[200William-EC SP67851] FW: ELECTRIC CHARGE FEELING 601/200 WILLIAM ST
Ed Sainsbury
edsainsbury at ozemail.com.au
Wed Jun 24 21:24:51 AEST 2015
George,
Would you also get Sharp Cooling to look at the A/C boiler room fuse/switch.
I had them inspect the A/C unit in my apartment, as it was not heating. They
have given my unit the all clear with full gas, and working perfectly.
However it was not producing any heat. They went upstairs and the boiler
room fuse has switched off. I believe that it has happened again, as my A/C
will not produce heat again.
Is anyone else experiencing this?
Secondly, I have no objection to the work order.
Regards,
Edward
From: George Ziri [mailto:georgeziri at bfms.com.au]
Sent: Wednesday, June 24, 2015 5:49 PM
To: Matt Perkins; ec at 200william.com; Pia Cunningham
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST -
ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
Good afternoon All
Please find attached the review of the cooling tower.
If there is no objection within 72 hours I will issue Sharp Cooling a work
order.
From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Matt Perkins
Sent: Friday, 12 June 2015 4:03 PM
To: ec at 200william.com; Pia Cunningham
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST -
ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
Hi Pia,
Further to my conversation with George on that matter. George is going to
engage Sharp cooling to check the ventilation/HVAC Plant for vibrations.
Can you please advice Mr LaForest that George will be arranging . (give me a
call for clarification)
Matt
On 12/06/2015 3:37 pm, Matt Perkins wrote:
Thanks Pia,
William form BMFS will be attending 601 to see if he can fell the same
effect Mr Laforest is feeling. I would say the next step from there is to
get the building engineer to prepare a report as to what if any action we
need to take.
Matt.
On 12/06/2015 3:22 pm, Pia Cunningham wrote:
Hi All,
Please see email from electrician:
Hi Pia,
As you are aware, Craig Laforest called our Glenco office on 21/10/2014 and
we listened to his concerns and provided the following opinion based on our
own general knowledge. Craig explained that he had concerns about some kind
of radiation which he feels is emanating from above his apartment which he
says causes him sleeplessness, nausea and irritation. We suggested that
"radiation" as such is unlikely and could be caused by RF transmitters or
microwave communications equipment etc. On occasion mobile net transmitters
and receivers are installed on roof tops under a position lease agreement,
owned and serviced by a Telecommunications carrier. Craig indicated that
this is not the case for this building.
The possibilities which we can speculate which could be the cause or a
factor in causing what Craig claims to be experiencing are as follows;
Vibration - vibration from motors through a ducting system could possibly
create a low frequency vibration noise. Low frequency sound waves can cause
nausea and discomfort.
Static electricity - static electricity is a common problem and can cause
discomfort for very sensitive people. This varies with ambient weather
conditions and is enhanced by the presence of synthetic materials - carpet,
blankets, furniture. Static is felt as an electric charge which builds up
and often will be felt as a zap when you touch a metallic object or another
person as the charge is released.
Air pressure - I mentioned that sudden variations in air pressure can cause
dizziness. This can be observed if you stand with your ear to an elevator
door. One ear experiences different pressure to the other which makes you
feel giddy. Whether or not the lift shaft could cause such an effect is
unknown but I would expect this to be unlikely.
Summary
. Our advice to Craig was to carry out a test by isolating the
ventilation system (above his apartment ) and test whether he notices a
change. At this per we have not confirm if this is feasible as it may impact
on the ventilation operation. If he does notice a change, an air
conditioning or ventilation specialist needs to attend to balance the motor
& address vibration issues.
. Arrange for a company who are expert in detecting radiation to
attend site and carry out relevant testing with appropriate equipment.
. Liaise with electrical engineering company for further evaluation
on other possibilities that may be imminent.
We are happy to assist in any other way and look forward to hearing from
you.
Regards,
Glenn Rosen
<http://www.glenco.com.au/> <image003.jpg>
<http://www.glenco.com.au/> <image004.jpg>
<https://www.facebook.com/glencoelectricalservices> <image005.jpg>
<https://twitter.com/GlencoES> <image006.png>
<http://www.linkedin.com/pub/glenn-rosen/16/317/6b1> <image007.png>
Glenco Electrical Services
Glenco Security and Alarms
T: (02) 9700 9996 | F: (02) 9700 9966 | PO Box 7402, Alexandria NSW 2015
W: <http://www.glenco.com.au/> www.glenco.com.au | E:
service at glenco.com.au
This e-mail and any attachments are confidential. If you are not the
intended recipient, you must not disclose or use the information contained
in it. If you have received this e-mail in error, please contact us
immediately and delete all copies. Glenco is not responsible for any changes
made to a document other than those made by Glenco, or for the effect on the
document's meaning. Before opening or using attachments please check them
for viruses.
Should you have any queries regarding the above, please do not hesitate to
contact me.
Have a nice day,
Kind regards,
Pia Cunningham
Strata Manager
BMC Manager and
Company Title Manager
Phone: (02) 9266 2600 | Email: <mailto:northshore at stratatitle.com.au>
pcunningham at stratatitle.com.au | Address: PO Box 72, STRAWBERRY HILLS NSW
2012, Level 7, 447 Kent Street, SYDNEY NSW 2000
<http://www.stratatitle.com.au/>
cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
<http://www.facebook.com/StrataTitleManagement>
cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
<http://www.linkedin.com/company/strata-title-management-stm>
cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box
<http://www.twitter.com/STMStrata>
cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
<http://www.pinterest.com/STMStrata> pinterest.png
<http://plus.google.com/+StrataTitleManagemenSydney> google_plus.png
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when
relating to a client matter.
Please view Vesture's full email communication disclaimer on our website -
<http://www.stratatitle.com.au/disclaimer/>
www.stratatitle.com.au/disclaimer/
Tile2014_YoungStrataManager_HighCom_S
Important Notice: Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.
From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Ed Sainsbury
Sent: Thursday, 11 June 2015 9:45 PM
To: ec at 200william.com
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST -
ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
EC,
I get a strange magnetic field in my apartment next to the column in the
kitchen. If I put a compass there it reacts strongly away from North and is
effected by what is in the column. I assume that it is an electrical
conduit?
Having said that, I would ask that the EC put in writing to Mr Laforest that
he gather some kind of evidence as it is a strange type of request. If there
is an issue, the strata can look at the facts.
Regards,
Edward
From: Barney Kitay [mailto:barnet at kitays.com]
Sent: Thursday, June 11, 2015 3:04 PM
To: George Ziri
Cc: ec at 200william.com
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST -
ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
I believe that if George is not able to "feel" it, he should get an
independent consultant at his own cost to provide evidence of this "power"
if something is discovered AND subsequently corrected (by the strata), he
can be reimbursed. i don't think we should fund a wild goose chase...
---
Kind Regards
Barney
m: +61 (0)400 200 446
e: barnet at kitays.com
==================================================
On 11-06-2015 14:21, George Ziri wrote:
Good afternoon All,
I have briefed Matt on this matter and confirm below.
Approximently 2 years ago the owner of 601 called me into his apartment to
investigate the "feeling of power" over the bed in the main bedroom. When I
stood near the bed I was not able to agree or feel the power. The owner
insisted it was there.
I suggested to the owner to obtain an independent assessment by an
electrical enginneer. To date this has not occurred.
There may or may not be power circulating the apartment but I have never
encounted or heard of this unless one was standing in a room with mains
power exceeding 415v.
Please advise if you wish for me to arrnage our facilities manager to
inspect. And if the matter isnt discovered then how to proceed.
From: ec-bounces at 200william.com [mailto:ec-bounces at 200william.com] On Behalf
Of Pia Cunningham
Sent: Thursday, 11 June 2015 10:17 AM
To: Matt Perkins; ec at 200william.com
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST -
ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
Hi George,
Can you please investigate?
Have a lovely day,
Pia Cunningham
Strata Title Management
Ph: 9266 2600
-------- Original message --------
From: Matt Perkins <matt at spectrum.com.au>
Date: 11/06/2015 9:32 am (GMT+09:30)
To: ec at 200william.com
Subject: Re: [200William-EC SP67851] FW: MESSAGE FROM CRAIG LAFOREST -
ELECTRIC CHARGE FEELING 601/200 WILLIAM STREET, WOOLLOOMOOLOO
Hi Pia,
I suggest you get George to investigate if this is a strata problem or if
he should contact his own Electrician.
Matt.
/On 11/06/2015 9:16 am, Pia Cunningham wrote:
Good Morning All,
Please see below email from Craig regarding a power surge in his unit again.
Should we send someone to investigate?
Should you have any queries regarding the above, please do not hesitate to
contact me.
Have a nice day,
Kind regards,
Pia Cunningham
Strata Manager
BMC Manager and
Company Title Manager
Phone: (02) 9266 2600 | Email: <mailto:northshore at stratatitle.com.au>
pcunningham at stratatitle.com.au | Address: PO Box 72, STRAWBERRY HILLS NSW
2012, Level 7, 447 Kent Street, SYDNEY NSW 2000
<http://www.stratatitle.com.au/>
cid:BEA4112D-982D-40A7-9E7A-95F7B76E7ACE at fritz.box
<http://www.facebook.com/StrataTitleManagement>
cid:C9038DE0-22F0-48A5-82C9-2AAA48233316 at fritz.box
<http://www.linkedin.com/company/strata-title-management-stm>
cid:E179D377-28C0-4C30-A8C6-AEA7CFCA04E5 at fritz.box
<http://www.twitter.com/STMStrata>
cid:1950DB4B-6066-468B-8AD1-875EFBC4D48C at fritz.box
<http://www.pinterest.com/STMStrata> pinterest.png
<http://plus.google.com/+StrataTitleManagemenSydney> google_plus.png
Emailed Communication / Documents Disclaimer
STM Limited takes no responsibility for content included in this email when
relating to a client matter.
Please view Vesture's full email communication disclaimer on our website -
<http://www.stratatitle.com.au/disclaimer/>
www.stratatitle.com.au/disclaimer/
Tile2014_YoungStrataManager_HighCom_S
Important Notice: Owners should be aware that all correspondence, including
letters, facsimile transmissions and emails are retained on the file of your
scheme and may be subject to inspection by owners and residents within your
scheme, as well as prospective purchasers for any lot that may be for sale
within your scheme. As such author discretion is advised.
From: CSCL [mailto:cscl at optusnet.com.au]
Sent: Wednesday, 10 June 2015 1:49 PM
To: Pia Cunningham
Cc: traceyquick at hotmail.com
Subject: MESSAGE FROM CRAIG LAFOREST - ELECTRIC CHARGE FEELING 601/200
WILLIAM STREET, WOOLLOOMOOLOO
Hello Pia,
I left you a message over the weekend but wanted to contact you as soon as
possible about an old concern which has started again. We are still feeling
what can be best described as a 'charge' in my bedroom particularly ,and the
second bedroom partially. It can happen at any time of the day or night.
Would you please have this investigated by an expert asap. You'll remember I
sent through an expert's advice on this matter. This testing will probably
take several days/nights to find where this is coming from but it feels like
it is directly from the ceiling area/walls above the main bedroom and second
bedroom.
I look forward to hearing from you at the earliest opportunity.
Thanks Pia and best wishes,
Craig
_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec
--
/* Matt Perkins
Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
Level 6, 350 George Street Sydney 2000
Spectrum Networks is a member of the Communications Alliance & TIO
*/
_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec
_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec
--
/* Matt Perkins
Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
Level 6, 350 George Street Sydney 2000
Spectrum Networks is a member of the Communications Alliance & TIO
*/
_______________________________________________
EC mailing list
EC at 200william.com
http://200william.com/mailman/listinfo/ec
--
/* Matt Perkins
Direct 1300 137 379 Spectrum Networks Ptd. Ltd.
Office 1300 133 299 matt at spectrum.com.au
Level 6, 350 George Street Sydney 2000
Spectrum Networks is a member of the Communications Alliance & TIO
*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0001.html
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 35654 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0002.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 17026 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0008.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4236 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0009.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3977 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0010.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4502 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0011.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1473 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0012.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1732 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0013.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 60738 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0003.jpe
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1493 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0014.png
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1724 bytes
Desc: not available
Url : http://200william.com/mailman/private/ec/attachments/20150624/1d5562b4/attachment-0015.png
More information about the EC
mailing list