[200William-EC SP67851] SP 67851 - URGENT Tribunal Order for Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851

Matt Perkins matt at spectrum.com.au
Tue Apr 19 11:22:57 AEST 2016


Thanks Brook. I agree and consent to your proposal.

Matt


On 19/04/2016 11:20 AM, Brook Beves wrote:
>
> Dear Patrick and Committee
>
> Thank you Patrick for your response.
>
> In the absence of ever having been provided with the Order of NCAT or 
> any correspondence or submissions made on behalf of the Owners 
> Corporation by STM, I have spoken at length with George Ziri formerly 
> of BFMS who is thoroughly familiar with the history of this issue and 
> work done and expenses incurred to date.
>
> It has been opined that the water ingress may be coming from 2 
> possible areas:
>
>  1. The planter boxes on the perimeter of level 7 although that area
>     was stripped of plants some years ago, re-waterproofed and the
>     problem was resolved devoid of any plants.
>  2. The raised round podiums on level 7 outside terrace area.  When
>     the entire level 7 terrace flooring was pulled up and re-tiled in
>     2009 the only area which was not re-surfaced was these raised
>     round podiums and it is possible that water is penetrating through
>     that area and seeping under the re-tiled terrace flooring.
>
> Subject to the cost of this dye testing being met by the Engineer who 
> has a “duty of care” to the Owners Corporation for their incorrect 
> professional assessment and rectification of this problem, I have no 
> objection to the further dye testing to:
>
> 1)The planter boxes where they meet the tiles; and
>
> 2)The raised round podiums
>
> The consent of the others member of the Executive Committee is sought.
>
> Many thanks
>
> Brook Beves
>
> ------------------------------------------------------------------------
>
> *From:*Patrick Rush [mailto:prush at stratatitle.com.au]
> *Sent:* Monday, 18 April 2016 12:48 PM
> *To:* 'Brook Beves'
> *Cc:* ec at 200william.com
> *Subject:* RE: SP 67851 - URGENT Tribunal Order for Water Penetration 
> in Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851
>
> Hi Brooke & Committee,
>
> I believe that as the water ingress may be coming from failed 
> waterproofing in the planter boxes above as advised by Lee, the Engineer.
>
> I believe that the Owners Corporation should be pushing for the 
> testing to be carried out on these planter boxes to then be advised 
> where exactly the source of the water ingress is.
>
> As Craig, is pushing to now take the Owners Corporation back to Fair 
> Trading (Tribunal) with this matter I believe this to be the best 
> option and then once the source of the water leak has been identified 
> then further action can be taken or not depending on the source.
>
>
> Please advise if you agree with this approach and i will again email 
> Lee and advise the Owners Corporation believe the costs of such 
> testing should be at no extra cost.
>
>
> Apologies for the delay, I was unwell and off work all of last week!
>
> Kind regards,
>
> *Patrick Rush*
>
> Strata Manager
>
> Phone:(02) 9266 2600 | Email:prush at stratatitle.com.au 
> <mailto:northshore at stratatitle.com.au> | Address:PO Box2727, Taren 
> Point, NSW 2229
>
> **
>
> cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box 
> <http://www.stratatitle.com.au/>cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box 
> <http://www.facebook.com/StrataTitleManagement>cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box<http://www.linkedin.com/company/strata-title-management-stm>cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box 
> <http://www.twitter.com/STMStrata>pinterest.png 
> <http://www.pinterest.com/STMStrata>google_plus.png 
> <http://plus.google.com/+StrataTitleManagemenSydney>
>
> **
>
> *Emailed Communication / Documents Disclaimer*
>
> STM Limited takes no responsibility for content included in this email 
> when relating to a client matter.
>
> Please view Vesture’s full email communication disclaimer on our 
> website –www.stratatitle.com.au/disclaimer/ 
> <http://www.stratatitle.com.au/disclaimer/>
>
> *Important Notice: *Owners should be aware that all correspondence, 
> including letters, facsimile transmissions and emails are retained on 
> the file of your scheme and may be subject to inspection by owners and 
> residents within your scheme, as well as prospective purchasers for 
> any lot that may be for sale within your scheme. As such author 
> discretion is advised.
>
> *From:*Brook Beves [mailto:brookbeves at bigpond.com]
> *Sent:* Thursday, 31 March 2016 3:03 PM
> *To:* Patrick Rush
> *Cc:* ec at 200william.com
> *Subject:* Re: [200William-EC SP67851] SP 67851 - URGENT Tribunal 
> Order for Water Penetration in Unit 601 - CRAIG LAFOREST VS BODY 
> CORPORATE STRATA PLAN 67851
>
> Dear Katie/Patrick
>
> You have seen the response from myself and Matt concerning this saga 
> and we would now seek the opinion of STM concerning this matter going 
> back before the Tribunal for a re-hearing. I do not believe the facts 
> were properly put to the Tribunal for their full consideration and I 
> will be most willing to represent the Owners Corporation at a further 
> hearing.
>
> Brook
>
> Sent from my iPhone
>
>
> On 31 Mar 2016, at 2:40 PM, Matt Perkins <matt at spectrum.com.au 
> <mailto:matt at spectrum.com.au>> wrote:
>
>     Hi Brook
>     This would also be my preferred option. If we indeed have that
>     option. I have asked Patrick his predecessors at STM this multiple
>     times. I have never received  and answer as to what the process is
>     to challenge the ruling of the tribunal.
>
>     Matt.
>
>
>     On 31/03/2016 2:08 PM, Brook Beves wrote:
>
>         No. Firstly how much will this further cost the BC. Haven't we
>         already spent thousands on this issue ie engineers reports etc
>         where is this going? As the engineer originally opined the
>         water does not penetrate the interior of 601 and is water
>         dripping over the upper balcony onto the balcony of 601 which
>         are both common property. I would seek direction/advice from
>         STM as to this matter going back before the tribunal so these
>         matters can be properly litigated
>
>         Brook
>
>         Sent from my iPhone
>
>
>         On 31 Mar 2016, at 1:56 PM, Matt Perkins <matt at spectrum.com.au
>         <mailto:matt at spectrum.com.au>> wrote:
>
>             Sounds like a good option to me. All those in favor?
>
>             Matt
>
>             On 31/03/2016 1:40 PM, Patrick Rush wrote:
>
>                 Dear Committee,
>
>                 The building manager has advised as follows:
>
>                 /‘//We have not carried out any dye test to that area
>                 and willing to arrange Unplugged plumbing to carry out
>                 the testing. Please advise.’/
>
>                 We request that you confirm urgent instructions as to
>                 how you wish to proceed.
>
>                 Kind regards,
>
>                 *Katie Salim on behalf of *
>
>                 *Patrick Rush*
>
>                 Strata Manager
>
>                 Phone:(02) 9266 2600 | Email:prush at stratatitle.com.au
>                 <mailto:prush at stratatitle.com.au> | Address:PO
>                 Box2727, Taren Point, NSW 2229
>
>                 **
>
>                 <mime-attachment.png>
>                 <http://www.stratatitle.com.au/><mime-attachment.png>
>                 <http://www.facebook.com/StrataTitleManagement><mime-attachment.png><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.png>
>                 <http://www.twitter.com/STMStrata><mime-attachment.png> <http://www.pinterest.com/STMStrata><mime-attachment.png>
>                 <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                 **
>
>                 *Emailed Communication / Documents Disclaimer*
>
>                 STM Limited takes no responsibility for content
>                 included in this email when relating to a client matter.
>
>                 Please view Vesture’s full email communication
>                 disclaimer on our website
>                 –www.stratatitle.com.au/disclaimer/
>                 <http://www.stratatitle.com.au/disclaimer/>
>
>                 *Important Notice: *Owners should be aware that all
>                 correspondence, including letters, facsimile
>                 transmissions and emails are retained on the file of
>                 your scheme and may be subject to inspection by owners
>                 and residents within your scheme, as well as
>                 prospective purchasers for any lot that may be for
>                 sale within your scheme. As such author discretion is
>                 advised.
>
>                 *From:*ec-bounces at 200william.com
>                 <mailto:ec-bounces at 200william.com>
>                 [mailto:ec-bounces at 200william.com] *On Behalf Of *Matt
>                 Perkins
>                 *Sent:* Tuesday, 22 March 2016 5:21 PM
>                 *To:* ec at 200william.com <mailto:ec at 200william.com>
>                 *Subject:* Re: [200William-EC SP67851] SP 67851 -
>                 URGENT Tribunal Order for Water Penetration in Unit
>                 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA PLAN 67851
>
>                 I think the building Manager may have done this
>                 allready. Can we get some input from the building
>                 manager. ?
>
>
>                 Matt
>
>                 On 22/03/2016 4:42 PM, Patrick Rush wrote:
>
>                     Dear Committee,
>
>                     As you are aware we had requested Costin Roe
>                     Consulting Pty Ltd and Strata Engineering
>                     Solutions agree to carry out further testing to
>                     Unit 601 and provide the results at no extra cost
>                     to the Owners Corporation.
>
>                     Costin Roe Consulting have replied as follows:
>
>                     /‘As this is an external contractor I will have to
>                     seek approval from our directors for the payment.
>                     As a quicker option I would suggest applying a
>                     coloured dye along the northern edge of the
>                     terrace and running a hose on it. If the water
>                     droplets take on the colour of the dye then it is
>                     clear that the water is coming from the terrace.’/
>
>                     Please confirm how you wish to proceed.
>
>                     Kind regards,
>
>                     *Katie Salim on behalf of *
>
>                     *Patrick Rush*
>
>                     Strata Manager
>
>                     Phone:(02) 9266 2600 |
>                     Email:prush at stratatitle.com.au
>                     <mailto:prush at stratatitle.com.au> | Address:PO
>                     Box2727, Taren Point, NSW 2229
>
>                     **
>
>                     <mime-attachment.png>
>                     <http://www.stratatitle.com.au/><mime-attachment.png>
>                     <http://www.facebook.com/StrataTitleManagement><mime-attachment.png><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.png>
>                     <http://www.twitter.com/STMStrata><mime-attachment.png>
>                     <http://www.pinterest.com/STMStrata><mime-attachment.png>
>                     <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                     **
>
>                     *Emailed Communication / Documents Disclaimer*
>
>                     STM Limited takes no responsibility for content
>                     included in this email when relating to a client
>                     matter.
>
>                     Please view Vesture’s full email communication
>                     disclaimer on our website
>                     –www.stratatitle.com.au/disclaimer/
>                     <http://www.stratatitle.com.au/disclaimer/>
>
>                     *Important Notice: *Owners should be aware that
>                     all correspondence, including letters, facsimile
>                     transmissions and emails are retained on the file
>                     of your scheme and may be subject to inspection by
>                     owners and residents within your scheme, as well
>                     as prospective purchasers for any lot that may be
>                     for sale within your scheme. As such author
>                     discretion is advised.
>
>                     *From:*Patrick Rush
>                     *Sent:* Thursday, 10 March 2016 3:46 PM
>                     *To:* 'Brook Beves'; 'Barney Kitay';
>                     ec at 200william.com <mailto:ec at 200william.com>
>                     *Subject:* RE: SP 67851 - URGENT Tribunal Order
>                     for Water Penetration in Unit 601 - CRAIG LAFOREST
>                     VS BODY CORPORATE STRATA PLAN 67851
>
>                     Dear Committee,
>
>
>                     Thank you and I will commence the process below
>                     and also make sure to advise the Owner of Unit 601
>                     what action has been taken to date.
>
>                     Kind regards,
>
>                     *Patrick Rush*
>
>                     Strata Manager
>
>                     Phone:(02) 9266 2600 |
>                     Email:prush at stratatitle.com.au
>                     <mailto:prush at stratatitle.com.au> | Address:PO
>                     Box2727, Taren Point, NSW 2229
>
>                     **
>
>                     <mime-attachment.png>
>                     <http://www.stratatitle.com.au/><mime-attachment.png>
>                     <http://www.facebook.com/StrataTitleManagement><mime-attachment.png><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.png>
>                     <http://www.twitter.com/STMStrata><mime-attachment.png>
>                     <http://www.pinterest.com/STMStrata><mime-attachment.png>
>                     <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                     **
>
>                     *Emailed Communication / Documents Disclaimer*
>
>                     STM Limited takes no responsibility for content
>                     included in this email when relating to a client
>                     matter.
>
>                     Please view Vesture’s full email communication
>                     disclaimer on our website
>                     –www.stratatitle.com.au/disclaimer/
>                     <http://www.stratatitle.com.au/disclaimer/>
>
>                     *Important Notice: *Owners should be aware that
>                     all correspondence, including letters, facsimile
>                     transmissions and emails are retained on the file
>                     of your scheme and may be subject to inspection by
>                     owners and residents within your scheme, as well
>                     as prospective purchasers for any lot that may be
>                     for sale within your scheme. As such author
>                     discretion is advised.
>
>                     *From:*Brook Beves [mailto:brookbeves at bigpond.com]
>                     *Sent:* Tuesday, 8 March 2016 7:25 PM
>                     *To:* 'Barney Kitay'; Patrick Rush;
>                     ec at 200william.com <mailto:ec at 200william.com>
>                     *Subject:* RE: [200William-EC SP67851] SP 67851 -
>                     URGENT Tribunal Order for Water Penetration in
>                     Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA
>                     PLAN 67851
>
>                     I agree
>
>                     Brook
>
>                     ------------------------------------------------------------------------
>
>                     *From:*ec-bounces at 200william.com
>                     <mailto:ec-bounces at 200william.com>
>                     [mailto:ec-bounces at 200william.com] *On Behalf Of
>                     *Barney Kitay
>                     *Sent:* Tuesday, 8 March 2016 6:18 PM
>                     *To:* Patrick Rush; ec at 200william.com
>                     <mailto:ec at 200william.com>
>                     *Subject:* Re: [200William-EC SP67851] SP 67851 -
>                     URGENT Tribunal Order for Water Penetration in
>                     Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA
>                     PLAN 67851
>
>                     Agreed.
>
>                     Thanks guys
>
>                     Kind regards
>
>                     Barney
>
>                     0400 200 446
>
>                     Please excuse brevity. Sent from my Samsung Galaxy
>                     smartphone.
>
>
>
>                     -------- Original message --------
>                     From: Patrick Rush <prush at stratatitle.com.au
>                     <mailto:prush at stratatitle.com.au>>
>                     Date: 08/03/2016 18:34 (GMT+10:00)
>                     To: ec at 200william.com <mailto:ec at 200william.com>
>                     Subject: Re: [200William-EC SP67851] SP 67851 -
>                     URGENT Tribunal Order for Water Penetration in
>                     Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA
>                     PLAN 67851
>
>                     Dear Committee,
>
>
>                     Can you please advise if you agree with Matt and
>                     my comments so that I can proceed and advise the
>                     Owner of Unit 6021 the plan of action by the
>                     Owners Corporation?
>
>                     Kind regards,
>
>                     *Patrick Rush*
>
>                     Strata Manager
>
>                     Phone:(02) 9266 2600 |
>                     Email:prush at stratatitle.com.au
>                     <mailto:prush at stratatitle.com.au> | Address:PO
>                     Box2727, Taren Point, NSW 2229
>
>                     **
>
>                     <mime-attachment.gif>
>                     <http://www.stratatitle.com.au/><mime-attachment.gif>
>                     <http://www.facebook.com/StrataTitleManagement><mime-attachment.gif><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.gif>
>                     <http://www.twitter.com/STMStrata><mime-attachment.gif>
>                     <http://www.pinterest.com/STMStrata><mime-attachment.gif>
>                     <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                     **
>
>                     *Emailed Communication / Documents Disclaimer*
>
>                     STM Limited takes no responsibility for content
>                     included in this email when relating to a client
>                     matter.
>
>                     Please view Vesture’s full email communication
>                     disclaimer on our website
>                     –www.stratatitle.com.au/disclaimer/
>                     <http://www.stratatitle.com.au/disclaimer/>
>
>                     *Important Notice: *Owners should be aware that
>                     all correspondence, including letters, facsimile
>                     transmissions and emails are retained on the file
>                     of your scheme and may be subject to inspection by
>                     owners and residents within your scheme, as well
>                     as prospective purchasers for any lot that may be
>                     for sale within your scheme. As such author
>                     discretion is advised.
>
>                     *From:*ec-bounces at 200william.com
>                     <mailto:ec-bounces at 200william.com>
>                     [mailto:ec-bounces at 200william.com] *On Behalf Of
>                     *Matt Perkins
>                     *Sent:* Tuesday, 8 March 2016 5:32 PM
>                     *To:* ec at 200william.com <mailto:ec at 200william.com>
>                     *Subject:* Re: [200William-EC SP67851] SP 67851 -
>                     URGENT Tribunal Order for Water Penetration in
>                     Unit 601 - CRAIG LAFOREST VS BODY CORPORATE STRATA
>                     PLAN 67851
>
>                     Thanks Patrick,
>                      I agree with your bellow comments. Can you also
>                     please keep the owner of 601 informed as to the
>                     direction of further testing to identify the water
>                     ingress.
>
>                     I really think any further works that would not
>                     have been necessary had the ingress been diagnosed
>                     correctly by the engineer be covered by the
>                     engineer's PI insurance.
>
>                     Matt.
>
>
>                     On 8/03/2016 9:56 AM, Patrick Rush wrote:
>
>                         Dear Committee,
>
>                         Please see attached invoices which I believe
>                         relate directly the inspections and repairs
>                         carried out to Unit 601’s balcony and the
>                         effervescence that was part of the Fair
>                         trading NSW Tribunal Orders for the owners
>                         Corporation to repair.
>
>                         If I am correct and all of the attached
>                         invoices including work carried out by
>                         Dribuild Concepts Pty Ltd, Robertson’s
>                         Painting & Decorating and Strata Engineering
>                         Solutions come to a total of $ 24,838.00
>                         including GST.
>
>
>                         As I believe most of these costs would not
>                         have been incurred if Strata Engineering
>                         Solutions had originally diagnosed the issue
>                         being possibly the planter box above
>                         requesting approval to carry out the Electric
>                         Field Vector Mapping (EFVM) water testing to
>                         ascertain the exact location of the water
>                         ingress to Unit 601’s balcony then the Owners
>                         Corporation should I believe request for this
>                         testing to be carried out an no charge by
>                         Strata Engineering Solutions.
>
>                         If in fact the water ingress is found due to
>                         this test then other expenses that have been
>                         incurred can be actioned latter but at this
>                         stage the most important issue is to resolve
>                         and rectify the water ingress issue Unit 601
>                         has on their balcony.
>
>
>                         Please advise if agree and as the EFVM cost
>                         $2,178.00 including GST, I can request this be
>                         carried out at no cost due to the previous
>                         error in the reporting by Strata Engineering
>                         Solutions.
>
>                         William, can you advise if you have had a
>                         response from Lee as to if this test will
>                         conclusively identify the source of the water
>                         ingress to Unit 601’s balcony? Please also
>                         advise if you have any other input and can
>                         confirm all the attached invoices are for work
>                         on Unit 601’s balcony based on the original
>                         report from Strata Engineering Solutions?
>
>                         Kind regards,
>
>                         *Patrick Rush*
>
>                         Strata Manager
>
>                         Phone:(02) 9266 2600 |
>                         Email:prush at stratatitle.com.au
>                         <mailto:northshore at stratatitle.com.au> |
>                         Address:PO Box2727, Taren Point, NSW 2229
>
>                         **
>
>                         <mime-attachment.gif>
>                         <http://www.stratatitle.com.au/><mime-attachment.gif>
>                         <http://www.facebook.com/StrataTitleManagement><mime-attachment.gif><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.gif>
>                         <http://www.twitter.com/STMStrata><mime-attachment.gif>
>                         <http://www.pinterest.com/STMStrata><mime-attachment.gif>
>                         <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                         **
>
>                         *Emailed Communication / Documents Disclaimer*
>
>                         STM Limited takes no responsibility for
>                         content included in this email when relating
>                         to a client matter.
>
>                         Please view Vesture’s full email communication
>                         disclaimer on our website
>                         –www.stratatitle.com.au/disclaimer/
>                         <http://www.stratatitle.com.au/disclaimer/>
>
>                         *Important Notice: *Owners should be aware
>                         that all correspondence, including letters,
>                         facsimile transmissions and emails are
>                         retained on the file of your scheme and may be
>                         subject to inspection by owners and residents
>                         within your scheme, as well as prospective
>                         purchasers for any lot that may be for sale
>                         within your scheme. As such author discretion
>                         is advised.
>
>                         *From:*ec-bounces at 200william.com
>                         <mailto:ec-bounces at 200william.com>
>                         [mailto:ec-bounces at 200william.com] *On Behalf
>                         Of *Matt Perkins
>                         *Sent:* Wednesday, 2 March 2016 4:59 PM
>                         *To:* ec at 200william.com <mailto:ec at 200william.com>
>                         *Subject:* Re: [200William-EC SP67851] SP
>                         67851 - URGENT Tribunal Order for Water
>                         Penetration in Unit 601 - CRAIG LAFOREST VS
>                         BODY CORPORATE STRATA PLAN 67851
>
>                         It's my understanding that the common area's
>                         that are being referred to is the balcony and
>                         water dripping from the balcony edge above
>                         onto the balcony used by 601 and Mr Laforests
>                         Furniture. Im sure George could confirm if he
>                         is still available.
>
>                         Matt.
>
>
>
>
>                          On 2/03/2016 4:26 PM, Patrick Rush wrote:
>
>                             Dear Committee,
>
>                             Before I go any further and answer Matt’s
>                             queries, can you please confirm that the
>                             above is the order in which the Owners
>                             Corporation are attempting to comply with?
>
>                             As, if this is correct, can you confirm
>                             that the only items that are being
>                             repaired are the water ingress issues into
>                             the kitchen area of unit 601 and the
>                             common areas, whatever these may be?
>
>
>                             I am not sure why references to the
>                             balcony and discolouration are being made
>                             and why such maintenance needs to be
>                             undertaken if the above order is what is
>                             being actioned.
>
>
>                             Please advise?
>
>                             Kind regards,
>
>                             *Patrick Rush*
>
>                             Strata Manager
>
>                             Phone:(02) 9266 2600 |
>                             Email:prush at stratatitle.com.au
>                             <mailto:prush at stratatitle.com.au> |
>                             Address:PO Box2727, Taren Point, NSW 2229
>
>                             **
>
>                             <mime-attachment.gif>
>                             <http://www.stratatitle.com.au/><mime-attachment.gif>
>                             <http://www.facebook.com/StrataTitleManagement><mime-attachment.gif><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.gif>
>                             <http://www.twitter.com/STMStrata><mime-attachment.gif>
>                             <http://www.pinterest.com/STMStrata><mime-attachment.gif>
>                             <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                             **
>
>                             *Emailed Communication / Documents Disclaimer*
>
>                             STM Limited takes no responsibility for
>                             content included in this email when
>                             relating to a client matter.
>
>                             Please view Vesture’s full email
>                             communication disclaimer on our website
>                             –www.stratatitle.com.au/disclaimer/
>                             <http://www.stratatitle.com.au/disclaimer/>
>
>                             *Important Notice: *Owners should be aware
>                             that all correspondence, including
>                             letters, facsimile transmissions and
>                             emails are retained on the file of your
>                             scheme and may be subject to inspection by
>                             owners and residents within your scheme,
>                             as well as prospective purchasers for any
>                             lot that may be for sale within your
>                             scheme. As such author discretion is advised.
>
>                             *From:*ec-bounces at 200william.com
>                             <mailto:ec-bounces at 200william.com>
>                             [mailto:ec-bounces at 200william.com] *On
>                             Behalf Of *Matt Perkins
>                             *Sent:* Friday, 26 February 2016 2:48 PM
>                             *To:* ec at 200william.com
>                             <mailto:ec at 200william.com>;
>                             lee.carroll at costinroe.com.au
>                             <mailto:lee.carroll at costinroe.com.au>
>                             *Subject:* Re: [200William-EC SP67851] SP
>                             67851 - URGENT Tribunal Order for Water
>                             Penetration in Unit 601 - CRAIG LAFOREST
>                             VS BODY CORPORATE STRATA PLAN 67851
>
>                             Hi Patrick,
>                              It appears from Lee's report that the
>                             original advise to paint the surface was
>                             incorrect as the source of water was not
>                             correctly identified. As a result we will
>                             need to not only correctly identify the
>                             source of the water but repaint the
>                             surface once the true source has been
>                             found. I note that the report sites the
>                             building manager's report that guided the
>                             engineer. I find this a little puzzling as
>                             is it not the engineers roll to test the
>                             building manages assumptions.
>
>                             We have a number of issues here.
>
>                             Firstly. There is no money in the budget
>                             to investigate this problem further  even
>                             though we have been ordered by the
>                             tribunal to do so.
>                             Secondly. Is there any recourse through PI
>                             to recoup any of the money spent due to
>                             the incorrect advice.
>                             Finally. Is there a mechanism where we can
>                             ask the tribunal to re-consider, or extend
>                             the time frame which we have to comply
>                             given the budget constraints.
>
>                             Other then one of the options above I see
>                             no other option less then to call a EGM to
>                             vote on a Special Levy to fix the water
>                             leaks for Apartment 601 once true
>                             estimates have been gathered.
>
>                             Furthermore what would prevent every
>                             apartment in the building requesting this
>                             type of water staining be eliminated from
>                             their balcony.  Every balcony I have been
>                             on in the building including my own has
>                             this staining. I know in my case it's from
>                             the above apartment's aluminum railing
>                             which is full of water slowly dripping
>                             through.  Fixing these issues for the
>                             entire building could add up to many
>                             hundreds of thousands of dollars where the
>                             problem is only cosmetic and it is to
>                             appease one person.
>
>                             We are looking to guidance from STM here.
>                             So far professional advice has only
>                             resulted in more and more money spent with
>                             zero gain to the strata and more
>                             frustration to the owner of 601.
>
>                             In the mean time i suggest we go ahead
>                             with the testing as advised.
>                             Matt.
>
>
>
>                             On 26/02/2016 2:13 PM, Lee Carroll wrote:
>
>                                 *CO12765.00*
>
>                                 Hi Patrick/William,
>
>                                 Please find attached our report
>                                 subsequent to the site inspection on
>                                 the 19^th February.
>
>                                 Should you have any queries please
>                                 don’t hesitate to contact me.
>
>                                 Best Regards,
>
>                                 *Lee Carroll
>                                 **Senior Engineer (Remedial/Forensic)*
>
>                                 <mime-attachment.gif>
>
>
>                                 Strata Engineering Solutions
>
>                                 A business of Costin Roe Consulting
>                                 Pty Ltd
>                                 ABN 50 003 696 446
>
>                                 Level 1, 8 Windmill Street, Walsh Bay
>                                 PO Box N419, Sydney, NSW 1220 Australia
>                                 tel: +61 2 9251 7699 fax: +61 2 9241
>                                 3731 mobile:0448 -007-469
>
>                                 email: Lee.Carroll at strataeng.com.au
>                                 <mailto:Lee.Carroll at strataeng.com.au>
>
>                                 web: www.strataeng.com.au
>                                 <http://www.strataeng.com.au>
>
>                                 All our other details remain the same
>
>                                 Postal address: PO Box N419, Sydney
>                                 NSW 1220
>
>                                 Phone: 02-9251 7699 Fax: 02-9241 3731
>
>                                 Email: mail at costinroe.com.au
>                                 <mailto:mail at costinroe.com.au> Email:
>                                 mail at strataeng.com.au
>                                 <mailto:mail at strataeng.com.au> Web:
>                                 www.costinroe.com.au
>                                 <http://www.costinroe.com.au>
>
>                                 *Offices in Sydney, Adelaide,
>                                 Brisbane, Melbourne, Newcastle and
>                                 Wollongong.*
>
>                                 The information transmitted is
>                                 intended only for the person or entity
>                                 to which it is addressed and may
>                                 contain confidential and/or privileged
>                                 material.  Any review
>
>                                 retransmission, dissemination, or
>                                 other use of, or taking of any action
>                                 in reliance upon, this information by
>                                 persons or entities other than the
>                                 intended recipient is
>
>                                 prohibited. If you receive this in
>                                 error, please contact the sender and
>                                 delete the material from any
>                                 computer.  It is the duty of the
>                                 recipient to virus scan and otherwise
>
>                                 test the information provided before
>                                 loading it onto any computer system. 
>                                 Costin Roe Consulting Pty Ltd does not
>                                 warrant that the information is free
>                                 of a virus or any
>
>                                 other defect or error.
>
>
>                                 *From:*Patrick Rush
>                                 [mailto:prush at stratatitle.com.au]
>                                 *Sent:* Tuesday, 16 February 2016 5:18 PM
>                                 *To:* 'Info BFMS'; Lee Carroll
>                                 *Cc:* George Ziri; 'ec at 200william.com
>                                 <mailto:ec at 200william.com>'
>                                 *Subject:* RE: SP 67851 - URGENT
>                                 Tribunal Order for Water Penetration
>                                 in Unit 601 - CRAIG LAFOREST VS BODY
>                                 CORPORATE STRATA PLAN 67851
>
>                                 Hi William,
>
>
>                                 Craig, the Owner of unit 601 has
>                                 contacted me and advised that he has
>                                 returned from overseas and is happy to
>                                 be contacted to organise the
>                                 inspection as requested by the Committee.
>
>                                 Can you please organise and I will
>                                 advsie Craig you will be in touch to
>                                 organise?
>
>                                 Kind regards,
>
>                                 *Patrick Rush*
>
>                                 Strata Manager
>
>                                 Phone:(02) 9266 2600 |
>                                 Email:prush at stratatitle.com.au
>                                 <mailto:prush at stratatitle.com.au> |
>                                 Address:PO Box2727, Taren Point, NSW 2229
>
>                                 **
>
>                                 <mime-attachment.gif>
>                                 <http://www.stratatitle.com.au/><mime-attachment.gif>
>                                 <http://www.facebook.com/StrataTitleManagement><mime-attachment.gif><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.gif>
>                                 <http://www.twitter.com/STMStrata><mime-attachment.gif>
>                                 <http://www.pinterest.com/STMStrata><mime-attachment.gif>
>                                 <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                                 **
>
>                                 *Emailed Communication / Documents
>                                 Disclaimer*
>
>                                 STM Limited takes no responsibility
>                                 for content included in this email
>                                 when relating to a client matter.
>
>                                 Please view Vesture’s full email
>                                 communication disclaimer on our
>                                 website
>                                 –www.stratatitle.com.au/disclaimer/
>                                 <http://www.stratatitle.com.au/disclaimer/>
>
>                                 *Important Notice: *Owners should be
>                                 aware that all correspondence,
>                                 including letters, facsimile
>                                 transmissions and emails are retained
>                                 on the file of your scheme and may be
>                                 subject to inspection by owners and
>                                 residents within your scheme, as well
>                                 as prospective purchasers for any lot
>                                 that may be for sale within your
>                                 scheme. As such author discretion is
>                                 advised.
>
>                                 *From:*Info BFMS [
>                                 <mailto:%5bmailto:info at bfms.com.au%5d>mailto:info at bfms.com.au]
>
>                                 *Sent:* Friday, 12 February 2016 9:17 AM
>                                 *To:* Patrick Rush;
>                                 'lee.carroll at costinroe.com.au
>                                 <mailto:lee.carroll at costinroe.com.au>'
>                                 *Cc:* George Ziri; 'ec at 200william.com
>                                 <mailto:ec at 200william.com>'
>                                 *Subject:* RE: SP 67851 - URGENT
>                                 Tribunal Order for Water Penetration
>                                 in Unit 601 - CRAIG LAFOREST VS BODY
>                                 CORPORATE STRATA PLAN 67851
>
>                                 Hi Lee
>
>                                 FYI
>
>                                 The lot owner Craig is currently away
>                                 and returning next week.
>
>                                 For any further queries, please
>                                 contact our office.
>
>                                 Kind regards,
>
>                                 <mime-attachment.gif>
>
>                                 *From:*Patrick Rush
>                                 [mailto:prush at stratatitle.com.au]
>                                 *Sent:* Thursday, 11 February 2016 3:39 PM
>                                 *To:* 'lee.carroll at costinroe.com.au
>                                 <mailto:lee.carroll at costinroe.com.au>'
>                                 <lee.carroll at costinroe.com.au
>                                 <mailto:lee.carroll at costinroe.com.au>>
>                                 *Cc:* George Ziri
>                                 <georgeziri at bfms.com.au
>                                 <mailto:georgeziri at bfms.com.au>>; Info
>                                 BFMS <info at bfms.com.au
>                                 <mailto:info at bfms.com.au>>;
>                                 'ec at 200william.com
>                                 <mailto:ec at 200william.com>'
>                                 <ec at 200william.com
>                                 <mailto:ec at 200william.com>>
>                                 *Subject:* RE: SP 67851 - URGENT
>                                 Tribunal Order for Water Penetration
>                                 in Unit 601 - CRAIG LAFOREST VS BODY
>                                 CORPORATE STRATA PLAN 67851
>                                 *Importance:* High
>
>                                 Hi Lee,
>
>                                 It has been requested by the Committee
>                                 that you carry out a further
>                                 inspection of unit 601 in relation to
>                                 the below further complaints and
>                                 attached images.
>
>
>                                 Can you please organise this
>                                 inspection with the Building Manager
>                                 and Craig, the Owner of unit 601 and
>                                 advsie when you will be completing the
>                                 inspection once organised.
>
>
>                                 Please provide a detailed report based
>                                 on your inspection?
>
>                                 Kind regards,
>
>                                 *Patrick Rush*
>
>                                 Strata Manager
>
>                                 Phone:(02) 9266 2600 |
>                                 Email:prush at stratatitle.com.au
>                                 <mailto:prush at stratatitle.com.au> |
>                                 Address:PO Box2727, Taren Point, NSW 2229
>
>                                 **
>
>                                 <mime-attachment.gif>
>                                 <http://www.stratatitle.com.au/><mime-attachment.gif>
>                                 <http://www.facebook.com/StrataTitleManagement><mime-attachment.gif><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.gif>
>                                 <http://www.twitter.com/STMStrata><mime-attachment.gif>
>                                 <http://www.pinterest.com/STMStrata><mime-attachment.gif>
>                                 <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                                 **
>
>                                 *Emailed Communication / Documents
>                                 Disclaimer*
>
>                                 STM Limited takes no responsibility
>                                 for content included in this email
>                                 when relating to a client matter.
>
>                                 Please view Vesture’s full email
>                                 communication disclaimer on our
>                                 website
>                                 –www.stratatitle.com.au/disclaimer/
>                                 <http://www.stratatitle.com.au/disclaimer/>
>
>                                 *Important Notice: *Owners should be
>                                 aware that all correspondence,
>                                 including letters, facsimile
>                                 transmissions and emails are retained
>                                 on the file of your scheme and may be
>                                 subject to inspection by owners and
>                                 residents within your scheme, as well
>                                 as prospective purchasers for any lot
>                                 that may be for sale within your
>                                 scheme. As such author discretion is
>                                 advised.
>
>                                 *From:*Patrick Rush
>                                 *Sent:* Thursday, 28 January 2016 1:43 PM
>                                 *To:* ec at 200william.com
>                                 <mailto:ec at 200william.com>
>                                 *Cc:* George Ziri; Info BFMS
>                                 *Subject:* RE: SP 67851 - URGENT
>                                 Tribunal Order for Water Penetration
>                                 in Unit 601 - CRAIG LAFOREST VS BODY
>                                 CORPORATE STRATA PLAN 67851
>                                 *Importance:* High
>
>                                 Dear Committee,
>
>                                 Please see the below email from Craig,
>                                 the Owner of Unit 601 in relation to
>                                 the NCAT (Tribunal) Orders for repairs
>                                 to the areas causing water ingress to
>                                 the balcony area and other associated
>                                 maintenance items.
>
>                                 Please see below answers in red from
>                                 Craig in relation to Lee from Cost In
>                                 Roe’s response to attending site to
>                                 inspect.
>
>
>                                 Craig is obviously upset with the
>                                 progress and feels the matter and
>                                 repairs undertaken late in 2015 have
>                                 made the issue worse and require
>                                 urgent attention.
>
>
>                                 Craig’s has asked me to seek some
>                                 direction from you about this matter
>                                 and would like for you to advise the
>                                 Building Manager, myself and the
>                                 Engineers to attend to the matter
>                                 urgently to have further repairs
>                                 undertaken to stop further water leaking.
>
>                                 Please advise on the above urgently?
>
>                                 Kind regards,
>
>                                 *Patrick Rush*
>
>                                 Strata Manager
>
>                                 Phone:(02) 9266 2600 |
>                                 Email:prush at stratatitle.com.au
>                                 <mailto:prush at stratatitle.com.au> |
>                                 Address:PO Box2727, Taren Point, NSW 2229
>
>                                 **
>
>                                 <mime-attachment.gif>
>                                 <http://www.stratatitle.com.au/><mime-attachment.gif>
>                                 <http://www.facebook.com/StrataTitleManagement><mime-attachment.gif><http://www.linkedin.com/company/strata-title-management-stm><mime-attachment.gif>
>                                 <http://www.twitter.com/STMStrata><mime-attachment.gif>
>                                 <http://www.pinterest.com/STMStrata><mime-attachment.gif>
>                                 <http://plus.google.com/+StrataTitleManagemenSydney>
>
>                                 **
>
>                                 *Emailed Communication / Documents
>                                 Disclaimer*
>
>                                 STM Limited takes no responsibility
>                                 for content included in this email
>                                 when relating to a client matter.
>
>                                 Please view Vesture’s full email
>                                 communication disclaimer on our
>                                 website
>                                 –www.stratatitle.com.au/disclaimer/
>                                 <http://www.stratatitle.com.au/disclaimer/>
>
>                                 *Important Notice: *Owners should be
>                                 aware that all correspondence,
>                                 including letters, facsimile
>                                 transmissions and emails are retained
>                                 on the file of your scheme and may be
>                                 subject to inspection by owners and
>                                 residents within your scheme, as well
>                                 as prospective purchasers for any lot
>                                 that may be for sale within your
>                                 scheme. As such author discretion is
>                                 advised.
>
>                                 *From:*Lee Carroll
>                                 [mailto:lee.carroll at costinroe.com.au]
>                                 *Sent:* Thursday, 21 January 2016 5:03 PM
>                                 *To:* Info BFMS
>                                 *Cc:* George Ziri; ec at 200william.com
>                                 <mailto:ec at 200william.com>; Patrick
>                                 Rush; Catherine Plane; Wayne E. Costin
>                                 *Subject:* 12765.00 160121 RE: SP
>                                 67851 - URGENT Tribunal Order for
>                                 Water Penetration in Unit 601 - CRAIG
>                                 LAFOREST VS BODY CORPORATE STRATA PLAN
>                                 67851
>
>                                 Hi William,
>
>                                 I have attached some photographs taken
>                                 on the 22^nd December 2015 on my last
>                                 site visit.
>
>                                 Whilst the bubbling is worse in your
>                                 photographs, it is not dramatically so.
>
>                                 The area of bubbling and water
>                                 dropping onto my terrace is 3 times
>                                 more than prior to the works being
>                                 carried out recently by the
>                                 contractor.  In addition, the water
>                                 has a dirt/rust colour which is
>                                 staining everywhere below the
>                                 overhang. The water is dropping
>                                 through at a considerable rate 24/7
>                                 regardless of whether there is any
>                                 rain.  This has been the same problem
>                                 for the last 8 years.
>
>                                 I would suggest we wait a bit longer
>                                 before getting the painter back to
>                                 patch the effected areas.
>
>                                 The area doesn’t need patching – we
>                                 need to expose where the water is
>                                 coming from/through ie its source.
>
>                                 The bubbling and efflorescence appears
>                                 to be mostly confined the slab edge
>                                 which is in keeping with my theory.
>
>                                 The rust staining on the paint bubbles
>                                 is concerning as it indicates
>                                 corrosion of reinforcement in the
>                                 concrete.
>
>                                 Again, why would we patch if rust
>                                 staining is coming through?! Patching
>                                 cannot be completed quickly enough
>                                 from the amount of water which is
>                                 forcing its way through.  As is
>                                 currently happening patching only
>                                 sends the water in a different
>                                 direction within the wall frame and
>                                 subsequently water drops through from
>                                 a new area.
>
>                                 As discussed we had a job in Mosman
>                                 awhile back with a similar issue. The
>                                 planter box has seven layers of
>                                 membrane installed and yet the water
>                                 persisted. It turned out to be coming
>                                 under the planter box from the terrace
>                                 area. There may be a similar issue
>                                 here, although in my opinion there
>                                 would should also be water penetration
>                                 visible on the soffit of the slab as
>                                 the slab edge if this was the case.
>
>                                 It should be noted that this is not
>                                 water penetration into Unit 601. It is
>                                 merely
>
>                                 (merely??) water dripping off the slab
>                                 edge over the balcony, which would be
>                                 expected anyway, at least when it
>                                 rains. Again, the water drips
>                                 constantly 24/7 even when there is NO
>                                 rain. The issue is the efflorescence
>                                 and rust staining on the tiles and
>                                 furniture.
>
>                                 I have confirmed in previous email
>                                 correspondence to the Strata Manager
>                                 that I will take the Body Corporate
>                                 once taken to Tribunal. Unless I
>                                 receive confirmation by February 16
>                                 that another way of handling this
>                                 matter is to take place, I will follow
>                                 through with the Tribunal.
>
>                                 I have been advised by the
>                                 representatives of the Tribunal that
>                                 severe penalties will be charged to
>                                 the owners if the original order by
>                                 the Tribunal is not once and for all
>                                 carried out.
>
>                                 Craig Laforest
>
>                                 Best Regards,
>
>                                 *Lee Carroll
>                                 **Senior Engineer (Remedial/Forensic)*
>
>                                 <mime-attachment.gif>
>
>
>                                 Strata Engineering Solutions
>
>                                 A business of Costin Roe Consulting
>                                 Pty Ltd
>                                 ABN 50 003 696 446
>
>                                 Level 1, 8 Windmill Street, Walsh Bay
>                                 PO Box N419, Sydney, NSW 1220 Australia
>                                 tel: +61 2 9251 7699 fax: +61 2 9241
>                                 3731 mobile:0448 -007-469
>
>                                 email: Lee.Carroll at strataeng.com.au
>                                 <mailto:Lee.Carroll at strataeng.com.au>
>
>                                 web: www.strataeng.com.au
>                                 <http://www.strataeng.com.au>
>
>                                 All our other details remain the same
>
>                                 Postal address: PO Box N419, Sydney
>                                 NSW 1220
>
>                                 Phone: 02-9251 7699 Fax: 02-9241 3731
>
>                                 Email: mail at costinroe.com.au
>                                 <mailto:mail at costinroe.com.au>    
>                                 Email: mail at strataeng.com.au
>                                 <mailto:mail at strataeng.com.au> Web:
>                                 www.costinroe.com.au
>                                 <http://www.costinroe.com.au>
>
>                                 *Offices in Sydney, Adelaide,
>                                 Brisbane, Melbourne, Newcastle and
>                                 Wollongong.*
>
>                                 The information transmitted is
>                                 intended only for the person or entity
>                                 to which it is addressed and may
>                                 contain confidential and/or privileged
>                                 material.  Any review
>
>                                 retransmission, dissemination, or
>                                 other use of, or taking of any action
>                                 in reliance upon, this information by
>                                 persons or entities other than the
>                                 intended recipient is
>
>                                 prohibited. If you receive this in
>                                 error, please contact the sender and
>                                 delete the material from any
>                                 computer.  It is the duty of the
>                                 recipient to virus scan and otherwise
>
>                                 test the information provided before
>                                 loading it onto any computer system. 
>                                 Costin Roe Consulting Pty Ltd does not
>                                 warrant that the information is free
>                                 of a virus or any
>
>                                 other defect or error.
>
>
>                                 *From:*Info BFMS
>                                 [mailto:info at bfms.com.au]
>                                 *Sent:* Thursday, 21 January 2016 2:49 PM
>                                 *To:* Lee Carroll
>                                 *Cc:* George Ziri; ec at 200william.com
>                                 <mailto:ec at 200william.com>; 'Patrick Rush'
>                                 *Subject:* RE: SP 67851 - URGENT
>                                 Tribunal Order for Water Penetration
>                                 in Unit 601 - CRAIG LAFOREST VS BODY
>                                 CORPORATE STRATA PLAN 67851
>
>                                 Hi Lee
>
>                                 As discussed, please see attached
>                                 photos of the water penetration in
>                                 apartment 601 for your reference.
>
>                                 Please advise.
>
>                                 For any further queries, please
>                                 contact our office.
>
>                                 Kind regards,
>
>                                 <mime-attachment.gif>
>
>
>
>
>
>
>                                 _______________________________________________
>
>                                 EC mailing list
>
>                                 EC at 200william.com
>                                 <mailto:EC at 200william.com>
>
>                                 http://200william.com/mailman/listinfo/ec
>
>
>
>
>
>
>                             -- 
>
>                             /* Matt Perkins
>
>                                     Direct 1300 137 379       
>                             Spectrum Networks Ptd. Ltd.
>
>                                     Office 1300 133 299
>                             matt at spectrum.com.au
>                             <mailto:matt at spectrum.com.au>
>
>                                                                Level
>                             6, 350 George Street Sydney 2000
>
>                                     Spectrum Networks is a member of
>                             the Communications Alliance & TIO
>
>                             */
>
>
>
>
>
>                             _______________________________________________
>
>                             EC mailing list
>
>                             EC at 200william.com <mailto:EC at 200william.com>
>
>                             http://200william.com/mailman/listinfo/ec
>
>
>
>
>
>                         -- 
>
>                         /* Matt Perkins
>
>                                 Direct 1300 137 379        Spectrum
>                         Networks Ptd. Ltd.
>
>                                 Office 1300 133 299
>                         matt at spectrum.com.au
>                         <mailto:matt at spectrum.com.au>
>
>                                                            Level 6,
>                         350 George Street Sydney 2000
>
>                                 Spectrum Networks is a member of the
>                         Communications Alliance & TIO
>
>                         */
>
>
>
>
>                         _______________________________________________
>
>                         EC mailing list
>
>                         EC at 200william.com <mailto:EC at 200william.com>
>
>                         http://200william.com/mailman/listinfo/ec
>
>
>
>
>                     -- 
>
>                     /* Matt Perkins
>
>                             Direct 1300 137 379        Spectrum
>                     Networks Ptd. Ltd.
>
>                             Office 1300 133 299 matt at spectrum.com.au
>                     <mailto:matt at spectrum.com.au>
>
>                                                        Level 6, 350
>                     George Street Sydney 2000
>
>                             Spectrum Networks is a member of the
>                     Communications Alliance & TIO
>
>                     */
>
>
>
>
>                     _______________________________________________
>
>                     EC mailing list
>
>                     EC at 200william.com <mailto:EC at 200william.com>
>
>                     http://200william.com/mailman/listinfo/ec
>
>
>
>
>                 -- 
>
>                 /* Matt Perkins
>
>                         Direct 1300 137 379        Spectrum Networks
>                 Ptd. Ltd.
>
>                         Office 1300 133 299 matt at spectrum.com.au
>                 <mailto:matt at spectrum.com.au>
>
>                                                    Level 6, 350 George
>                 Street Sydney 2000
>
>                         Spectrum Networks is a member of the
>                 Communications Alliance & TIO
>
>                 */
>
>
>
>                 _______________________________________________
>
>                 EC mailing list
>
>                 EC at 200william.com <mailto:EC at 200william.com>
>
>                 http://200william.com/mailman/listinfo/ec
>
>
>
>             -- 
>
>             /* Matt Perkins
>
>                     Direct 1300 137 379        Spectrum Networks Ptd.
>             Ltd.
>
>                     Office 1300 133 299 matt at spectrum.com.au
>             <mailto:matt at spectrum.com.au>
>
>                                                Level 6, 350 George
>             Street Sydney 2000
>
>                     Spectrum Networks is a member of the
>             Communications Alliance & TIO
>
>             */
>
>             _______________________________________________
>             EC mailing list
>             EC at 200william.com <mailto:EC at 200william.com>
>             http://200william.com/mailman/listinfo/ec
>
>
>
>     -- 
>
>     /* Matt Perkins
>
>             Direct 1300 137 379        Spectrum Networks Ptd. Ltd.
>
>             Office 1300 133 299 matt at spectrum.com.au
>     <mailto:matt at spectrum.com.au>
>
>                                        Level 6, 350 George Street
>     Sydney 2000
>
>             Spectrum Networks is a member of the Communications
>     Alliance & TIO
>
>     */
>
>
>
> _______________________________________________
> EC mailing list
> EC at 200william.com
> http://200william.com/mailman/listinfo/ec


-- 
/* Matt Perkins
         Direct 1300 137 379        Spectrum Networks Ptd. Ltd.
         Office 1300 133 299        matt at spectrum.com.au
                                    Level 6, 350 George Street Sydney 2000
         Spectrum Networks is a member of the Communications Alliance & TIO
*/

-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0001.html 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1976 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0006.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 589 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0007.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 613 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0008.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 851 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0009.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 879 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0010.gif 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1004 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20160419/8f1177e3/attachment-0011.gif 


More information about the EC mailing list