[200William-EC SP67851] SP 67851 - URGENT Tribunal Order forWater Penetration in Unit 601 - CRAIG LAFOREST VS BODYCORPORATE STRATA PLAN 67851

Brook Beves brookbeves at bigpond.com
Tue Apr 19 11:40:50 AEST 2016


Dear Patrick

 

As you are now aware the further Dye testing has been approved by majority
of the EC, subject to the areas to be tested and that the costs shall be met
by the Engineer.

 

Regards, 

Brook Beves

 

  _____  

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Brook Beves
Sent: Tuesday, 19 April 2016 11:20 AM
To: 'Patrick Rush'
Cc: ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order
forWater Penetration in Unit 601 - CRAIG LAFOREST VS BODYCORPORATE STRATA
PLAN 67851

 

 

Dear Patrick and Committee

 

Thank you Patrick for your response.  

 

In the absence of ever having been provided with the Order of NCAT or any
correspondence or submissions made on behalf of the Owners Corporation by
STM, I have spoken at length with George Ziri formerly of BFMS who is
thoroughly familiar with the history of this issue and work done and
expenses incurred to date. 

 

It has been opined that the water ingress may be coming from 2 possible
areas:

 

1.	The planter boxes on the perimeter of level 7 although that area was
stripped of plants some years ago, re-waterproofed and the problem was
resolved devoid of any plants.
2.	The raised round podiums on level 7 outside terrace area.  When the
entire level 7 terrace flooring was pulled up and re-tiled in 2009 the only
area which was not re-surfaced was these raised round podiums and it is
possible that water is penetrating through that area and seeping under the
re-tiled terrace flooring.

 

Subject to the cost of this dye testing being met by the Engineer who has a
"duty of care" to the Owners Corporation for their incorrect professional
assessment and rectification of this problem, I have no objection to the
further dye testing to:

 

1)                     The planter boxes where they meet the tiles; and

2)                     The raised round podiums 

 

The consent of the others member of the Executive Committee is sought.  

 

Many thanks 

Brook Beves

 

  _____  

From: Patrick Rush [mailto:prush at stratatitle.com.au] 
Sent: Monday, 18 April 2016 12:48 PM
To: 'Brook Beves'
Cc: ec at 200william.com
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

 

Hi Brooke & Committee,

 

I believe that as the water ingress may be coming from failed waterproofing
in the planter boxes above as advised by Lee, the Engineer.

 

I believe that the Owners Corporation should be pushing for the testing to
be carried out on these planter boxes to then be advised where exactly the
source of the water ingress is.

 

As Craig, is pushing to now take the Owners Corporation back to Fair Trading
(Tribunal) with this matter I believe this to be the best option and then
once the source of the water leak has been identified then further action
can be taken or not depending on the source.


Please advise if you agree with this approach and i will again email Lee and
advise the Owners Corporation believe the costs of such testing should be at
no extra cost.


Apologies for the delay, I was unwell and off work all of last week!

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au
<mailto:northshore at stratatitle.com.au>  | Address: PO Box 2727, Taren Point,
NSW 2229

 

 <http://www.stratatitle.com.au/>
cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
<http://www.facebook.com/StrataTitleManagement>
cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
<http://www.linkedin.com/company/strata-title-management-stm>
cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box
<http://www.twitter.com/STMStrata>
cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
<http://www.pinterest.com/STMStrata> pinterest.png
<http://plus.google.com/+StrataTitleManagemenSydney> google_plus.png

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website -
<http://www.stratatitle.com.au/disclaimer/>
www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: Brook Beves [mailto:brookbeves at bigpond.com] 
Sent: Thursday, 31 March 2016 3:03 PM
To: Patrick Rush
Cc: ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

Dear Katie/Patrick

You have seen the response from myself and Matt concerning this saga and we
would now seek the opinion of STM concerning this matter going back before
the Tribunal for a re-hearing. I do not believe the facts were properly put
to the Tribunal for their full consideration and I will be most willing to
represent the Owners Corporation at a further hearing.

Brook

Sent from my iPhone


On 31 Mar 2016, at 2:40 PM, Matt Perkins <matt at spectrum.com.au> wrote:

Hi Brook
This would also be my preferred option. If we indeed have that option. I
have asked Patrick his predecessors at STM this multiple times. I have never
received  and answer as to what the process is to challenge the ruling of
the tribunal.  

Matt.


On 31/03/2016 2:08 PM, Brook Beves wrote:

No. Firstly how much will this further cost the BC. Haven't we already spent
thousands on this issue ie engineers reports etc where is this going? As the
engineer originally opined the water does not penetrate the interior of 601
and is water dripping over the upper balcony onto the balcony of 601 which
are both common property. I would seek direction/advice from STM as to this
matter going back before the tribunal so these matters can be properly
litigated

Brook

Sent from my iPhone


On 31 Mar 2016, at 1:56 PM, Matt Perkins <matt at spectrum.com.au> wrote:

Sounds like a good option to me. All those in favor? 

Matt

On 31/03/2016 1:40 PM, Patrick Rush wrote:

Dear Committee,

 

The building manager has advised as follows:

'We have not carried out any dye test to that area and willing to arrange
Unplugged plumbing to carry out the testing. Please advise.'

 

We request that you confirm urgent instructions as to how you wish to
proceed.

Kind regards,

Katie Salim on behalf of 

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.png>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.png>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.png>     <http://www.twitter.com/STMStrata>
<mime-attachment.png>     <http://www.pinterest.com/STMStrata>
<mime-attachment.png>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.png>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Matt Perkins
Sent: Tuesday, 22 March 2016 5:21 PM
To: ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

I think the building Manager may have done this allready. Can we get some
input from the building manager. ? 


Matt

On 22/03/2016 4:42 PM, Patrick Rush wrote:

Dear Committee,

 

As you are aware we had requested Costin Roe Consulting Pty Ltd and Strata
Engineering Solutions agree to carry out further testing to Unit 601 and
provide the results at no extra cost to the Owners Corporation.

 

Costin Roe Consulting have replied as follows:

'As this is an external contractor I will have to seek approval from our
directors for the payment. As a quicker option I would suggest applying a
coloured dye along the northern edge of the terrace and running a hose on
it. If the water droplets take on the colour of the dye then it is clear
that the water is coming from the terrace.'

 

Please confirm how you wish to proceed.

Kind regards,

Katie Salim on behalf of 

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.png>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.png>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.png>     <http://www.twitter.com/STMStrata>
<mime-attachment.png>     <http://www.pinterest.com/STMStrata>
<mime-attachment.png>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.png>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: Patrick Rush 
Sent: Thursday, 10 March 2016 3:46 PM
To: 'Brook Beves'; 'Barney Kitay'; ec at 200william.com
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

 

Dear Committee,


Thank you and I will commence the process below and also make sure to advise
the Owner of Unit 601 what action has been taken to date.

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.png>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.png>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.png>     <http://www.twitter.com/STMStrata>
<mime-attachment.png>     <http://www.pinterest.com/STMStrata>
<mime-attachment.png>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.png>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: Brook Beves [mailto:brookbeves at bigpond.com] 
Sent: Tuesday, 8 March 2016 7:25 PM
To: 'Barney Kitay'; Patrick Rush; ec at 200william.com
Subject: RE: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

I agree

Brook

 


  _____  


From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Barney Kitay
Sent: Tuesday, 8 March 2016 6:18 PM
To: Patrick Rush; ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

Agreed. 

Thanks guys 

 

 

 

Kind regards

 

Barney

0400 200 446

 

Please excuse brevity. Sent from my Samsung Galaxy smartphone.



-------- Original message --------
From: Patrick Rush <prush at stratatitle.com.au> 
Date: 08/03/2016 18:34 (GMT+10:00) 
To: ec at 200william.com 
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851 

Dear Committee,


Can you please advise if you agree with Matt and my comments so that I can
proceed and advise the Owner of Unit 6021 the plan of action by the Owners
Corporation?

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.gif>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.gif>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.gif>     <http://www.twitter.com/STMStrata>
<mime-attachment.gif>     <http://www.pinterest.com/STMStrata>
<mime-attachment.gif>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.gif>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Matt Perkins
Sent: Tuesday, 8 March 2016 5:32 PM
To: ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

Thanks Patrick,
 I agree with your bellow comments. Can you also please keep the owner of
601 informed as to the direction of further testing to identify the water
ingress. 

I really think any further works that would not have been necessary had the
ingress been diagnosed correctly by the engineer be covered by the
engineer's PI insurance. 

Matt.


On 8/03/2016 9:56 AM, Patrick Rush wrote:

Dear Committee,

 

Please see attached invoices which I believe relate directly the inspections
and repairs carried out to Unit 601's balcony and the effervescence that was
part of the Fair trading NSW Tribunal Orders for the owners Corporation to
repair.

 

If I am correct and all of the attached invoices including work carried out
by Dribuild Concepts Pty Ltd, Robertson's Painting & Decorating and Strata
Engineering Solutions come to a total of $ 24,838.00 including GST.


As I believe most of these costs would not have been incurred if Strata
Engineering Solutions had originally diagnosed the issue being possibly the
planter box above requesting approval to carry out the Electric Field Vector
Mapping (EFVM) water testing to ascertain the exact location of the water
ingress to Unit 601's balcony then the Owners Corporation should I believe
request for this testing to be carried out an no charge by Strata
Engineering Solutions.

 

If in fact the water ingress is found due to this test then other expenses
that have been incurred can be actioned latter but at this stage the most
important issue is to resolve and rectify the water ingress issue Unit 601
has on their balcony.


Please advise if agree and as the EFVM cost $2,178.00 including GST, I can
request this be carried out at no cost due to the previous error in the
reporting by Strata Engineering Solutions.

 

William, can you advise if you have had a response from Lee as to if this
test will conclusively identify the source of the water ingress to Unit
601's balcony? Please also advise if you have any other input and can
confirm all the attached invoices are for work on Unit 601's balcony based
on the original report from Strata Engineering Solutions?

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email:  <mailto:northshore at stratatitle.com.au>
prush at stratatitle.com.au | Address: PO Box 2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.gif>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.gif>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.gif>     <http://www.twitter.com/STMStrata>
<mime-attachment.gif>     <http://www.pinterest.com/STMStrata>
<mime-attachment.gif>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.gif>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Matt Perkins
Sent: Wednesday, 2 March 2016 4:59 PM
To: ec at 200william.com
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

It's my understanding that the common area's that are being referred to is
the balcony and water dripping from the balcony edge above onto the balcony
used by 601 and Mr Laforests Furniture. Im sure George could confirm if he
is still available. 

Matt.




 On 2/03/2016 4:26 PM, Patrick Rush wrote:

Dear Committee,

 

Before I go any further and answer Matt's queries, can you please confirm
that the above is the order in which the Owners Corporation are attempting
to comply with?

 

As, if this is correct, can you confirm that the only items that are being
repaired are the water ingress issues into the kitchen area of unit 601 and
the common areas, whatever these may be?


I am not sure why references to the balcony and discolouration are being
made and why such maintenance needs to be undertaken if the above order is
what is being actioned.


Please advise?

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.gif>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.gif>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.gif>     <http://www.twitter.com/STMStrata>
<mime-attachment.gif>     <http://www.pinterest.com/STMStrata>
<mime-attachment.gif>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.gif>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Matt Perkins
Sent: Friday, 26 February 2016 2:48 PM
To: ec at 200william.com; lee.carroll at costinroe.com.au
Subject: Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal Order for
Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN
67851

 

Hi Patrick,
 It appears from Lee's report that the original advise to paint the surface
was incorrect as the source of water was not correctly identified. As a
result we will need to not only correctly identify the source of the water
but repaint the surface once the true source has been found. I note that the
report sites the building manager's report that guided the engineer. I find
this a little puzzling as is it not the engineers roll to test the building
manages assumptions. 

We have a number of issues here. 

Firstly. There is no money in the budget to investigate this problem further
even though we have been ordered by the tribunal to do so. 
Secondly. Is there any recourse through PI to recoup any of the money spent
due to the incorrect advice. 
Finally. Is there a mechanism where we can ask the tribunal to re-consider,
or extend the time frame which we have to comply given the budget
constraints. 

Other then one of the options above I see no other option less then to call
a EGM to vote on a Special Levy to fix the water leaks for Apartment 601
once true estimates have been gathered. 

Furthermore what would prevent every apartment in the building requesting
this type of water staining be eliminated from their balcony.  Every balcony
I have been on in the building including my own has this staining. I know in
my case it's from the above apartment's aluminum railing which is full of
water slowly dripping through.  Fixing these issues for the entire building
could add up to many hundreds of thousands of dollars where the problem is
only cosmetic and it is to appease one person.  

We are looking to guidance from STM here. So far professional advice has
only resulted in more and more money spent with zero gain to the strata and
more frustration to the owner of 601. 

In the mean time i suggest we go ahead with the testing as advised. 
Matt.

 

On 26/02/2016 2:13 PM, Lee Carroll wrote:

CO12765.00

 

Hi Patrick/William,

 

Please find attached our report subsequent to the site inspection on the
19th February.

 

Should you have any queries please don't hesitate to contact me.

 

 

Best Regards,

Lee Carroll
Senior Engineer (Remedial/Forensic)

<mime-attachment.gif>


Strata Engineering Solutions

A business of Costin Roe Consulting Pty Ltd
ABN 50 003 696 446

Level 1, 8 Windmill Street, Walsh Bay
PO Box N419, Sydney, NSW 1220 Australia
tel: +61 2 9251 7699 fax: +61 2 9241 3731 mobile:0448 -007-469 

email: Lee.Carroll at strataeng.com.au

web: www.strataeng.com.au

 

All our other details remain the same

Postal address:  PO Box N419, Sydney NSW 1220

Phone: 02-9251 7699     Fax: 02-9241 3731

Email: mail at costinroe.com.au     Email: mail at strataeng.com.au     Web:
www.costinroe.com.au

Offices in Sydney, Adelaide, Brisbane, Melbourne, Newcastle and Wollongong.

The information transmitted is intended only for the person or entity to
which it is addressed and may contain confidential and/or privileged
material.  Any review

retransmission, dissemination, or other use of, or taking of any action in
reliance upon, this information by persons or entities other than the
intended recipient is

prohibited.  If you receive this in error, please contact the sender and
delete the material from any computer.  It is the duty of the recipient to
virus scan and otherwise

test the information provided before loading it onto any computer system.
Costin Roe Consulting Pty Ltd does not warrant that the information is free
of a virus or any

other defect or error.

 


 

From: Patrick Rush [mailto:prush at stratatitle.com.au] 
Sent: Tuesday, 16 February 2016 5:18 PM
To: 'Info BFMS'; Lee Carroll
Cc: George Ziri; 'ec at 200william.com'
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

 

Hi William,


Craig, the Owner of unit 601 has contacted me and advised that he has
returned from overseas and is happy to be contacted to organise the
inspection as requested by the Committee.

 

Can you please organise and I will advsie Craig you will be in touch to
organise?

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.gif>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.gif>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.gif>     <http://www.twitter.com/STMStrata>
<mime-attachment.gif>     <http://www.pinterest.com/STMStrata>
<mime-attachment.gif>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.gif>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: Info BFMS [ <mailto:%5bmailto:info at bfms.com.au%5d>
mailto:info at bfms.com.au] 
Sent: Friday, 12 February 2016 9:17 AM
To: Patrick Rush; 'lee.carroll at costinroe.com.au'
Cc: George Ziri; 'ec at 200william.com'
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

 

Hi Lee

 

FYI

 

The lot owner Craig is currently away and returning next week.

 

 

For any further queries, please contact our office.

 

Kind regards,

 

<mime-attachment.gif>

 

From: Patrick Rush [mailto:prush at stratatitle.com.au] 
Sent: Thursday, 11 February 2016 3:39 PM
To: 'lee.carroll at costinroe.com.au' <lee.carroll at costinroe.com.au>
Cc: George Ziri <georgeziri at bfms.com.au>; Info BFMS <info at bfms.com.au>;
'ec at 200william.com' <ec at 200william.com>
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851
Importance: High

 

Hi Lee,

 

It has been requested by the Committee that you carry out a further
inspection of unit 601 in relation to the below further complaints and
attached images.


Can you please organise this inspection with the Building Manager and Craig,
the Owner of unit 601 and advsie when you will be completing the inspection
once organised.


Please provide a detailed report based on your inspection?

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.gif>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.gif>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.gif>     <http://www.twitter.com/STMStrata>
<mime-attachment.gif>     <http://www.pinterest.com/STMStrata>
<mime-attachment.gif>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.gif>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: Patrick Rush 
Sent: Thursday, 28 January 2016 1:43 PM
To: ec at 200william.com
Cc: George Ziri; Info BFMS
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851
Importance: High

 

Dear Committee,

 

Please see the below email from Craig, the Owner of Unit 601 in relation to
the NCAT (Tribunal) Orders for repairs to the areas causing water ingress to
the balcony area and other associated maintenance items.

 

Please see below answers in red from Craig in relation to Lee from Cost In
Roe's response to attending site to inspect.


Craig is obviously upset with the progress and feels the matter and repairs
undertaken late in 2015 have made the issue worse and require urgent
attention.


Craig's has asked me to seek some direction from you about this matter and
would like for you to advise the Building Manager, myself and the Engineers
to attend to the matter urgently to have further repairs undertaken to stop
further water leaking.

 

Please advise on the above urgently?

 

 

Kind regards,

Patrick Rush

Strata Manager

 

Phone: (02) 9266 2600 | Email: prush at stratatitle.com.au | Address: PO Box
2727, Taren Point, NSW 2229

 

 <http://www.stratatitle.com.au/> <mime-attachment.gif>
<http://www.facebook.com/StrataTitleManagement> <mime-attachment.gif>
<http://www.linkedin.com/company/strata-title-management-stm>
<mime-attachment.gif>     <http://www.twitter.com/STMStrata>
<mime-attachment.gif>     <http://www.pinterest.com/STMStrata>
<mime-attachment.gif>
<http://plus.google.com/+StrataTitleManagemenSydney> <mime-attachment.gif>

 

Emailed Communication / Documents Disclaimer

STM Limited takes no responsibility for content included in this email when
relating to a client matter. 

Please view Vesture's full email communication disclaimer on our website
-www.stratatitle.com.au/disclaimer/

Important Notice:  Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.

 

From: Lee Carroll [mailto:lee.carroll at costinroe.com.au] 
Sent: Thursday, 21 January 2016 5:03 PM
To: Info BFMS
Cc: George Ziri; ec at 200william.com; Patrick Rush; Catherine Plane; Wayne E.
Costin
Subject: 12765.00 160121 RE: SP 67851 - URGENT Tribunal Order for Water
Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

 

Hi William,

 

I have attached some photographs taken on the 22nd December 2015 on my last
site visit.

 

Whilst the bubbling is worse in your photographs, it is not dramatically so.

 

The area of bubbling and water dropping onto my terrace is 3 times more than
prior to the works being carried out recently by the contractor.  In
addition, the water has a dirt/rust colour which is staining everywhere
below the overhang.  The water is dropping through at a considerable rate
24/7 regardless of whether there is any rain.  This has been the same
problem for the last 8 years.

 

I would suggest we wait a bit longer before getting the painter back to
patch the effected areas.

 

The area doesn't need patching - we need to expose where the water is coming
from/through ie its source.

 

The bubbling and efflorescence appears to be mostly confined the slab edge
which is in keeping with my theory.

 

The rust staining on the paint bubbles is concerning as it indicates
corrosion of reinforcement in the concrete.

 

Again, why would we patch if rust staining is coming through?! Patching
cannot be completed quickly enough from the amount of water which is forcing
its way through.  As is currently happening patching only sends the water in
a different direction within the wall frame and subsequently water drops
through from a new area.

 

As discussed we had a job in Mosman awhile back with a similar issue. The
planter box has seven layers of membrane installed and yet the water
persisted. It turned out to be coming under the planter box from the terrace
area. There may be a similar issue here, although in my opinion there would
should also be water penetration visible on the soffit of the slab as the
slab edge if this was the case.

 

It should be noted that this is not water penetration into Unit 601. It is
merely

(merely??) water dripping off the slab edge over the balcony, which would be
expected anyway, at least when it rains. Again, the water drips constantly
24/7 even when there is NO rain.  The issue is the efflorescence and rust
staining on the tiles and furniture.

 

I have confirmed in previous email correspondence to the Strata Manager that
I will take the Body Corporate once taken to Tribunal.  Unless I receive
confirmation by February 16 that another way of handling this matter is to
take place, I will follow through with the Tribunal.

 

I have been advised by the representatives of the Tribunal that severe
penalties will be charged to the owners if the original order by the
Tribunal is not once and for all carried out.

Craig Laforest

 

Best Regards,

Lee Carroll
Senior Engineer (Remedial/Forensic)

<mime-attachment.gif>


Strata Engineering Solutions

A business of Costin Roe Consulting Pty Ltd
ABN 50 003 696 446

Level 1, 8 Windmill Street, Walsh Bay
PO Box N419, Sydney, NSW 1220 Australia
tel: +61 2 9251 7699 fax: +61 2 9241 3731 mobile:0448 -007-469 

email: Lee.Carroll at strataeng.com.au

web: www.strataeng.com.au

 

 

 

All our other details remain the same

Postal address:  PO Box N419, Sydney NSW 1220

Phone: 02-9251 7699     Fax: 02-9241 3731

Email:  <mailto:mail at costinroe.com.au> mail at costinroe.com.au     Email:
mail at strataeng.com.au     Web: www.costinroe.com.au

Offices in Sydney, Adelaide, Brisbane, Melbourne, Newcastle and Wollongong.

The information transmitted is intended only for the person or entity to
which it is addressed and may contain confidential and/or privileged
material.  Any review

retransmission, dissemination, or other use of, or taking of any action in
reliance upon, this information by persons or entities other than the
intended recipient is

prohibited.  If you receive this in error, please contact the sender and
delete the material from any computer.  It is the duty of the recipient to
virus scan and otherwise

test the information provided before loading it onto any computer system.
Costin Roe Consulting Pty Ltd does not warrant that the information is free
of a virus or any

other defect or error.

 


 

From: Info BFMS [mailto:info at bfms.com.au] 
Sent: Thursday, 21 January 2016 2:49 PM
To: Lee Carroll
Cc: George Ziri; ec at 200william.com; 'Patrick Rush'
Subject: RE: SP 67851 - URGENT Tribunal Order for Water Penetration in Unit
601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

 

Hi Lee

As discussed, please see attached photos of the water penetration in
apartment 601 for your reference.

Please advise.

 

 

 

For any further queries, please contact our office.

 

Kind regards,

 

<mime-attachment.gif>

 







_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec







-- 
/* Matt Perkins 
        Direct 1300 137 379        Spectrum Networks Ptd. Ltd. 
        Office 1300 133 299        matt at spectrum.com.au 
                                   Level 6, 350 George Street Sydney 2000
        Spectrum Networks is a member of the Communications Alliance & TIO  
*/






_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec






-- 
/* Matt Perkins 
        Direct 1300 137 379        Spectrum Networks Ptd. Ltd. 
        Office 1300 133 299        matt at spectrum.com.au 
                                   Level 6, 350 George Street Sydney 2000
        Spectrum Networks is a member of the Communications Alliance & TIO  
*/





_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec





-- 
/* Matt Perkins 
        Direct 1300 137 379        Spectrum Networks Ptd. Ltd. 
        Office 1300 133 299        matt at spectrum.com.au 
                                   Level 6, 350 George Street Sydney 2000
        Spectrum Networks is a member of the Communications Alliance & TIO  
*/





_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec





-- 
/* Matt Perkins 
        Direct 1300 137 379        Spectrum Networks Ptd. Ltd. 
        Office 1300 133 299        matt at spectrum.com.au 
                                   Level 6, 350 George Street Sydney 2000
        Spectrum Networks is a member of the Communications Alliance & TIO  
*/

 

_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec

 

-- 
/* Matt Perkins 
        Direct 1300 137 379        Spectrum Networks Ptd. Ltd. 
        Office 1300 133 299        matt at spectrum.com.au 
                                   Level 6, 350 George Street Sydney 2000
        Spectrum Networks is a member of the Communications Alliance & TIO  
*/

_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec

 

-- 
/* Matt Perkins 
        Direct 1300 137 379        Spectrum Networks Ptd. Ltd. 
        Office 1300 133 299        matt at spectrum.com.au 
                                   Level 6, 350 George Street Sydney 2000
        Spectrum Networks is a member of the Communications Alliance & TIO  
*/

-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0001.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1004 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0006.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 879 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0007.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 851 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0008.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 613 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0009.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 589 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0010.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1976 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/1e261511/attachment-0011.gif 


More information about the EC mailing list