au/wp-content/uploads/whipps_linkedin.png]<http://www.linkedin.com/company/aj-whipps-consulting-group>  [http://ajwhipps.com.au/wp-content/uploads/whipps_facebook.png] <https://www.facebook.com/ajwhipps>   [http://ajwhipps.com.au/wp-content/uploads/whipps_instagram.png] <http://instagram.com/aj_whipps_consulting_group>
This electronic mail is solely for the use of the addressee and may contain information which is confidential. Unauthorized use of any information contained in this email is strictly prohibited. If you receive this electronic mail in error, please delete it from your system immediately and notify the sender by electronic mail or using any of the above contact details.






--

/* Matt Perkins

        Direct 1300 137 379        Spectrum Networks Ptd. Ltd.

        Office 1300 133 299        matt at spectrum.com.au<mailto:matt at spectrum.com.au>

                                   Level 6, 350 George Street Sydney 2000

        Spectrum Networks is a member of the Communications Alliance & TIO

*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0001.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3125 bytes
Desc: image001.jpg
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0001.jpg 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 4236 bytes
Desc: image002.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0009.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3977 bytes
Desc: image003.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0010.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 4502 bytes
Desc: image004.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0011.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1488 bytes
Desc: image005.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0012.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1725 bytes
Desc: image006.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0013.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 7103 bytes
Desc: image007.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0014.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 494 bytes
Desc: image008.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0015.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 402 bytes
Desc: image009.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0016.png 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 585 bytes
Desc: image010.png
Url : http://200william.com/mailman/private/ec/attachments/20170804/58869697/attachment-0017.png 


More information about the EC mailing list